    Plywood allowed on non-combustible interior walls, with drywall finish in Type IIB

    Have a Building classified as a Type IIB building, using steel studs for interior walls. Contractor wants to put full sheets of OSB sheathing against the studs in the bathroom and behind the cabinets in the kitchen/snack area, as use it for "blocking", for attachment of the cabinets, grab bars, mirrors, and wall hung sinks. He then will put 5/8" gyp. bd over the top of that for the finish.

    Is that allowed? I cannot see anything definite under the IBC 603 exceptions that clearly defines that or not.

    Thanks

  2. #2
    Sawhorse
    Join Date
    Nov 2009
    Location
    West of the river CT
    Posts
    2,894
    Thanks
    437
    Thanked 216 Times in 204 Posts
    OSB will not work for blocking IMO.....does not hold a screw that well (grab bars and cabinets)...Again..IMO....FRT plywood would certainly be fine, the IBC does not put a limit on the amount of combustible blocking that I am aware of...but you might have to look at NFPA 13 for concealed combustible spaces.....
    Please support Jim Brown, Deputy Building Official from Gillette, Wyoming for ICC Board of Directors.
    My questions and answers are based on some bastardized hodge podge starting with the 2003 I-codes amended by the state of CT in 2005 and 2009 including the 2005 NEC ....and as of today.....The 2011 Connecticut Amendments to the 2009 International Energy Conservation Code portion of the 2005 State Building Code has been posted to the State Building Inspector’s website

  3. #3
    Member
    Join Date
    Dec 2013
    Location
    Waupun
    Posts
    6
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Building in not sprinklered.
    Should have mentioned that in original post.

  4. #4
    Sawhorse mtlogcabin's Avatar
    Join Date
    Oct 2009
    Location
    Big Sky Country
    Posts
    4,668
    Thanks
    67
    Thanked 600 Times in 476 Posts
    Welcome to the forum

    What the contractor wants to do is not "blocking" as understood in the construction trades

    If he wants to fully sheath the wall to provide attachment points for various items then he could use exception 25. Be aware that fire-retardant would requires specific fasteners and should not come in direct contact with standard steel studs as it could cause deterioration of the metal studs.

    2304.9.5 Fasteners and connectors in contact with preservative-treated and fire-retardant-treated wood.
    Fasteners and connectors in contact with preservative-treated and fire-retardant-treated wood shall be in accordance with Sections 2304.9.5.1 through 2304.9.5.4. The coating weights for zinc-coated fasteners shall be in accordance with ASTM A 153.
    Exception: Plain carbon steel fasteners in SBX/DOT and zinc borate preservative-treated wood in an interior, dry environment shall be permitted.
    Interesting non-lethal, yet legal Self Defense Products available on the market. Feel free to check out this web page , then share with family/friends.
    It is nice to know there are some options offered to protect our loved ones. You may also contact via web page link with any questions, or message me.
    www.mydamselpro.net/graceclawson

  5. #5
    Sawhorse
    Join Date
    Oct 2009
    Posts
    7,277
    Thanks
    65
    Thanked 414 Times in 384 Posts
    Welcome!!!

    How did you find us

  6. #6
    Member
    Join Date
    Dec 2013
    Location
    Waupun
    Posts
    6
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Somebody I work with was doing code research and found this forum. He has used it multiple times with success with getting answers from his posts and finding answers already posted. He forwarded me the link and today was the first time I needed to post a question.

  7. #7
    Sawhorse mark handler's Avatar
    Join Date
    Oct 2009
    Location
    So. CA
    Posts
    6,441
    Thanks
    97
    Thanked 737 Times in 584 Posts

    Proper support in metal stud walls
    Last edited by mark handler; January 9th, 2014 at 19:25.
    “Never argue with stupid people, they will drag you down to their level and then beat you with experience.”― Mark Twain

  8. #8
    Sawhorse
    Join Date
    Oct 2009
    Posts
    7,277
    Thanks
    65
    Thanked 414 Times in 384 Posts
    Quote Originally Posted by Morphdesigns View Post
    Somebody I work with was doing code research and found this forum. He has used it multiple times with success with getting answers from his posts and finding answers already posted. He forwarded me the link and today was the first time I needed to post a question.
    Well welcome again

    Ask for code sections and helps to state what building code used and edition

  9. #9
    Sawhorse
    Join Date
    Nov 2009
    Location
    West of the river CT
    Posts
    2,894
    Thanks
    437
    Thanked 216 Times in 204 Posts
    I understand why he wants to use sheet goods...I did a university locker room in another life and by the time everything was blocked (mirrors, pt and tp dispensers, soap, partitions, grab bars, coat hooks, sinks, etc.....) it wouls have been 4X faster to sheath the whole wall...Maybe the same gage sheet metal as the blocking Mark shows, but in sheet form?

    MT...My book doesn't go up to 25....I will have to look at that one....
    Please support Jim Brown, Deputy Building Official from Gillette, Wyoming for ICC Board of Directors.
    My questions and answers are based on some bastardized hodge podge starting with the 2003 I-codes amended by the state of CT in 2005 and 2009 including the 2005 NEC ....and as of today.....The 2011 Connecticut Amendments to the 2009 International Energy Conservation Code portion of the 2005 State Building Code has been posted to the State Building Inspector’s website

  10. #10
    Sawhorse High Desert's Avatar
    Join Date
    Oct 2009
    Location
    Oregon
    Posts
    872
    Thanks
    23
    Thanked 57 Times in 44 Posts
    Cobustilble blocking is permitted for handrails, millwork, cabinets and door frames per 603.1 Item 11. If they want to fully sheet the wall, they need to do what mtlogcabin said...used FRT plywood
    "I’m a victim of soicumstance!" - Curly Howard
    Oregon Codes http://www.oregonbcd.org/

  11. #11
    Sawhorse mark handler's Avatar
    Join Date
    Oct 2009
    Location
    So. CA
    Posts
    6,441
    Thanks
    97
    Thanked 737 Times in 584 Posts
    Metal BACKING PLATE ADDED SUPPORT WHERE SHELVES, CABINETS, FIXTURES OR HANDRAILS ARE INSTALLED
    http://www.clarkdietrich.com/product.../backing-plate

    “Never argue with stupid people, they will drag you down to their level and then beat you with experience.”― Mark Twain

  12. The Following User Says Thank You to mark handler For This Useful Post:

    Yikes (January 10th, 2014)

  13. #12
    Sawhorse
    Join Date
    Nov 2009
    Location
    West of the river CT
    Posts
    2,894
    Thanks
    437
    Thanked 216 Times in 204 Posts
    Quote Originally Posted by High Desert View Post
    Cobustilble blocking is permitted for handrails, millwork, cabinets and door frames per 603.1 Item 11. If they want to fully sheet the wall, they need to do what mtlogcabin said...used FRT plywood
    603 allows combustible blocking......The question is,how much? I see no limit expressed or implied...."14. Blocking such as..." Gives examples...it is IMO, not intended to ba a catch all list.....
    Please support Jim Brown, Deputy Building Official from Gillette, Wyoming for ICC Board of Directors.
    My questions and answers are based on some bastardized hodge podge starting with the 2003 I-codes amended by the state of CT in 2005 and 2009 including the 2005 NEC ....and as of today.....The 2011 Connecticut Amendments to the 2009 International Energy Conservation Code portion of the 2005 State Building Code has been posted to the State Building Inspector’s website

  14. #13
    Sawhorse High Desert's Avatar
    Join Date
    Oct 2009
    Location
    Oregon
    Posts
    872
    Thanks
    23
    Thanked 57 Times in 44 Posts
    Didn't say it was a catch all list. Just said it was allowed in noncombustible construction. Also added that if they want to sheet the wall fully, it would have to be FRT plywood. The OP said they wanted to use the plywood to attach cabinets, grab bars , mirrors, sinks, etc. The proper material for that in section 603 is blocking, not sheathing the entire wall with plywood.
    "I’m a victim of soicumstance!" - Curly Howard
    Oregon Codes http://www.oregonbcd.org/

  15. #14
    Sawhorse
    Join Date
    Nov 2009
    Location
    West of the river CT
    Posts
    2,894
    Thanks
    437
    Thanked 216 Times in 204 Posts
    I am just trying to make clear that this code requirement is not.....what would the difference be between a wall fully blocked or a wall fully sheathed and laminated with drywall? (besides the extension rings for you sparkies )....FRTW is also combustible (even though much less so)...and can only be used where allowed by 603.1 1 or anywhere combustible wood is allowed
    Please support Jim Brown, Deputy Building Official from Gillette, Wyoming for ICC Board of Directors.
    My questions and answers are based on some bastardized hodge podge starting with the 2003 I-codes amended by the state of CT in 2005 and 2009 including the 2005 NEC ....and as of today.....The 2011 Connecticut Amendments to the 2009 International Energy Conservation Code portion of the 2005 State Building Code has been posted to the State Building Inspector’s website

  16. #15
    Sawhorse Builder Bob's Avatar
    Join Date
    Oct 2009
    Location
    Sunny SC - Coastal (not Charleston or Myrtle Beach)
    Posts
    1,280
    Thanks
    45
    Thanked 107 Times in 87 Posts
    Not an engineer, but thought I would try to answer your question - the blocking has a smaller surface area and a higher thermal mass than plywood.......the plywood is a smaller thermal mass thus absorbs heat at a faster rate and would allow the plywood through pryolysis to degrade, generate ignitable vapors, and ignite faster and quicker than a 2x4 blocking material.

    Also, blocking is not continuous thus has built in fire stops... plywood doesn't.

    Pyrolysis is usually the first chemical reaction that occurs in the burning of many solid organic fuels, like wood, cloth, and paper, and also of some kinds of plastic. In a wood fire, the visible flames are not due to combustion of the wood itself, but rather of the gases released by its pyrolysis, whereas the flame-less burning of a solid, called smouldering, is the combustion of the solid residue (char or charcoal) left behind by pyrolysis. Thus, the pyrolysis of common materials like wood, plastic, and clothing is extremely important for fire safety and firefighting.

    Pyrolysis is a thermochemical decomposition of organic material at elevated temperatures in the absence of oxygen (or any halogen). It involves the simultaneous change of chemical composition and physical phase, and is irreversible.


    The face of the plywood would be ex[posed on one side- either the internal stud cavity or to the room exposure.......type II construction limits the combustible products located within to make the building as fire resistant as possible without adding structural fire protection to the mix - (rule of thumb - type II-A does have limited structural protection within the design of the building)
    Lost is the south......
    ******************************
    Can you build to the minimum standards?

    Help us by supporting this forum .....If the advice you seek saved you a few bucks, pass on the wealth to this forum

    http://www.thebuildingcodeforum.com/forum/payments.php

    FWIW- MCP,CBO,CPE, ASCET, and A BYOB Ga. Dawg Fan!

  17. The Following 2 Users Say Thank You to Builder Bob For This Useful Post:

    Jim B (January 21st, 2014), mjesse (January 10th, 2014)

  18. #16
    Sawhorse
    Join Date
    Nov 2009
    Location
    West of the river CT
    Posts
    2,894
    Thanks
    437
    Thanked 216 Times in 204 Posts
    BB...... That is wicked scientific, and I do appreciate you taking the time to write......but what is to say that the blocking cannot be plywood? And where is the code requirement that it cannot run the entire height of a stud bay and each bay in the wall? I am sure as soon as they can find a way to make it work or market it there will be PVC blocking
    Please support Jim Brown, Deputy Building Official from Gillette, Wyoming for ICC Board of Directors.
    My questions and answers are based on some bastardized hodge podge starting with the 2003 I-codes amended by the state of CT in 2005 and 2009 including the 2005 NEC ....and as of today.....The 2011 Connecticut Amendments to the 2009 International Energy Conservation Code portion of the 2005 State Building Code has been posted to the State Building Inspector’s website

  19. #17
    Sawhorse
    Join Date
    Nov 2009
    Location
    West of the river CT
    Posts
    2,894
    Thanks
    437
    Thanked 216 Times in 204 Posts


    How much is too much?
    Please support Jim Brown, Deputy Building Official from Gillette, Wyoming for ICC Board of Directors.
    My questions and answers are based on some bastardized hodge podge starting with the 2003 I-codes amended by the state of CT in 2005 and 2009 including the 2005 NEC ....and as of today.....The 2011 Connecticut Amendments to the 2009 International Energy Conservation Code portion of the 2005 State Building Code has been posted to the State Building Inspector’s website

  20. #18
    Sawhorse
    Join Date
    Oct 2009
    Location
    metro DC
    Posts
    2,812
    Thanks
    13
    Thanked 72 Times in 65 Posts
    Code seems to be silent on the amount of combustibles... unless you go to 717.5 which throws us back to 603 .. judgment call, I guess.
    (PE)ach
    some days are just that..

  21. #19
    Sawhorse Builder Bob's Avatar
    Join Date
    Oct 2009
    Location
    Sunny SC - Coastal (not Charleston or Myrtle Beach)
    Posts
    1,280
    Thanks
    45
    Thanked 107 Times in 87 Posts
    steve ray, the blocking used in your picture I would agree with. the intent of the code is to "limit" combustibles in a type I or type II building. I would agree that the blocking in your picture is ok as long as this is for cabinetry and/or grab bars. I also noticed that the level of blocking varies from room to room.
    Lost is the south......
    ******************************
    Can you build to the minimum standards?

    Help us by supporting this forum .....If the advice you seek saved you a few bucks, pass on the wealth to this forum

    http://www.thebuildingcodeforum.com/forum/payments.php

    FWIW- MCP,CBO,CPE, ASCET, and A BYOB Ga. Dawg Fan!

  22. #20
    Sawhorse
    Join Date
    Nov 2009
    Location
    West of the river CT
    Posts
    2,894
    Thanks
    437
    Thanked 216 Times in 204 Posts
    We usually "ask" for FRTW...if they want to sheath a wet wall for blocking purposes, I do not have an issue with that. If you ever had that kind of fire inside the wall I am sure the water pipe would let loose and self supress....
    Please support Jim Brown, Deputy Building Official from Gillette, Wyoming for ICC Board of Directors.
    My questions and answers are based on some bastardized hodge podge starting with the 2003 I-codes amended by the state of CT in 2005 and 2009 including the 2005 NEC ....and as of today.....The 2011 Connecticut Amendments to the 2009 International Energy Conservation Code portion of the 2005 State Building Code has been posted to the State Building Inspector’s website

Bookmarks


Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •