    Egress Door

    Someone asked me today whether a separate deadbolt would be allowed in addition to a lever handle latchset on a single bathroom door in a non-residential facility. My response was that the door should be able to be unlatched with one operation, per IBC 2009 1008.1.9.5:

    1008.1.9.5 Unlatching. The unlatching of any door or leaf shall not require more than one operation.
    Exceptions:
    1. Places of detention or restraint.
    2. Where manually operated bolt locks are permitted by Section 1008.1.9.4.
    3. Doors with automatic flush bolts as permitted by Section 1008.1.9.3, Exception 3.
    4. Doors from individual dwelling units and sleeping units of Group R occupancies as permitted by Section 1008.1.9.3, Exception 4.


    My colleague then suggested that a bathroom door might not be considered a means of egress door so it wouldn't have to comply with the requirements of Chapter 10. I have always viewed a door in this application (single toilet, single office, etc.) as providing egress from that space. The IBC definition of an exit access doorway is, "A door or access point along the path of egress travel from an occupied room, area or space where the path of egress enters an intervening room, corridor, unenclosed exit access stair or unenclosed exit access ramp."

    Would a single toilet be considered an "occupied room?" How about a janitor's closet or storage room? Don't these doors have to meet the requirements for egress? If these types of doors are not "doors in a means of egress" I'm going to have to reprogram my mind.

    As always, thank you for your help.
    Last edited by LGreene; August 6th, 2010 at 18:35.

  2. #2
    Silver Member
    Join Date
    Nov 2009
    Location
    Northeastern Ohio
    Posts
    211
    Thanks
    0
    Thanked 0 Times in 0 Posts
    I agree with you. A toilet room, janitor closet, and storage rooms are "occupied spaces" when someone is in them. They then need a way out. Now maybe, there might be some confusion on your colleagues' part due that these are not considered "normally occupied spaces" in sections 1020.1.1, 1024.1, and 1023.6. The only place "normally occupied space" is defined is in the Commentary.

  3. #3
    Sawhorse Yankee's Avatar
    Join Date
    Mar 2010
    Location
    New England
    Posts
    1,342
    Thanks
    60
    Thanked 44 Times in 37 Posts
    Yes they are occupied spaces

  4. #4
    Moderator Mule's Avatar
    Join Date
    Oct 2009
    Location
    Texas
    Posts
    1,520
    Thanks
    20
    Thanked 59 Times in 48 Posts
    I don't know about that!
    OCCUPIABLE SPACE. A room or enclosed space designed
    for human occupancy in which individuals congregate for
    amusement, educational or similar purposes or in which occupants
    are engaged at labor, and which is equipped with means
    of egress and light and ventilation facilities meeting the
    requirements of this code.


    Maybe....which occupants are engaged at labor....Sometimes I labor......I know I know....TMI!
    Mule
    Building Official
    Texas

    Built to Code = Building the worst that the code will allow!

  5. #5
    Administrator fatboy's Avatar
    Join Date
    Oct 2009
    Location
    Northern CO
    Posts
    4,048
    Thanks
    72
    Thanked 303 Times in 247 Posts
    I'd have to agree with you Ms. Greene.
    Arguing with an inspector is like wrestling with a pig in mud, pretty soon you realize that the pig is enjoying it!

    This response brought to you by one of the paying members of the Building Code Forum.
    You can join the paying members and support this forum, for a small donation at
    http://www.thebuildingcodeforum.com/forum/payments.php

  6. #6
    Sawhorse north star's Avatar
    Join Date
    Oct 2009
    Posts
    2,233
    Thanks
    281
    Thanked 173 Times in 163 Posts
    * * *

    Is this single toilet a public toilet, and is it the ONLY toilet?

    * * *


  7. #7
    Sawhorse Builder Bob's Avatar
    Join Date
    Oct 2009
    Location
    Sunny SC - Coastal (not Charleston or Myrtle Beach)
    Posts
    1,265
    Thanks
    43
    Thanked 104 Times in 86 Posts
    ICC/ ANSI A117.1
    604.8.3 Doors. Toilet compartment doors,
    including door hardware, shall comply with Section
    404.1, except if the approach is to the latch
    side of the compartment door clearance
    between the door side of the stall and any
    obstruction shall be 42 inches (1065 mm) minimum.
    Doors shall be located in the front partition
    or in the side wall or partition farthest from the
    water closet.Where located in the front partition,
    the door opening shall be 4 inches (100 mm)
    maximum from the side wall or partition farthest
    from the water closet.Where located in the side
    wall or partition, the door opening shall be 4
    inches (100 mm) maximum from the front partition.
    The door shall be self–closing. A door pull
    complying with Section 404.2.6 shall be placed
    on both sides of the door near the latch. Toilet
    compartment doors shall not swing into the
    required minimum area of the compartment.

    404.2.6 Door Hardware. Handles, pulls,
    latches, locks, and other operable parts on
    accessible doors shall have a shape that is
    easy to grasp with one hand and does not
    require tight grasping, pinching, or twisting of
    the wrist to operate. Operable parts of such
    hardware shall be 34 inches (865 mm) minimum
    and 48 inches (1220 mm) maximum
    above the floor. Where sliding doors are in the
    fully open position, operating hardware shall be
    exposed and usable from both sides.
    Lost is the south......
    ******************************
    Can you build to the minimum standards?

    Help us by supporting this forum .....If the advice you seek saved you a few bucks, pass on the wealth to this forum

    http://www.thebuildingcodeforum.com/forum/payments.php

    FWIW- MCP,CBO,CPE, ASCET, and A BYOB Ga. Dawg Fan!

  8. #8
    Sawhorse TJacobs's Avatar
    Join Date
    Oct 2009
    Location
    Peoples Republic of Illinois
    Posts
    1,310
    Thanks
    80
    Thanked 43 Times in 37 Posts
    I also agree with Ms. Greene.
    Jake

    This response brought to you by one of the paying members of the Building Code Forum.
    You can join the paying members and support this forum, for a small donation at
    http://www.thebuildingcodeforum.com/forum/payments.php

  9. #9
    Corporate Supporter LGreene's Avatar
    Join Date
    Oct 2009
    Location
    Needham, Massachusetts
    Posts
    875
    Blog Entries
    15
    Thanks
    220
    Thanked 88 Times in 72 Posts
    Mule does raise an interesting point (along with more information than I was looking for)...the definition of occupiable space wouldn't include a single toilet (IMO). On the other hand, I can't imagine single toilets not being subject to the requirements for egress. I've submitted a request for an opinion to the ICC and I'll let you know what I hear.

    North Star: Is this single toilet a public toilet, and is it the ONLY toilet?
    It's sort of a general question, not specific to a certain restroom, but imagine the staff bathrooms in a school, a single bathroom in a restaurant, or the family restroom in an airport.

    Thanks everyone!

  10. #10
    Administrator fatboy's Avatar
    Join Date
    Oct 2009
    Location
    Northern CO
    Posts
    4,048
    Thanks
    72
    Thanked 303 Times in 247 Posts
    The reality is, if you are standing in a space, you are occupying it. JMHO
    Arguing with an inspector is like wrestling with a pig in mud, pretty soon you realize that the pig is enjoying it!

    This response brought to you by one of the paying members of the Building Code Forum.
    You can join the paying members and support this forum, for a small donation at
    http://www.thebuildingcodeforum.com/forum/payments.php

  11. #11
    Sawhorse
    Join Date
    Oct 2009
    Location
    metro DC
    Posts
    2,811
    Thanks
    13
    Thanked 72 Times in 65 Posts
    not included for figuring number of exits since it'll be the same people who are always in the building; the doors don't have to swing out (unless you can get 50 people in there)... don't need an exit sign (since it'll be pretty obvious how to get back out), etc.

    Security is sometimes a consideration (even to the point of having to push a button to exit), then pull the door. That's two operations.. (should be tied to the alarm system in case of emergency.. but they not always are.. hopefully if power goes out the controlled access releases).

    Look at 1008.1.9.3 (2009), but it's not marked as having changed.

    I don't believe the intent of the code is to prohibit the use of locks on bathroom doors.
    (PE)ach
    some days are just that..

  12. #12
    Corporate Supporter LGreene's Avatar
    Join Date
    Oct 2009
    Location
    Needham, Massachusetts
    Posts
    875
    Blog Entries
    15
    Thanks
    220
    Thanked 88 Times in 72 Posts
    Peach: Security is sometimes a consideration (even to the point of having to push a button to exit), then pull the door. That's two operations.. (should be tied to the alarm system in case of emergency.. but they not always are.. hopefully if power goes out the controlled access releases).

    Look at 1008.1.9.3 (2009), but it's not marked as having changed.

    I don't believe the intent of the code is to prohibit the use of locks on bathroom doors.
    Hi Peach -

    I don't think the intent of the code is to prohibit locks on bathrooms, but I don't see an exception that would allow multiple locks. Section 1008.1.9.5 (2009) requires one motion to unlatch the door - the act of pushing or pulling the door isn't counted, just the operation(s) required to release the latch. I don't typically specify products that would require someone to press a button and then open the door because of the section 1008.1.9 requirement that "egress doors shall be readily openable from the egress side without the use of a key or special knowledge or effort." Having to push a button on the wall could be seen as requiring special knowledge. For access-controlled egress doors, the button on the wall is in addition to the motion sensor which automatically unlocks the door upon approach of an occupant, as well as power failure/fire alarm unlock.

    There's nothing in section 1008.1.9.3 that describes a bathroom door:

    1008.1.9.3 Locks and latches. Locks and latches shall be permitted to prevent operation of doors where any of the following exists:
    1. Places of detention or restraint.
    2. In buildings in occupancy Group A having an occupant load of 300 or less, Groups B, F, M and S, and in places of religious worship, the main exterior door or doors are permitted to be equipped with key-operated locking devices from the egress side provided:
    2.1. The locking device is readily distinguishable as locked;
    2.2. A readily visible durable sign is posted on the egress side on or adjacent to the door stating: THIS DOOR TO REMAIN UNLOCKED WHEN BUILDING IS OCCUPIED. The sign shall be in letters 1 inch (25 mm) high on a contrasting background;
    and
    2.3. The use of the key-operated locking device is revokable by the building official for due cause.
    3. Where egress doors are used in pairs, approved automatic flush bolts shall be permitted to be used, provided that the door leaf having the automatic flush bolts has no doorknob or surface-mounted hardware.
    4. Doors from individual dwelling or sleeping units of Group R occupancies having an occupant load of 10 or less are permitted to be equipped with a night latch, dead bolt or security chain, provided such devices are openable from the inside without the use of a key or tool.
    5. Fire doors after the minimum elevated temperature has disabled the unlatching mechanism in accordance with listed fire door test procedures.

  13. #13
    Sawhorse Yankee's Avatar
    Join Date
    Mar 2010
    Location
    New England
    Posts
    1,342
    Thanks
    60
    Thanked 44 Times in 37 Posts
    All I know is that if I am sitting in there and the fire alarm goes off and the lights go out, I want to get out ASAP!

  14. #14
    Gold Member
    Join Date
    Oct 2009
    Location
    The SoCal Beach
    Posts
    852
    Thanks
    57
    Thanked 32 Times in 31 Posts
    All I know is that if I am sitting in there and the fire alarm goes off and the lights go out, I want to get out ASAP!
    Exactly! (But finish your "paperwork".......)

  15. #15
    Sawhorse north star's Avatar
    Join Date
    Oct 2009
    Posts
    2,233
    Thanks
    281
    Thanked 173 Times in 163 Posts
    * * *
    LGreene,

    Could we say that the restrooms are an ' incidental use' room / space, so that we could
    classify them as an occupied space? - - Section 508.2.1: Occupancy classification. "An
    incidental use area shall be classified in accordance with the occupancy of that portion of
    the building in which it is located or the building shall be classified as a mixed occupancy
    and shall comply with Section 508.3.", thereby classifying them as 'occupied '?


    Yikes,

    Section 1006.1 [ in the `06 IBC ] would require emergency lighting in the toilet
    rooms, ...to help you, eeeerrrr, the user to complete their use in a safe and
    hygienic manner. Section 1006.1: "The means of egress, including the exit
    discharge, shall be illuminated at all times the building space served by the
    means of egress is occupied."

    * * *


  16. #16
    Sawhorse
    Join Date
    Oct 2009
    Posts
    7,042
    Thanks
    61
    Thanked 402 Times in 373 Posts
    north star just say it

    YOU have to always finish the paperwork!!!!!!!!!!!!!!!

  17. #17
    Sawhorse
    Join Date
    Oct 2009
    Location
    metro DC
    Posts
    2,811
    Thanks
    13
    Thanked 72 Times in 65 Posts
    we don't require exit signs over the ONE door in a classroom..
    (PE)ach
    some days are just that..

  18. #18
    Corporate Supporter LGreene's Avatar
    Join Date
    Oct 2009
    Location
    Needham, Massachusetts
    Posts
    875
    Blog Entries
    15
    Thanks
    220
    Thanked 88 Times in 72 Posts
    Thanks for your input everyone. I received an answer from the ICC and I've pasted it below:

    Subject: 09 IBC 1008.1.9.5 (PH-8/9)

    Questions: Is a single bathroom in a non-residential facility considered an "occupiable space" which would therefore have to comply with the "one operation to unlatch" requirement of this section? Would a lever handle latch set and a separate deadbolt (2 motions to unlatch) be acceptable on a toilet room, or should the door comply with the one operation to unlatch requirement? The definition of occupiable space doesn't clearly state that a single toilet would have to comply, but common sense says that a door leading out of a bathroom would need to meet the requirements for an exit access door.

    Answers: Toilet rooms are not considered ‘occupiable’ based on the definition of Occupiable Spaces in Chapter 2. However, doors accessing toilet rooms are expected to have operable parts on both sides that unlatch with a single operation. A door without either a latch or a lock would also comply. Toilet room door hardware, when provided, is held to the same requirements as all other hardware on doors intended for human passage. The exceptions in the above sections identify the only locations where bolt locks or multiple hardware operations are permitted. Single-user toilet rooms that need a lock function for privacy must un-lock and un-latch with one operation.