    NFPA 13 or 13R?

    I've got a 4-story Holiday Inn Express submitted for review with over 50% of the ground floor as A3 occupancy (meeting/banquet rooms, indoor pool, breakfast area, lobby, etc.) The hotel has approx 100 rooms with rooms on the remainder of the 1st floor, as well as all of the 2nd, 3rd, & 4th floors.

    Architect is proposing an NFPA 13R system for the whole building... I countered with a full 13 system since 903.3.1.2 doesn't address A occupancies.

    Opinions?
    Last edited by vegas paul; August 26th, 2010 at 14:06.

  2. #2
    Sawhorse mtlogcabin's Avatar
    Join Date
    Oct 2009
    Location
    Big Sky Country
    Posts
    5,165
    Thanks
    75
    Thanked 753 Times in 598 Posts
    13R in the sleeping rooms/floors, 13 all other uses/areas. Remember if he is using the sprinklers for an area increase it has to be a full NFPA 13 throughout (506.3 06 ed)

  3. #3
    Supporter
    Join Date
    Nov 2009
    Location
    Southern California
    Posts
    761
    Thanks
    57
    Thanked 39 Times in 30 Posts
    I agree with mtlog cabin. Our apartment buildings always have 13 int he leasing offices, commnity rooms, etc.
    In addition to his comment for area increase, you may need a full 13 if you are using sprinklers for a story increase.

  4. #4
    Silver Member
    Join Date
    Oct 2009
    Location
    Salina, KS
    Posts
    492
    Thanks
    0
    Thanked 1 Time in 1 Post
    What about the concealed spaces above the 4th floor? Does the fact that the 4th floor have only guest rooms matter?

  5. #5
    Silver Member
    Join Date
    Oct 2009
    Posts
    437
    Thanks
    1
    Thanked 3 Times in 3 Posts
    Agree w/ mtlogcabin. I just had the same building go up here, except that there were no sleeping rooms on the 1st floor. It was a Holiday Inn, without the "Express". The 1st floor was all A-2, and was fully sprinklered per 13. the upper floors were 13R. I wasn't the "fire inspector" on the project, but we worked together alot on the bulding.

    Hold them to both, IMHO.

  6. #6
    Sawhorse TJacobs's Avatar
    Join Date
    Oct 2009
    Location
    60102
    Posts
    1,319
    Thanks
    87
    Thanked 46 Times in 40 Posts
    The attic on a 13R does not need to be sprinklered, so if they qualify for 13R on the upper floor, no attic sprinklers.
    Jake

    http://www.nwboca.org

    This response brought to you by one of the paying members of the Building Code Forum.
    You can join the paying members and support this forum, for a small donation at
    http://www.thebuildingcodeforum.com/forum/payments.php

  7. #7
    Silver Member
    Join Date
    Oct 2009
    Posts
    437
    Thanks
    1
    Thanked 3 Times in 3 Posts
    In our case they sprinklered the attic, and then did away with the draftstopping, per 2006 IBC 717.4.2 #4.

  8. #8
    Platinum Member
    Join Date
    Nov 2009
    Location
    state of jefferson
    Posts
    1,077
    Thanks
    20
    Thanked 44 Times in 36 Posts
    Quote Originally Posted by Glennman CBO View Post
    In our case they sprinklered the attic, and then did away with the draftstopping, per 2006 IBC 717.4.2 #4.
    same here!

  9. #9
    Sawhorse
    Join Date
    Oct 2009
    Location
    metro DC
    Posts
    2,826
    Thanks
    13
    Thanked 74 Times in 66 Posts
    I believe you'll find that 18" concealed spaces require sprinklers using either 13 or 13R... which means you sprinkle concealed combustible floor ceiling areas too.
    (PE)ach
    some days are just that..

  10. #10
    Sawhorse hlfireinspector's Avatar
    Join Date
    Nov 2009
    Location
    North Mississippi
    Posts
    280
    Thanks
    30
    Thanked 20 Times in 15 Posts
    Same here "B Western" sprinkler floor/ceiling void /had no attic flat roof. If flat roof don't forget stair to roof and roof connection on standpipe.

  11. #11
    Moderator FM William Burns's Avatar
    Join Date
    Oct 2009
    Location
    The Mitten State
    Posts
    2,669
    Thanks
    178
    Thanked 171 Times in 130 Posts
    Agree with others Combo 13/13R. Also make sure if they need a pump for the 4th floor it's a listed one with all the trim and alarms to the FACP. They got mad at me when I pointed that out. BTW...Holiday Inn is taking back the "express" in our region and they are all going over face lifts

    "Fire suppression is a failure in prevention, practice fire safety, the life saved may be your own"


  12. #12
    Supporter
    Join Date
    Nov 2009
    Location
    Southern California
    Posts
    761
    Thanks
    57
    Thanked 39 Times in 30 Posts
    FM William Burns - everytime I read your posts, I hear them with Jim Carrey's voice and maniacal laugh in my head! Does that happen to anyone else out there?

  13. #13
    Silver Member
    Join Date
    Oct 2009
    Location
    South Texas
    Posts
    340
    Thanks
    14
    Thanked 9 Times in 9 Posts
    Yikes,

    Actually your post makes me feel better, I thought I was the only one hearing voices in my head.

  14. #14
    Moderator FM William Burns's Avatar
    Join Date
    Oct 2009
    Location
    The Mitten State
    Posts
    2,669
    Thanks
    178
    Thanked 171 Times in 130 Posts
    Would you like the profile picture of me kissing the deer? Imagine what your minds would do with that

    "Fire suppression is a failure in prevention, practice fire safety, the life saved may be your own"


  15. #15
    Silver Member
    Join Date
    Oct 2009
    Location
    South Texas
    Posts
    340
    Thanks
    14
    Thanked 9 Times in 9 Posts
    I say go for it FM WB. If we can't make fun of ourselves and our friends who can we make fun of?

  16. #16
    Moderator FM William Burns's Avatar
    Join Date
    Oct 2009
    Location
    The Mitten State
    Posts
    2,669
    Thanks
    178
    Thanked 171 Times in 130 Posts
    Got that right TexT

    "Fire suppression is a failure in prevention, practice fire safety, the life saved may be your own"


  17. #17
    Administrator RJJ's Avatar
    Join Date
    Oct 2009
    Location
    about 1' east of the white water
    Posts
    2,793
    Thanks
    3
    Thanked 62 Times in 52 Posts
    Agree with the combo! Also with peach on the concealed space 18". If its not there then no issue.

    Well! Guys You all must be in dream world! I know FM and he doesn't look or sound like what you are thinking! OH YA kissing deer! That's 4 legged!

  18. #18
    Silver Member
    Join Date
    Oct 2009
    Posts
    437
    Thanks
    1
    Thanked 3 Times in 3 Posts
    When things start going crazy around here I click onto you tube on FM Bill and laugh my head off (at home of course). I think they should let us go into the you tube skit as required learing here at work!

  19. #19
    Sawhorse Builder Bob's Avatar
    Join Date
    Oct 2009
    Location
    Sunny SC - Coastal (not Charleston or Myrtle Beach)
    Posts
    1,326
    Thanks
    46
    Thanked 112 Times in 92 Posts
    Should be a true 13 system with applications of 13 being used for the areas containing sleeping rooms....... See appendix A1.1.

    It is recognized that an occupancy incidental to the operations of the residential occupancy might exist within that residential occupancy. Such incidental occupancy would be considered part of the predominant (residential) occupancy and subject to the provisions of the predominant (residential) occupancy by 6.1.14.2 of NFPA 101 and similar provisions in many local building and fire codes. Use of NFPA 13R throughout the entire building in this case is allowed.
    Where buildings are greater than four stories in height, or where buildings are of mixed use where residential is not the predominant occupancy, residential portions of such buildings should be protected with residential or quick-response sprinklers in accordance with 8.4.5 of NFPA 13. Other portions of such buildings should be protected in accordance with NFPA 13. Where buildings of mixed use can be totally separated so that the residential portion is considered a separate building under the local code, NFPA 13R can be used in the residential portion while NFPA 13 is used in the rest of the building. (Examples of incidental accessory occupancies found in NFPA 13R installations can include parking garages/areas, community laundry rooms, clubhouses, exercise facilities, tenant storage, and so forth.)
    Lost is the south......
    ******************************
    Can you build to the minimum standards?

    Help us by supporting this forum .....If the advice you seek saved you a few bucks, pass on the wealth to this forum

    http://www.thebuildingcodeforum.com/forum/payments.php

    FWIW- MCP,CBO,CPE, ASCET, and A BYOB Ga. Dawg Fan!

Bookmarks


Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •