Thread: allowable building area (frontage and sprinklered),

  1. #1
    Member
    Join Date
    Feb 2011
    Location
    Bay Area, San Francisco, San Jose, CA
    Posts
    24
    Thanks
    4
    Thanked 1 Time in 1 Post

    allowable building area (frontage and sprinklered),

    The single story sprinklered building in question is open 21' on the sides, 41' in back, and fronts the public way open with 60'

    The formula below only considers frontage and sprinklers.

    Question:where in the code does the building get any increase for the sides and back yards in addition to this formula, or does it?
    (my understanding is it has to be 60 all sides to be unlimited)

    Aa = At + [(At)(If)/100] + [(At)(Is)/100] = ______________________

    Thanks,
    Keith
    Last edited by Keith; March 29th, 2011 at 14:31.

  2. #2
    Platinum Member
    Join Date
    Dec 2009
    Location
    Husker Country
    Posts
    1,583
    Thanks
    63
    Thanked 99 Times in 80 Posts
    from the 2006

    506.2 Frontage increase.

    Every building shall adjoin or have access to a public way to receive an area increase for frontage. Where a building has more than 25 percent of its perimeter on a public way or open space having a minimum width of 20 feet (6096 mm), the frontage increase shall be determined in accordance with the following:

    If = [F / P – 0.25] W / 30 (Equation 5-2)

    where:

    If = Area increase due to frontage.

    F = Building perimeter that fronts on a public way or open space having 20 feet (6096 mm) open minimum width (feet).

    P = Perimeter of entire building (feet).

    W = Width of public way or open space (feet) in accordance with Section 506.2.1.

  3. #3
    Sawhorse
    Join Date
    Oct 2009
    Location
    Henrico VA
    Posts
    1,032
    Thanks
    3
    Thanked 115 Times in 102 Posts
    The open space on rear and sides counts as frontage-- would be better titiled open space increase.

    Where the width of the open space on the same lot or to the far side of the public way varies, you can break up the portions and integrate over the perimiter to get a weighted average W.
    W/30 at any point shall not exceed 1, except if all other unlimited area building requirements are met then it can have a maximum value of 2.

    From 2009 IBC
    506.2 Frontage increase. Every building shall adjoin or have access to a public way to receive a building area increase for frontage. Where a building has more than 25 percent of its perimeter on a public way or open space having a minimum width of 20 feet (6096 mm), the frontage increase shall be determined in accordance with the following:

    If=[F/P-0.25]W/30

    (Equation 5-2)

    where:

    If= Area increase due to frontage.

    F = Building perimeter that fronts on a public way or open space having 20 feet (6096 mm) open minimum width (feet).

    P = Perimeter of entire building (feet).

    W = Width of public way or open space (feet) in accordance with Section 506.2.1.
    506.2.1 Width limits. The value of W shall be at least 20 feet (6096 mm). Where the value of W varies along the perimeter of the building, the calculation performed in accordance with Equation 5-2 shall be based on the weighted average of each portion of exterior wall and open space where the value of W is greater than or equal to 20 feet (6096 mm). Where the value of W exceeds 30 feet (9144 mm), a value of 30 feet (9144 mm) shall be used in calculating the weighted average, regardless of the actual width of the open space. Where two or more buildings are on the same lot, W shall be measured from the exterior face of a building to the exterior face of an opposing building, as applicable.

    Exception: The value of W divided by 30 shall be permitted to be a maximum of 2 when the building meets all requirements of Section 507 except for compliance with the 60-foot (18 288 mm) public way or yard requirement, as applicable.

    506.2.2 Open space limits. Such open space shall be either on the same lot or dedicated for public use and shall be accessed from a street or approved fire lane.

  4. #4
    Sawhorse RLGA's Avatar
    Join Date
    Oct 2009
    Location
    Phoenix, AZ
    Posts
    552
    Thanks
    11
    Thanked 112 Times in 88 Posts
    To add to Coug Dad's and Frank's post, since you have two yards that are less than 30 feet, you have to calculate a "weighted" W instead of using W=30.

    W/30 cannot exceed 1, therefore W cannot be more than 30. If your building could qualify for unlimited area but the only thing preventing that from happening is the 60-foot yards all around, then W/30 cannot exceed 2, thus W cannot be more than 60.

    Assuming the former, to calculate a weighted W, you have to know what your building perimeter is. For the sake of an example, let's assume your building is 100 feet by 200 feet, with the 100-foot portions having the 21-foot yards.

    Since the front has a yard that exceeds 30 feet, W=30 for that portion, as well as the back with its 41-foot yard. For the sides, W=21. To calculate the weighted average, take each W and multiply it by the portion of the perimeter that W is applicable, sum the totals up and divide by the total perimeter of the building. Using the example building, the calculation would be as follows:

    Weighted W = [(30' x 200') + (30' x 200') + (21' x 100') + (21' x 100')]/600'

    Weighted W = 27'

    Therefore, your calculation for If would be as follows:

    If = [600'/600' - 0.25]27/30
    If = {edit - slight calculation error} 0.675 or 67.5%
    Last edited by RLGA; March 29th, 2011 at 12:27.
    Ron Geren
    RLGA Technical Services
    www.specsandcodes.com

  5. The Following User Says Thank You to RLGA For This Useful Post:

    steveray (March 29th, 2011)

  6. #5
    Sawhorse
    Join Date
    Nov 2009
    Location
    West of the river CT
    Posts
    2,689
    Thanks
    399
    Thanked 190 Times in 178 Posts
    Great simple explanation Ron!
    Please support Jim Brown, Deputy Building Official from Gillette, Wyoming for ICC Board of Directors.
    My questions and answers are based on some bastardized hodge podge starting with the 2003 I-codes amended by the state of CT in 2005 and 2009 including the 2005 NEC ....and as of today.....The 2011 Connecticut Amendments to the 2009 International Energy Conservation Code portion of the 2005 State Building Code has been posted to the State Building Inspectorís website

  7. #6
    Sawhorse TJacobs's Avatar
    Join Date
    Oct 2009
    Location
    Peoples Republic of Illinois
    Posts
    1,310
    Thanks
    80
    Thanked 43 Times in 37 Posts
    deleted by poster
    Last edited by TJacobs; March 29th, 2011 at 12:23. Reason: duplicate info
    Jake

    This response brought to you by one of the paying members of the Building Code Forum.
    You can join the paying members and support this forum, for a small donation at
    http://www.thebuildingcodeforum.com/forum/payments.php

  8. #7
    Sawhorse RLGA's Avatar
    Join Date
    Oct 2009
    Location
    Phoenix, AZ
    Posts
    552
    Thanks
    11
    Thanked 112 Times in 88 Posts
    I made a calculation error in my earlier post, but I have corrected it. See above.

    Also, you're welcome, steveray.
    Ron Geren
    RLGA Technical Services
    www.specsandcodes.com

  9. #8
    Member
    Join Date
    Dec 2009
    Posts
    16
    Thanks
    1
    Thanked 0 Times in 0 Posts
    Keith,
    Sec. 506.2.2 Open space limits. Such open space shall be either on the same lot or dedicated for the public use and shall be accessed from a street or approved fire lane.
    Common mistake made when calculating frontage increase - is that rear yard is taken into account and there is no APPROVED FIRE LANE for rear yard access. In your case at least one of your 21 ft wide side yards shall serve as an approved fire lane. Landscaped yards are not considered approved fire lane. In most cases 20 ft wide paving with hummer-head turn around for fire engine will satisfy this requirement (check with your fire department for the definition of approved fire lane).
    An example for frontage increase calculation (using weighted average for variable depths of yards) and actual frontage increase calculator is included within “Building Code Height and Area Calculator” at
    www.ara4help.com

  10. #9
    Silver Member
    Join Date
    Dec 2009
    Location
    Vancouver, Washington
    Posts
    213
    Thanks
    5
    Thanked 5 Times in 4 Posts
    Does anyone have the commentary for section 506.2.2?
    I may have made that mistake, I don't recall a specific project, but it's a matter of interpretation. I have always interpreted that the access could be through the side yard to the street. If no side yards, then no using the back yard. Anyone else?

  11. #10
    Sawhorse RLGA's Avatar
    Join Date
    Oct 2009
    Location
    Phoenix, AZ
    Posts
    552
    Thanks
    11
    Thanked 112 Times in 88 Posts
    The open space must have access to a public way or fire lane. You cannot access one open space (i.e. back yard) through another open space (i.e. side yard), unless the through open space is a fire lane. This is based on the IBC Commentary.

    If the back open space of Keith's building did not have an alley, diveway to a public way, or fire lane through one of the side yards, then the back open space cannot be included in the frontage increase.

    However, as MarkRandall states, it's a matter of interpretation. Since the Commentary is not code, I've seen BO's allow yards for the frontage increase if all portions of the building exterior are within the distance prescribed in IFC Section 503.1.1.
    Ron Geren
    RLGA Technical Services
    www.specsandcodes.com

  12. #11
    Platinum Member
    Join Date
    Oct 2009
    Location
    alabama
    Posts
    3,709
    Thanks
    24
    Thanked 212 Times in 182 Posts
    The commentary is not the code and is not adopted as such.

    Where the commentary states that there are additional requirements beyond those listed in the code, it is no longer a legitimate interpretation of the code as written.

  13. #12
    Sawhorse mtlogcabin's Avatar
    Join Date
    Oct 2009
    Location
    Big Sky Country
    Posts
    4,549
    Thanks
    63
    Thanked 567 Times in 448 Posts
    shall be accessed from a street or approved fire lane.
    [F] FIRE LANE. A road or other passageway developed to allow the passage of fire apparatus. A fire lane is not necessarily intended for vehicular traffic other than fire apparatus.
    Common mistake made when calculating frontage increase - is that rear yard is taken into account and there is no APPROVED FIRE LANE for rear yard access
    Disagree Not all building access is provided by public streets so the option of an approved fire lane is allowed but not required. The open space areas have to have access to a public street or fire lane. Nothing prohibits accessing one open space from another
    Interesting non-lethal, yet legal Self Defense Products available on the market. Feel free to check out this web page , then share with family/friends.
    It is nice to know there are some options offered to protect our loved ones. You may also contact via web page link with any questions, or message me.
    www.mydamselpro.net/graceclawson

  14. #13
    Member
    Join Date
    Dec 2009
    Posts
    16
    Thanks
    1
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by mtlogcabin View Post
    [F] FIRE LANE. A road or other passageway developed to allow the passage of fire apparatus. A fire lane is not necessarily intended for vehicular traffic other than fire apparatus.

    Disagree Not all building access is provided by public streets so the option of an approved fire lane is allowed but not required. The open space areas have to have access to a public street or fire lane. Nothing prohibits accessing one open space from another
    I think intend of the code is to provide sufficient space for fire apparatus access to fight the fire, and not just any width of access thru other open spaces.
    Letís say the only access from the public way to the 40 ft wide rear yard is thru a 3 ft side yard. Would you use the rear yard for frontage increase? If yes, then what is the minimum width for the side yard to be considered an access?

  15. #14
    Sawhorse RLGA's Avatar
    Join Date
    Oct 2009
    Location
    Phoenix, AZ
    Posts
    552
    Thanks
    11
    Thanked 112 Times in 88 Posts
    mtlogcabin:

    I concur, but look in the 2009 Commentary (Before everyone starts posting that the Commentary is not code, I know that and said it previously; however, BOs will look at the Commentary to support their positions) at Figure 506.2.2(1) on page 5-19, which shows a building with a yard to the south accessible by a road, a 15' yard on the west, a 20' yard on the east, and a 100' yard on the north. The figure has no fire lane to the north yard and there is no alley, drive, etc. to the north yard. The Commentary text regarding the figure states:

    "Example 1: In Figure 506.2.2(1), the south and east side of the building facing the street can be considered open perimeter (frontage). The north side of the building cannot be considered open perimeter for purposes of the increase, since it is not accessible from the street or a fire lane. Even though the 20-foot-wide yard can be included in open frontage because it does not provide a fire lane to the rear of the building, the 100-foot yard cannot be included."

    The Commentary clearly provides an interpretation that is not directly supported by actual code text (however, it may have been the intent), but many BOs use the Commentary as the basis for their own interpretations.
    Ron Geren
    RLGA Technical Services
    www.specsandcodes.com

  16. #15
    Silver Member
    Join Date
    Dec 2009
    Location
    Vancouver, Washington
    Posts
    213
    Thanks
    5
    Thanked 5 Times in 4 Posts
    ara4help,
    My interpretation has been a yard that's large enough to be counted towards area increases (20'). As long as the yards are contiguous, not sure why it would matter. Fire personnel need room to move around the building to fight the fire. There's distances in the fire code of 150' to fire access and this number can be increased per IFC503.1.1 exception 1. As long as you meet the distances, I think you should be fine.
    I also agree the commentary is not code, thanks RLGA for posting that. I've been known to change my opinion based on what it says, but so far, I'm not convinced to change my interpretation.

  17. #16
    Sawhorse mtlogcabin's Avatar
    Join Date
    Oct 2009
    Location
    Big Sky Country
    Posts
    4,549
    Thanks
    63
    Thanked 567 Times in 448 Posts
    The commentary also points out the purpose of the open space

    "Provides access to the structure by fire service personel, a temporary refuge area for occupants as they leave the building in a fire emergency and reduced exposure to and from adjacent structures"

    I am not a firefighter but I do not believe an operations chief would send his equipment up the side of the building depicted in the commentary to fight a fire. His men with hoses yes, the truck no
    Interesting non-lethal, yet legal Self Defense Products available on the market. Feel free to check out this web page , then share with family/friends.
    It is nice to know there are some options offered to protect our loved ones. You may also contact via web page link with any questions, or message me.
    www.mydamselpro.net/graceclawson

  18. #17
    Silver Member
    Join Date
    Dec 2009
    Location
    Vancouver, Washington
    Posts
    213
    Thanks
    5
    Thanked 5 Times in 4 Posts
    Mtlogcabin, I was thinking along the same lines, but I'm not a fire fighter (and I don't play one on TV) so I avoided commenting. If a fire lane was provided close to a building, I agree, I can't imagine it being used for the fire truck to fight a fire. The truck would be toast in no time.