    1 hour fire wall

    Plans show an existing 1hr wall, one layer 5/8 rock on each side, 3 5/8 stud. Took quite a while longer than expected to install 7 new outlets.

    Quotes are from the 08 NEC unless otherwise noted.

  2. #2
    Sawhorse
    Join Date
    Oct 2009
    Posts
    6,481
    Thanks
    29
    Thanked 348 Times in 324 Posts
    Not sure if that is a listed one hour wall

  3. #3
    Sawhorse chris kennedy's Avatar
    Join Date
    Oct 2009
    Location
    Miami Fla
    Posts
    1,070
    Thanks
    62
    Thanked 66 Times in 55 Posts
    Quote Originally Posted by cda View Post
    Not sure if that is a listed one hour wall
    Is that a bit of humor?
    Quotes are from the 08 NEC unless otherwise noted.

  4. #4
    Platinum Member
    Join Date
    Nov 2009
    Location
    state of jefferson
    Posts
    1,046
    Thanks
    17
    Thanked 39 Times in 32 Posts
    better get some looong screws for the receptacle!

  5. #5
    Gold Member
    Join Date
    Jun 2011
    Location
    South Texas
    Posts
    582
    Thanks
    4
    Thanked 31 Times in 29 Posts
    ya can't always depend on the prints. Wow, a 2 & 3/4 mud ring.

  6. #6
    Sawhorse
    Join Date
    Nov 2009
    Location
    West of the river CT
    Posts
    2,493
    Thanks
    390
    Thanked 169 Times in 158 Posts
    More importantly......how do you patch it and maintain the (3 hour?) rating?
    Please support Jim Brown, Deputy Building Official from Gillette, Wyoming for ICC Board of Directors.
    My questions and answers are based on some bastardized hodge podge starting with the 2003 I-codes amended by the state of CT in 2005 and 2009 including the 2005 NEC ....and as of today.....The 2011 Connecticut Amendments to the 2009 International Energy Conservation Code portion of the 2005 State Building Code has been posted to the State Building Inspector’s website

  7. #7
    Sawhorse Examiner's Avatar
    Join Date
    Oct 2009
    Location
    USA
    Posts
    454
    Thanks
    0
    Thanked 25 Times in 24 Posts
    Is it a fire wall or a fire partition or a fire barrier? Fire walls have to remain in place upon the collapse of the building on either side. Fire partitions are often rated partitions used in corridors. Fire barrier are used for occupancy separation and shafts and require the same rating as the wall for their supporting structure. Office software will not let me see picture. I think others have answered your question.
    Chaos, Panic, Disorder.....my work is done here.
    Bureaucracy is a challenge to be conquered with a righteous attitude, the tolerance for stupidity and a bulldozer when necessary.

  8. #8
    Sawhorse Builder Bob's Avatar
    Join Date
    Oct 2009
    Location
    Sunny SC - Coastal (not Charleston or Myrtle Beach)
    Posts
    1,237
    Thanks
    42
    Thanked 93 Times in 78 Posts
    Looks like a practice where a three hour rating was required and somebody let them place the required rating on one side of the wall. Often, a common practice when dealing with existing buildings.

    3/4" sheet rock with 3 - 5/8" layers of sheet rock ..... Things that make you go Hhhhhmmmmmmm.....
    Lost is the south......
    ******************************
    Can you build to the minimum standards?

    Help us by supporting this forum .....If the advice you seek saved you a few bucks, pass on the wealth to this forum

    http://www.thebuildingcodeforum.com/forum/payments.php

    FWIW- MCP,CBO,CPE, ASCET, and A BYOB Ga. Dawg Fan!

  9. #9
    Platinum Member
    Join Date
    Oct 2009
    Location
    alabama
    Posts
    3,709
    Thanks
    24
    Thanked 212 Times in 182 Posts
    Quote Originally Posted by Builder Bob View Post
    Looks like a practice where a three hour rating was required and somebody let them place the required rating on one side of the wall. Often, a common practice when dealing with existing buildings.
    Please tell me you are joking.

  10. #10
    Platinum Member
    Join Date
    Dec 2009
    Location
    Husker Country
    Posts
    1,583
    Thanks
    63
    Thanked 99 Times in 80 Posts
    The Gypsum Association has some interesting 2, 3, and 4 hour rated walls that are asymmetric. WP 1529 and WP 1943 are examples.