Thread: Boiler room, exterior door

  1. #1
    Silver Member
    Join Date
    Oct 2009
    Location
    N/E Indiana
    Posts
    288
    Thanks
    0
    Thanked 23 Times in 18 Posts

    Boiler room, exterior door

    Table 508.2 indicates that a furnace/boiler room requires a 1-hr separation or sprinkler. If there is an exterior door leading to the boiler room and the exterior wall are otherwise not required to be a rated assembly, does the door have to be a rated assembly? Regardless of the exterior wall requirements, does the boiler room have to have rated walls on the exterior? Wall is 40 feet from property line and I am not sure about protected opening requirements. Thanks

  2. #2
    Platinum Member
    Join Date
    Dec 2009
    Location
    Husker Country
    Posts
    1,583
    Thanks
    63
    Thanked 99 Times in 80 Posts
    No rating would be required if you have adequate fire separation distance.