Thread: condensate line insulation, ac units

  1. #1
    Gold Member
    Join Date
    Jun 2011
    Location
    South Texas
    Posts
    582
    Thanks
    4
    Thanked 31 Times in 29 Posts

    condensate line insulation, ac units

    i've heard it tossed around the office that condensate lines for ac units only need to be insulated for only 12 feet from the unit. "it's in the code" , ok, now looking, where? we're in the '06 int'l codes. i've looked in the mech and plbg, and am not seeing it. any help is appreciated

  2. #2
    Sawhorse mtlogcabin's Avatar
    Join Date
    Oct 2009
    Location
    Big Sky Country
    Posts
    4,729
    Thanks
    67
    Thanked 607 Times in 483 Posts
    It's not in the code.
    No insulation required at all condensate drain lines

    Does not mean it should it not be looked at for a potential problem. The dewpoint on a paticular surface will depend on many variables.

  3. #3
    Sawhorse north star's Avatar
    Join Date
    Oct 2009
    Posts
    2,302
    Thanks
    289
    Thanked 177 Times in 166 Posts
    + + + +

    codeworks,

    Ask your "office tossers" to please provide you a code section or
    standard that requires the 12 ft. of insulation.

    + + + +



  4. #4
    Sawhorse Sifu's Avatar
    Join Date
    Sep 2011
    Posts
    592
    Thanks
    27
    Thanked 30 Times in 26 Posts
    I don't have it in front of me but I think that may come from the energy code. I think it gives the min. thickness and lengths.

  5. #5
    Sawhorse mtlogcabin's Avatar
    Join Date
    Oct 2009
    Location
    Big Sky Country
    Posts
    4,729
    Thanks
    67
    Thanked 607 Times in 483 Posts
    I don't believe condesate from an AC unit will meet the tempature ranges.

    N1103.3 Mechanical system piping insulation.
    Mechanical system piping capable of carrying fluids above 105F (40C) or below 55F (13C) shall be insulated to a minimum of R-3.

    Energy code
    503.2.8 Piping insulation.
    All piping serving as part of a heating or cooling system shall be thermally insulated in accordance with Table 503.2.8.

    Exceptions:

    1. Factory-installed piping within HVAC equipment tested and rated in accordance with a test procedure referenced by this code.

    2. Factory-installed piping within room fan-coils and unit ventilators tested and rated according to AHRI 440 (except that the sampling and variation provisions of Section 6.5 shall not apply) and 840, respectively.

    3. Piping that conveys fluids that have a design operating temperature range between 55F (13C) and 105F (41C).

    4. Piping that conveys fluids that have not been heated or cooled through the use of fossil fuels or electric power.

    5. Runout piping not exceeding 4 feet (1219 mm) in length and 1 inch (25 mm) in diameter between the control valve and HVAC coil.

  6. #6
    Sawhorse Sifu's Avatar
    Join Date
    Sep 2011
    Posts
    592
    Thanks
    27
    Thanked 30 Times in 26 Posts
    Yep, completely missed the word condensate. Now that I see it I don't think I have ever heard of a requirement for it either. But I do think that may be where they are getting the 12' figure. I seem to remember that figure as a requirement somewhere. I think the intent for insulating ac lines is to conserve energy/control energy loss. That would be lost on condensate disposal.

  7. #7
    Sawhorse ICE's Avatar
    Join Date
    Jun 2011
    Location
    A concrete jungle near you.
    Posts
    4,862
    Thanks
    145
    Thanked 299 Times in 244 Posts
    Quote Originally Posted by Sifu View Post
    I think the intent for insulating ac lines is to conserve energy/control energy loss. That would be lost on condensate disposal.
    I thought that you might appreciate an example.



  8. #8
    Sawhorse mtlogcabin's Avatar
    Join Date
    Oct 2009
    Location
    Big Sky Country
    Posts
    4,729
    Thanks
    67
    Thanked 607 Times in 483 Posts
    AC lines yes but there is no energy loss to the AC sytem through condesate disposal.

  9. #9
    Sawhorse
    Join Date
    Jan 2012
    Posts
    857
    Thanks
    8
    Thanked 123 Times in 116 Posts
    Most manufacturers specifically state in the IOM to insulate the primary condensate line when installed in locations where the dew point level of the condensate is possible.

  10. #10
    Silver Member
    Join Date
    Jan 2012
    Location
    California
    Posts
    105
    Thanks
    22
    Thanked 9 Times in 8 Posts
    Quote Originally Posted by Gregg Harris View Post
    Most manufacturers specifically state in the IOM to insulate the primary condensate line when installed in locations where the dew point level of the condensate is possible.
    That is the answer. Manufr installation instructions. A copy should be kept with the job site plan set.

  11. #11
    Sawhorse mtlogcabin's Avatar
    Join Date
    Oct 2009
    Location
    Big Sky Country
    Posts
    4,729
    Thanks
    67
    Thanked 607 Times in 483 Posts
    This was discussed on the "old" site. good reading
    http://www4.iccsafe.org/cgi-bin/ulti...c;f=2;t=002614

  12. #12
    Member
    Join Date
    Mar 2012
    Posts
    6
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Condensate drain insulation

    Quote Originally Posted by codeworks View Post
    i've heard it tossed around the office that condensate lines for ac units only need to be insulated for only 12 feet from the unit. "it's in the code" , ok, now looking, where? we're in the '06 int'l codes. i've looked in the mech and plbg, and am not seeing it. any help is appreciated
    FBC MECH.2010-307.2.5 Pipe Insulation. All horizontal primary condensate drains within unconditioned areas shall be insulated to prevent condensation from forming on the exterior of the drain. Attics get pretty hot down here in Florida. We make them insulate the entire drain in the attic.

  13. #13
    Member
    Join Date
    Mar 2012
    Posts
    6
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by ICE View Post
    I thought that you might appreciate an example.


    Missing nail plate!

  14. #14
    Sawhorse mtlogcabin's Avatar
    Join Date
    Oct 2009
    Location
    Big Sky Country
    Posts
    4,729
    Thanks
    67
    Thanked 607 Times in 483 Posts
    Quote Originally Posted by GETRDONE View Post
    FBC MECH.2010-307.2.5 Pipe Insulation. All horizontal primary condensate drains within unconditioned areas shall be insulated to prevent condensation from forming on the exterior of the drain. Attics get pretty hot down here in Florida. We make them insulate the entire drain in the attic.
    I know we did it in Fl since the early 70's I just did not know if it was a South Fl code or SBCCI.