Advanced Code Group (ACG) has been performing plan review services for municipalities, architectural firms, third-party agencies, contractors and code officials for over 10 years with great success and response. We would be happy to assist you with your I-Code plan review needs, whether on a limited or full time basis. Plan review is performed by several experienced inspectors, certified as plan reviewers in different disciplines. We offer expedited plan review services electronically. This has been a well received process that eliminates reprinting of drawings. At the end of plan review, you have the option to accept an electronic stamp on the plans or submit the final, approved drawings for traditional stamping with return via FedEx. Why print, submit then print changes and submit again when this can be done just once?

We will always do our best to work within your budget and allotted timeframe. Feel free to contact our office at 1-877-223-4462 or email us at codes@inspectpa.com for further information or just to discuss your needs.

Thank you,

Jeff Remas
Advanced Code Group
www.InspectPA.com
See more
See less

Staggered metal stud sound wall-2 hour rated??

Collapse
X
  • Filter
  • Time
  • Show
Clear All
new posts

  • Staggered metal stud sound wall-2 hour rated??

    I have a new job where i am coming in as the relief pitcher bottom of the 9th, no outs, bases loaded and the star player at bat.

    The contractor who was fired as well as the non-licensed architect created a sound wall out of the following materials
    -6" bottom and top track
    -staggered 4" studs on either side at 16" o.c.
    -(2) layers of 5/8" type "x" sheet rock"

    they thought that the 2 layers is what gave them the 2 hour rating, i had to explain to them that it is the entire assembly that is rated

    I can not find anywhere the ul rating for such a wall that is a min. of two hours

    can someone point me in the right direction to find this information?

    thank you in advance

  • #2
    You can do an equivalency rating for the wall's composition from Chapter 7 [IBC 2006 Section 721]. You do not have to quote UL numbers every time. Yes two layers of Type X sheetrock will give the wall a 2-hour rating. A 2-hour wall using metal studs can go down to 1 5/8” studs. Staggering studs is okay as long as the spacing on each side complies with the spacing for any other rated stud wall. Usually 24” max oc. Look for chase wall types in the UL, USG or other sheetrock manufacturers listings of rated assemblies.
    Chaos, Panic, Disorder.....my work is done here.
    Bureaucracy is a challenge to be conquered with a righteous attitude, the tolerance for stupidity and a bulldozer when necessary.

    Comment


    • #3
      thank you for the quick reply

      Comment


      • #4
        Originally posted by liarchitect View Post
        non-licensed architect
        No such thing.

        Comment


        • #5
          The one hour version is UL U340 in 2000 directory
          Sorry wood studs
          Last edited by hlfireinspector; July 13th, 2011, 09:53.

          Comment


          • #6
            The GA manual has a 2 hour wood stud wall at 16" OC stud spacing (3910) but not metal studs

            http://www.gypsum.org/pdf/GA-600-09_...egs_part1.html

            Comment


            • #7
              Many metal stud walls need to have bridging or straps at mid height in order to resist out oo plane loads. How would you install the bridging if the metal studs are staggered?

              Comment


              • #8
                Originally posted by Mark K View Post
                Many metal stud walls need to have bridging or straps at mid height in order to resist out oo plane loads. How would you install the bridging if the metal studs are staggered?
                No different.

                Especially if using clip angles & channel bridging.

                Comment


                • #9
                  With staggarged metal studs with 2x4 studs on a 6 inch track it is not clear that the prepunched holes in the studs will allow you locate the channel bridging without conflicting with the other offset studs.

                  Comment


                  • #10
                    You can do an equivalency rating for the wall's composition from Chapter 7 [IBC 2006 Section 721]. You do not have to quote UL numbers every time. Yes two layers of Type X sheetrock will give the wall a 2-hour rating.
                    The calculated method of fire-resistance in IBC 721 is limited to a maximum of 1 hour on wood studs (721.6.1.1)!

                    Looks like GA File No. 5060 or 5071 may be consistent with the subject assembly, though each is a proprietary system.
                    Last edited by AegisFPE; July 13th, 2011, 17:03. Reason: Added GA assembly info.
                    www.AEGISengineering.com

                    Comment


                    • #11
                      Originally posted by Mark K View Post
                      ... it is not clear that the prepunched holes in the studs will allow you locate the channel bridging without conflicting with the other offset studs.
                      They won't.

                      The bridging's not expected to go through every stud.

                      Comment


                      • #12
                        Originally posted by brudgers View Post
                        No such thing.
                        information architects and custodial engineers are typically the bain of the licensed A/E world, and usually only carry a driver license at best...but yes, there should be no such thing as a non-licensed architect. without a license you are not a professional architect or engineer. me thinks some laws might have been broken somewhere, somehow on this one.

                        did they stagger the drywall? was there a screw and tape inspection for the first layers? lots of unknowns if already built.

                        Comment