Announcement

Collapse
1 of 2 < >

***Forum Software Change***

Hi folks,

For those of you living under a rock, we have decided to completely change the software platform that this forum is operated by. We continue to strive to provide a high quality, spam free, professional, modern place where those involved in the building code arena can exchange information. We will be swapping to the new software in the next few days. A few more reminders in addition to the several emails that I sent out:

1) You will be required to reset your password. That is just the way it is. You will be prompted initially and there are very obvious links for you to click on for a password reset or reminder.
2) Make sure that your email address is up to date. If you signed up under an email that is no longer in use, we have no way to get a hold of you.
3) The swap is happening and happening soon. All of the log in links and main page will be the same URL so you should not have to create a new one. That part should be seamless.
4) We already changed servers to a faster one last week and unless I told you, you would never know. This is all setting the stage.
5) The forum will look similar but you will have to spend time looking around, figuring out how to do everything. It is a much, much better platform. This is a whine free zone.

***We asked for money to help offset the costs and a few very dedicated people really stepped up to the plate. We fell short of our goal and the costs are more than was estimated. I want to thank those few people that helped us to keep this forum up and running. AS A RESULT of falling short of our goal and the fact that 99.9% of the users did not help, there will be some permission changes happening over the next few weeks. We need everyone to step up and appreciate the value of this forum.

Thank you,

Jeff Remas
Administrator
2 of 2 < >

Plan Review Services

Advanced Code Group (ACG) has been performing plan review services for municipalities, architectural firms, third-party agencies, contractors and code officials for over 10 years with great success and response. We would be happy to assist you with your I-Code plan review needs, whether on a limited or full time basis. Plan review is performed by several experienced inspectors, certified as plan reviewers in different disciplines. We offer expedited plan review services electronically. This has been a well received process that eliminates reprinting of drawings. At the end of plan review, you have the option to accept an electronic stamp on the plans or submit the final, approved drawings for traditional stamping with return via FedEx. Why print, submit then print changes and submit again when this can be done just once?

We will always do our best to work within your budget and allotted timeframe. Feel free to contact our office at 1-877-223-4462 or email us at codes@inspectpa.com for further information or just to discuss your needs.

Thank you,

Jeff Remas
Advanced Code Group
www.InspectPA.com
See more
See less

Penetrations in Fire Walls

Collapse
X
  • Filter
  • Time
  • Show
Clear All
new posts

  • Penetrations in Fire Walls

    2009 IBC
    706.2 Structural stability. Fire walls shall have sufficient structural stability under fire conditions to allow collapse of construction on either side without collapse of the wall for the duration of time indicated by the required fire-resistance rating.

    I have heard this described as requiring the fire wall to be structurally independent, though that isn't the exact wording.

    But section 706.9 allows pentrations per 713, which are basically the same as for any other fire-rated assembly. So, how do you maintain structural independence with building utilities penetrating a fire wall?

    The situation I am looking at deals with a fire wall used as a horizontal exit, and the requirement to provide standpipe connection on either side of the exit. It has been suggested that the pipe supplying the standpipe cannot penetrate the fire wall because that would not meet section 706.2.

    Any thoughts?

  • #2
    1025.2 Separation.
    The separation between buildings or refuge areas connected by a horizontal exit shall be provided by a fire wall complying with Section 706; or it shall be provided by a fire barrier complying with Section 707

    707.5 Continuity.
    Fire barriers shall extend from the top of the floor/ceiling assembly below to the underside of the floor or roof sheathing, slab or deck above and shall be securely attached thereto. Such fire barriers shall be continuous through concealed spaces, such as the space above a suspended ceiling.

    Comment


    • #3
      You will have to pardon my ignorance of building code, but isn't a fire wall different than a fire barrier? Can a fire barrier still be used to create separate buildings?

      Comment


      • #4
        Can a fire barrier still be used to create separate buildings?
        No but it can be used to create a horizontal exit. Do they need to be seperate buildings?

        Comment


        • #5
          I think so. It's a pretty bid building. It's a type V-A, 4-story, with a total area somewhere around 280,000 sq. ft. I think there are 5 separate building areas in the current plan.

          Comment


          • #6
            280,000 sq ft V-A 4 stories

            What is the occupany group?

            It might be cheaper to up the construction Type in lieu of all the structurally independent fire walls 4 stories tall. I don't see how you can accomplish this.

            Comment


            • #7
              It's a large scale apartment complex. Occupancy is mostly group R-2, with some A-3 & B for amenity areas and leasing office. I see quite a few of these, but most are on top of a subterranean parking garage so there isn't really a need to cross the fire walls with the large utilities. This one is on grade and there is a separate parking structure.

              The problem I have is reconciling 706.2 with 706.9. How can penetrations be allowed through the fire wall, and still maintain the structural independence? Is it assumed that by the time the building collapses on one side of the wall, the utility lines are destroyed, or pretty much useless anyway? Does that assumption extend to a standpipe system, that may still be in use when the building collapses?

              Comment


              • #8
                Firewalls don't have to be structurally independent. They just have to be detailed so that if the construction on one side collapses it doesn't pull the fire wall down with it. Two typical ways of doing this are: For a masonry wall with wood joists perpendicular to it, the ends of the joists are fire cut. For a double stud wall with a rated gypsum shaftwall the gypsum board is attached to the wood framing with aluminum clips that melt in a fire.

                Comment


                • #9
                  You will have a hard time finding a drywall shaft wall that can go 4 stories or more than 40 feet...maybe a precast shaft wall (thermacrete).
                  Jake

                  http://www.nwboca.org

                  This response brought to you by one of the paying members of the Building Code Forum.
                  You can join the paying members and support this forum, for a small donation at
                  http://www.thebuildingcodeforum.com/forum/payments.php

                  Comment


                  • #10
                    Originally posted by TJacobs View Post
                    You will have a hard time finding a drywall shaft wall that can go 4 stories or more than 40 feet...maybe a precast shaft wall (thermacrete).
                    USG Area Separation Walls are good for 44'.

                    Setting it on top of a different wall type such as CMU would allow for taller construction.

                    http://www.usg.com/rc/system-catalog...g-en-SA925.pdf

                    Comment


                    • #11
                      Originally posted by Paul Sweet View Post
                      Firewalls don't have to be structurally independent. They just have to be detailed so that if the construction on one side collapses it doesn't pull the fire wall down with it. Two typical ways of doing this are: For a masonry wall with wood joists perpendicular to it, the ends of the joists are fire cut. For a double stud wall with a rated gypsum shaftwall the gypsum board is attached to the wood framing with aluminum clips that melt in a fire.
                      What about the utilities that cross the wall? If a 6" steel pipe crosses the wall, and one side of the building comes down, that 6" pipe is going to do some significant damage on the other side of the wall. I don't think they make any pipe couplings that are made to melt in a fire.

                      Comment


                      • #12
                        Originally posted by RBK View Post
                        I have heard this described as requiring the fire wall to be structurally independent, though that isn't the exact wording.
                        The description you have heard is incorrect.

                        The code says what it says.

                        Comment


                        • #13
                          Originally posted by RBK View Post
                          What about the utilities that cross the wall? If a 6" steel pipe crosses the wall, and one side of the building comes down, that 6" pipe is going to do some significant damage on the other side of the wall. I don't think they make any pipe couplings that are made to melt in a fire.
                          Run the pipe below the wall.

                          Comment


                          • #14
                            Originally posted by RBK View Post
                            What about the utilities that cross the wall? If a 6" steel pipe crosses the wall, and one side of the building comes down, that 6" pipe is going to do some significant damage on the other side of the wall. I don't think they make any pipe couplings that are made to melt in a fire.
                            Then I think the fire wall has done its job and allowed everybody plenty of time to get out of the structure..... after a fire, the firewall would have to be rebuilt anyway.....

                            Really don't see an issue as the firewall is not designed to remain there if the fire has damaged the surface of the wall exposed to the thermal heat of the fire. concrete, gypsum, masonry, or any other building material would be severely affected by the heat exposure because of the removal of water in the construction materials... these material would then become brittle and not have the tensile strength that they had before the fire/heat exposure.
                            Last edited by Builder Bob; August 10th, 2011, 13:43. Reason: typos, grammar, etc.
                            Lost is the south......
                            ******************************
                            Can you build to the minimum standards?

                            Help us by supporting this forum .....If the advice you seek saved you a few bucks, pass on the wealth to this forum

                            http://www.thebuildingcodeforum.com/forum/payments.php

                            FWIW- MCP,CBO,CPE, ASCET, and A BYOB Ga. Dawg Fan!

                            Comment


                            • #15
                              If the fire wall is designed utilizing a UL listed assembly which is a load-bearing wall, then there should be a corresponding assembly for the through penetration firestop system. For example, U921 is listed as a three hour bearing wall. C-AJ-1523 allows for a maximum diameter opening of 7 1/4 inches in a CMU assembly.

                              So, yes, you can have the penetration and still comply with 706.2.
                              This response brought to you by one of the paying members of the Building Code Forum.
                              You can join the paying members and support this forum, for a small donation at http://www.thebuildingcodeforum.com/forum/payments.php