Announcement

Collapse
1 of 2 < >

***Forum Software Change***

Hi folks,

For those of you living under a rock, we have decided to completely change the software platform that this forum is operated by. We continue to strive to provide a high quality, spam free, professional, modern place where those involved in the building code arena can exchange information. We will be swapping to the new software in the next few days. A few more reminders in addition to the several emails that I sent out:

1) You will be required to reset your password. That is just the way it is. You will be prompted initially and there are very obvious links for you to click on for a password reset or reminder.
2) Make sure that your email address is up to date. If you signed up under an email that is no longer in use, we have no way to get a hold of you.
3) The swap is happening and happening soon. All of the log in links and main page will be the same URL so you should not have to create a new one. That part should be seamless.
4) We already changed servers to a faster one last week and unless I told you, you would never know. This is all setting the stage.
5) The forum will look similar but you will have to spend time looking around, figuring out how to do everything. It is a much, much better platform. This is a whine free zone.

***We asked for money to help offset the costs and a few very dedicated people really stepped up to the plate. We fell short of our goal and the costs are more than was estimated. I want to thank those few people that helped us to keep this forum up and running. AS A RESULT of falling short of our goal and the fact that 99.9% of the users did not help, there will be some permission changes happening over the next few weeks. We need everyone to step up and appreciate the value of this forum.

Thank you,

Jeff Remas
Administrator
2 of 2 < >

Plan Review Services

Advanced Code Group (ACG) has been performing plan review services for municipalities, architectural firms, third-party agencies, contractors and code officials for over 10 years with great success and response. We would be happy to assist you with your I-Code plan review needs, whether on a limited or full time basis. Plan review is performed by several experienced inspectors, certified as plan reviewers in different disciplines. We offer expedited plan review services electronically. This has been a well received process that eliminates reprinting of drawings. At the end of plan review, you have the option to accept an electronic stamp on the plans or submit the final, approved drawings for traditional stamping with return via FedEx. Why print, submit then print changes and submit again when this can be done just once?

We will always do our best to work within your budget and allotted timeframe. Feel free to contact our office at 1-877-223-4462 or email us at codes@inspectpa.com for further information or just to discuss your needs.

Thank you,

Jeff Remas
Advanced Code Group
www.InspectPA.com
See more
See less

Church capacity

Collapse
X
  • Filter
  • Time
  • Show
Clear All
new posts

  • Church capacity

    An architect here, 2006 IBC:
    Consider a typical church, which I have in this case. A group of people gather at a time to worship and study. When they study, they are in classrooms throughout the building. When they worship, they are in an assembly room with fixed pews, dutifully seated with one person every 18" (these are really skinny people). There are some occasions when they will also gather for a fellowship dinner. In typical cases, not everyone who comes for worship services will also be there during class time. In fact, during my 39 years of church design, I've seen that most church's have about a 50% to 60% ratio, class to worship proportion. Some churches will average as high as 80% to 90%. We normally see the same pattern with "all church" dinners, in that there are seldom times when everyone will gather for a dinner; the ratio there for many churches is about 50%, but smaller churches actually can approach 100%.
    Now comes my current client. We have an assembly space with seating for 239 at 18" per person. I tabulate each pew individually and round down because if a pew does not fit 8.75 people, I only need to count 8 toward room capacity. When those people go to (or come from) classes, this building has 8 classrooms with a total of 111 capacity, or about 46% of worship attendance. When they fellowship, we have a fellowship hall available the seats 244 (7 sf/person), or about 102% capacity.
    The building official says the occupant load for this building is 239+111+244=594 and must be sprinkled. Logic would say that the people in worship are the same people who attend those classes and eat those dinners, so the maximum load is the 239 or 244, largest room capacity, both under the 300 capacity sprinkler trigger.
    The local zoning regulation for churches requires 1 car per 6 seats, based upon maximum seating capacity. If I use the 244 capacity, then I'm required to provide 41 spaces; I have 60 spaces. If I must use the total number of people with every room filled at once for total occupancy, then using the 1/6 factor, 594 people on site will require 99 cars. If I eliminate the building, I may be able to fit the extra 39 cars, but that would seem to be a Catch-22.

  • #2
    Careful with the parking lot justification, because 60 spaces x 6 occupants each = 360 persons, still over the threshold you are trying to stay under.

    IMHO it seems reasonable that the sanctuary and fellowship hall may not simultaneously be occupied, but it is challenging to exclude simultaneous occupancy of some or all of the classroom spaces based on my experience attending various churches.

    Incidentally, 239 or 244 plus 111 is pretty close to 360!

    Comment


    • #3
      The Code requires worst case scenario of all rooms being occupied at the same time.

      The BO is correct
      A man should look for what is, and not for what he thinks should be.---Albert Einstein
      “Never argue with stupid people, they will drag you down to their level and then beat you with experience.”― Mark Twain

      Comment


      • #4
        The nursery will be the only room used during worship time, so 15 additional at the most, still under 300. The parking lot factor that the city uses here is ridiculous, there won't be 6 people in every car on a Sunday morning; something like 3 people per car is more realistic, so 60 x 3 = 180, which won't even fill the auditorium. Their attendance was as high as 120 after being in existence for about 6 years, now since the tornado, running about 90. Trying to qualify 594 on this site is unreasonable.

        Comment


        • #5
          Visualizing the worst case scenario, how do that many people get there? We aren't allowed on-street parking. Even with a 1/6 car ratio, there is nowhere to put vehicles for 594 people. Also, does that mean that 594 is the number that I'll have to use to calculate toilets also? They were trying to rebuild on an existing slab, using existing plumbing. 300 ladies / 75 will be 4 toilets, we only had two in the pre-tornado structure. (245/2 = 123/75 = 2 toilets)

          Comment


          • #6
            The BO does have the ability to use actual numbers to reduce the OL for design purposes. This is most common in factories but may be used in all occupancies. It is not uncommon for churches and schools to have multiply areas that will not be occupied at the same time. I would be looking at the numbers during Easter and Christmas or other special events to get an actual load versus an average load.

            1004.1.1 Areas without fixed seating.
            The number of occupants shall be computed at the rate of one occupant per unit of area as prescribed in Table 1004.1.1. For areas without fixed seating, the occupant load shall not be less than that number determined by dividing the floor area under consideration by the occupant per unit of area factor assigned to the occupancy as set forth in Table 1004.1.1. Where an intended use is not listed in Table 1004.1.1, the building official shall establish a use based on a listed use that most nearly resembles the intended use.

            Exception: Where approved by the building official , the actual number of occupants for whom each occupied space, floor or building is designed, although less than those determined by calculation, shall be permitted to be used in the determination of the design occupant load .

            Comment


            • #7
              Sorry, repeat post
              Last edited by DwightB; August 19th, 2011, 21:43.

              Comment


              • #8
                Originally posted by AegisFPE View Post
                Careful with the parking lot justification, because 60 spaces x 6 occupants each = 360 persons
                Is there as section in IBC 2006 where building capacity is set according to parking spaces? I'd say no.

                Comment


                • #9
                  No , there isn't. And I agree with Mark, the code assumes fully occupied. But, as pointed out, the BO can look at actual numbers, if you can defend them, and give him something to hang his hat on.
                  Arguing with an inspector is like wrestling with a pig in mud, pretty soon you realize that the pig is enjoying it!

                  This response brought to you by one of the paying members of the Building Code Forum.
                  You can join the paying members and support this forum, for a small donation at
                  http://www.thebuildingcodeforum.com/forum/payments.php

                  Comment


                  • #10
                    Also assume multifunctions. church services and bible classes, meetings, and banquets.
                    A man should look for what is, and not for what he thinks should be.---Albert Einstein
                    “Never argue with stupid people, they will drag you down to their level and then beat you with experience.”― Mark Twain

                    Comment


                    • #11
                      Originally posted by DwightB View Post
                      An architect here, 2006 IBC: Consider a typical church, which I have in this case. A group of people gather at a time to worship and study. When they study, they are in classrooms throughout the building. When they worship, they are in an assembly room with fixed pews, dutifully seated with one person every 18" (these are really skinny people). There are some occasions when they will also gather for a fellowship dinner. In typical cases, not everyone who comes for worship services will also be there during class time. In fact, during my 39 years of church design, I've seen that most church's have about a 50% to 60% ratio, class to worship proportion. Some churches will average as high as 80% to 90%. We normally see the same pattern with "all church" dinners, in that there are seldom times when everyone will gather for a dinner; the ratio there for many churches is about 50%, but smaller churches actually can approach 100%. Now comes my current client. We have an assembly space with seating for 239 at 18" per person. I tabulate each pew individually and round down because if a pew does not fit 8.75 people, I only need to count 8 toward room capacity. When those people go to (or come from) classes, this building has 8 classrooms with a total of 111 capacity, or about 46% of worship attendance. When they fellowship, we have a fellowship hall available the seats 244 (7 sf/person), or about 102% capacity. The building official says the occupant load for this building is 239+111+244=594 and must be sprinkled. Logic would say that the people in worship are the same people who attend those classes and eat those dinners, so the maximum load is the 239 or 244, largest room capacity, both under the 300 capacity sprinkler trigger. The local zoning regulation for churches requires 1 car per 6 seats, based upon maximum seating capacity. If I use the 244 capacity, then I'm required to provide 41 spaces; I have 60 spaces. If I must use the total number of people with every room filled at once for total occupancy, then using the 1/6 factor, 594 people on site will require 99 cars. If I eliminate the building, I may be able to fit the extra 39 cars, but that would seem to be a Catch-22.
                      Sorry, but this is absolutely inexcusable.

                      If you have been designing churches for 29 years using such logic, then you have been doing it wrong for a really long time.

                      And the code compliant solution is to separate the sanctuary into its own fire area.
                      v

                      Comment


                      • #12
                        A judjment call is always allowed
                        such as a school - Classroom 1 student - cafeteria - 1 student at lunch
                        gym 1 student at recess - library 1 student at reading - auditorium 1 student at assembly

                        1 student 5 places or 5 places for 1 student
                        I apply the first for items like plumbing fixtures but each place provides egress
                        when Boca dissapeared so did non- simultaneous occupancy but it come down to use and occupancy

                        Comment


                        • #13
                          Regarding parking capacity limiting occupancy--many churches around here operate church buses to bring in those who cannot drive and to alliviate inadequate parking lots by shuttling from nearby shopping centers, there are also those who walk and those who bike especially in urban areas.

                          Comment


                          • #14
                            The only thing regarding parking in the codes is the amount of ADA require! Parking in most case is a zoning issue. Occupancy load is based on use and function of space.

                            Comment


                            • #15
                              I've never seen a buildings occupant load calculated on how many parking spaces it had. I agree with the bo on this. Assume all rooms occupied. You never know how the building will be used once complete, maybe they have a large and active congregation.



                              Noah webster wrote the dictionary, daniel webster was a statesmen

                              Comment

                              Working...
                              X