Advanced Code Group (ACG) has been performing plan review services for municipalities, architectural firms, third-party agencies, contractors and code officials for over 10 years with great success and response. We would be happy to assist you with your I-Code plan review needs, whether on a limited or full time basis. Plan review is performed by several experienced inspectors, certified as plan reviewers in different disciplines. We offer expedited plan review services electronically. This has been a well received process that eliminates reprinting of drawings. At the end of plan review, you have the option to accept an electronic stamp on the plans or submit the final, approved drawings for traditional stamping with return via FedEx. Why print, submit then print changes and submit again when this can be done just once?

We will always do our best to work within your budget and allotted timeframe. Feel free to contact our office at 1-877-223-4462 or email us at codes@inspectpa.com for further information or just to discuss your needs.

Thank you,

Jeff Remas
Advanced Code Group
www.InspectPA.com
See more
See less

Meter separation distance

Collapse
X
  • Filter
  • Time
  • Show
Clear All
new posts

  • Meter separation distance

    2009 IBC / NEC 2008
    Pennsylvania

    A customer would like to relocate the electric meter next to the gas meter. I'm not familiar with electrical codes at all. Is there a minimum distance per the electrical code to keep the electric meter away from the gas meter / service?

    Thanks in advance.
    I love making up my own code interpretations, don't you?

    I am a plan submitter, not a plan reviewer.

  • #2
    Usually the power company wants 3 feet from the venting on the pressure regulator......I do not know if there is a particular code section on this one.....I've looked for it residentially and not found it...never had the problem commercially.....
    Boy it's hot!.....And where are we going in this handbasket?

    Comment


    • #3
      Requirements are usually from electric co and/or gas co. I would make 2 phone calls.

      Comment


      • #4
        Southern California Edison require minimun 24" seperation between panel & gas meter.

        Comment


        • #5
          The NEC does not have any distance requirements for electric meters. This requirement will come from the utility companies.

          Questar Gas requires 3' of separation from the gas meter and the electrical meter in my area.

          Chris

          Comment


          • #6
            Yup......local service providers requirements.
            Arguing with an inspector is like wrestling with a pig in mud, pretty soon you realize that the pig is enjoying it!

            This response brought to you by one of the paying members of the Building Code Forum.
            You can join the paying members and support this forum, for a small donation at
            http://www.thebuildingcodeforum.com/forum/payments.php

            Comment


            • #7
              Thanks everyone!!!!
              I love making up my own code interpretations, don't you?

              I am a plan submitter, not a plan reviewer.

              Comment


              • #8
                Our gas supplier measures to the edge of the enclosure instead of the source of ignition.
                See if the gas supplier will allow piping the regulator vent opening if not otherwise feasible; IFGC 410.3.1

                Gas meters shall be located at least three (3) feet (0.9 m) from sources of ignition. [NFPA 54:5.7.2.3]

                ACCESS TO VIRGINIA CODES: 2009& 2012 Virginia Codes

                Comment


                • #9
                  From the 2006 IFGC:
                  Section 101.2.4 Systems and equipment outside the scope.

                  This code shall not apply to the following:
                  1. Portable LP-gas equipment of all types that is not connected to a fixed
                  fuel piping system.
                  2. Installation of farm equipment such as brooders, dehydrators, dryers
                  and irrigation equipment.
                  3. Raw material (feedstock) applications except for piping to special
                  atmosphere generators.
                  4. Oxygen-fuel gas cutting and welding systems.
                  5. Industrial gas applications using gases such as acetylene and acetylenic
                  compounds, hydrogen, ammonia, carbon monoxide, oxygen and nitrogen.
                  6. Petroleum refineries, pipeline compressor or pumping stations, loading
                  terminals, compounding plants, refinery tank farms and natural gas
                  processing plants.
                  7. Integrated chemical plants or portions of such plants where flammable
                  or combustible liquids or gases are produced by, or used in, chemical
                  reactions.
                  8. LP-gas installations at utility gas plants.
                  9. Liquefied natural gas (LNG) installations.
                  10. Fuel gas piping in power and atomic energy plants.
                  11. Proprietary items of equipment, apparatus or instruments such as
                  gas-generating sets, compressors and calorimeters.
                  12. LP-gas equipment for vaporization, gas mixing and gas manufacturing.
                  13. Temporary LP-gas piping for buildings under construction or renovation
                  that is not to become part of the permanent piping system.
                  14. Installation of LP-gas systems for railroad switch heating.
                  15. Installation of hydrogen gas, LP-gas and compressed natural gas
                  (CNG) systems on vehicles.
                  16. Except as provided in Section 401.1.1, gas piping, meters, gas pressure
                  regulators and other appurtenances used by the serving gas supplier
                  in the distribution of gas, other than undiluted LP-gas.
                  17. Building design and construction, except as specified herein.
                  18. Piping systems for mixtures of gas and air within the flammable range
                  with an operating pressure greater than 10 psig (69 kPa gauge).
                  19. Portable fuel cell appliances that are neither connected to a fixed
                  piping system nor interconnected to a power grid.



                  It's up to the gas supplier to determine their location.


                  .
                  Please pray for Wilson ("Daddy-O") and his family!


                  Comment


                  • #10
                    FV....I think NFPA 54 also has an exception for utility meters ( like IFGC per GT)....at least our version (1994 I think)....
                    Boy it's hot!.....And where are we going in this handbasket?

                    Comment


                    • #11
                      Steveray

                      Iím not sure either; I usually place a call to our gas company for verification.

                      Expanding on my reply to the OP where having a working relationship with the gas supplier and their existing gas meter may offer this option of vent piping the regulator opening away from sources of ignition such as electrical cabs, heat pumps/AC units etc., within the 3 ft. area. Iím not completely familiar with sections of NFPA 54 but apparently it may allow the provision to pipe the vent opening elsewhere since they have their meters inside buildings.

                      Too often this situation happens after the fact since apparently the POCO field personnel and the electricians are not aware of this gas code. If we can catch this before hand and conclude there is not another safe and feasible option available; discuss the situation with the gas company to agree that the exception does not become the rule.
                      ACCESS TO VIRGINIA CODES: 2009& 2012 Virginia Codes

                      Comment


                      • #12
                        Mark handler provided this link, pretty good info

                        Puget sound

                        pc1

                        Comment


                        • #13
                          http://www.inspectpa.com/forum/showt...ation-Distance
                          ďNever argue with stupid people, they will drag you down to their level and then beat you with experience.Ē― Mark Twain