    2009 IRC Smokes and Carbon Monoxide Alarms Requiements

    The 2009 IRC states:
    R314.3.1 Alterations, repairs and additions. When alterations,
    repairs or additions requiring a permit occur, or when
    one or more sleeping rooms are added or created in existing
    dwellings, the individual dwelling unit shall be equipped with
    smoke alarms located as required for new dwellings.

    Exceptions:
    1. Work involving the exterior surfaces of dwellings,
    such as the replacement of roofing or siding, or the
    addition or replacement of windows or doors, or the
    addition of a porch or deck, are exempt from the
    requirements of this section.

    2. Installation, alteration or repairs of plumbing or
    mechanical systems are exempt from the requirements
    of this section.


    The requirement of a permit kicks in the requirement of CM alarms if the existing structure has an attached garage OR has fuel fired appliances and SD's.

    SO this small addition of a sun room that started out with just one circuit for lights and outlets now requires installation of hardwired SD's to current code, one inside every bedroom and centrally located outside of the bedrooms, PLUS CM alarms in the vicinity of the bedrooms.

    Now the question. On exception 1 would you require SD per the code AND CM alarms when a Sun Room is being constructed?

    We are saying yes....It is an enclosed addition with windows and doors.
    Mule
    Building Official
    Texas

    Built to Code = Building the worst that the code will allow!

  2. #2
    Sawhorse mtlogcabin's Avatar
    Join Date
    Oct 2009
    Location
    Big Sky Country
    Posts
    4,403
    Thanks
    58
    Thanked 524 Times in 415 Posts
    Now the question. On exception 1 would you require SD per the code AND CM alarms when a Sun Room is being constructed?

    We are saying yes....It is an enclosed addition with windows and doors.
    ........................
    Interesting non-lethal, yet legal Self Defense Products available on the market. Feel free to check out this web page , then share with family/friends.
    It is nice to know there are some options offered to protect our loved ones. You may also contact via web page link with any questions, or message me.
    www.mydamselpro.net/graceclawson

  3. #3
    Administrator RJJ's Avatar
    Join Date
    Oct 2009
    Location
    about 1' east of the white water
    Posts
    2,778
    Thanks
    3
    Thanked 61 Times in 51 Posts
    YA! YA! I agree.

  4. #4
    Platinum Member
    Join Date
    Nov 2009
    Location
    state of jefferson
    Posts
    1,044
    Thanks
    17
    Thanked 39 Times in 32 Posts
    so do i, but the fruit and nut state deleted that exception.

  5. #5
    Sawhorse rktect 1's Avatar
    Join Date
    Oct 2009
    Location
    Illinois
    Posts
    730
    Thanks
    9
    Thanked 32 Times in 21 Posts
    It was worse in the 2006 codes.

    But yes, a sunroom (addition) would and has had me tell homeowners to upgrade the entire house.
    Less is only more where more is no good. - FLW

    Currently using 2006 ICC code cycle.

  6. #6
    Platinum Member
    Join Date
    Oct 2009
    Location
    alabama
    Posts
    3,709
    Thanks
    24
    Thanked 212 Times in 182 Posts
    Smoke alarms located as required for new dwellings
    There is nothing about CM detectors.

    And there is nothing about the installation being per the requirements of new construction.

    Battery operated smoke detectors can be placed at the required locations and meet the letter of the code.

    But I can understand how actually reading the code is not as much fun as jumping to conclusions and making homeowners dance for one's amusement.

  7. #7
    Moderator Mule's Avatar
    Join Date
    Oct 2009
    Location
    Texas
    Posts
    1,520
    Thanks
    20
    Thanked 59 Times in 48 Posts
    Quote Originally Posted by brudgers View Post
    There is nothing about CM detectors.

    And there is nothing about the installation being per the requirements of new construction.

    Battery operated smoke detectors can be placed at the required locations and meet the letter of the code.

    But I can understand how actually reading the code is not as much fun as jumping to conclusions and making homeowners dance for one's amusement.
    The only way you can use battery operated smokes is if you have to tear into a wall to provide interlocking of the smokes. If there is an attic or basement then they must be hardwired.

    R314.4 Power source. Smoke alarms shall receive their primary
    power from the building wiring when such wiring is
    served from a commercial source, and when primary power is
    interrupted, shall receive power from a battery.Wiring shall be
    permanent and without a disconnecting switch other than those
    required for overcurrent protection. Smoke alarms shall be
    interconnected.
    Exceptions:
    1. Smoke alarms shall be permitted to be battery operated
    when installed in buildings without commercial
    power.
    2. Interconnection and hard-wiring of smoke alarms in
    existing areas shall not be required where the alterations
    or repairs do not result in the removal of interior
    wall or ceiling finishes exposing the structure,
    unless there is an attic, crawl space or basement available
    which could provide access for hard wiring and
    interconnection without the removal of interior finishes.


    and yes there are requirements for CM's.
    R315.2 Where required in existing dwellings. Where work
    requiring a permit occurs in existing dwellings that have
    attached garages or in existing dwellings within which
    fuel-fired appliances exist, carbon monoxide alarms shall be
    provided in accordance with Section R315.1.
    Mule
    Building Official
    Texas

    Built to Code = Building the worst that the code will allow!

  8. #8
    Sawhorse rktect 1's Avatar
    Join Date
    Oct 2009
    Location
    Illinois
    Posts
    730
    Thanks
    9
    Thanked 32 Times in 21 Posts
    That isn't what my 2006 building code shows. Battery operated only works if no commercial power.

    And the state requires the CM detector.
    Less is only more where more is no good. - FLW

    Currently using 2006 ICC code cycle.

  9. #9
    Platinum Member
    Join Date
    Oct 2009
    Location
    alabama
    Posts
    3,709
    Thanks
    24
    Thanked 212 Times in 182 Posts
    From R313.3 Smoke alarms shall be permitted to be battery operated when installed in buildings without commercial power or in buildings that undergo alterations repairs or additions regulated by Section R313.2.1.


    Last edited by brudgers; March 8th, 2011 at 21:57.

  10. #10
    Platinum Member
    Join Date
    Oct 2009
    Location
    The Empire State
    Posts
    1,544
    Thanks
    376
    Thanked 43 Times in 39 Posts
    R313.2.1 Design and installation. Automatic residential fire sprinkler systems shall be designed and installed in accordance with Section P2904 or NFPA 13D.
    "I'll show that darned Code Official! Thinks he can make ME put in hard-wired smoke detectors, does he? I'll just put in a sprinkler system instead! That'll show HIM a thing or two." Good call Ben! LOL

  11. #11
    Platinum Member
    Join Date
    Oct 2009
    Location
    alabama
    Posts
    3,709
    Thanks
    24
    Thanked 212 Times in 182 Posts
    Come back to the issue.

    Requiring hardwired smoke alarms when someone screens in a porch is asinine.

  12. #12
    Sawhorse Francis Vineyard's Avatar
    Join Date
    Jan 2010
    Location
    Charlottesville, VA
    Posts
    1,550
    Thanks
    174
    Thanked 206 Times in 161 Posts
    Quote Originally Posted by brudgers View Post
    Come back to the issue.

    Requiring hardwired smoke alarms when someone screens in a porch is asinine.
    Agreed, "or the addition of windows . . . or the addition of a porch"; sprinklers required on alterations, repairs and additions might be next.
    Last edited by Francis Vineyard; March 9th, 2011 at 06:04. Reason: still confused
    Thanks for clicking on the advertisers to help keep the website free to all users.

    ACCESS TO VIRGINIA CODES: 2009 Commonwealth of Virginia Codes

  13. #13
    Sawhorse
    Join Date
    Nov 2009
    Location
    West of the river CT
    Posts
    2,476
    Thanks
    389
    Thanked 167 Times in 156 Posts
    We kinda follow Brudgers approach...(with a little less drama) new habitable space, 3-season, living type space...yes,...decks and unenclosed porches no...interior remodel, yes...CT pushes the locations....but not the hardwiring (fishing of wiring) if it would be a large expense compared to the job cost....
    Please support Jim Brown, Deputy Building Official from Gillette, Wyoming for ICC Board of Directors.
    My questions and answers are based on some bastardized hodge podge starting with the 2003 I-codes amended by the state of CT in 2005 and 2009 including the 2005 NEC ....and as of today.....The 2011 Connecticut Amendments to the 2009 International Energy Conservation Code portion of the 2005 State Building Code has been posted to the State Building Inspector’s website

  14. #14
    Sawhorse rktect 1's Avatar
    Join Date
    Oct 2009
    Location
    Illinois
    Posts
    730
    Thanks
    9
    Thanked 32 Times in 21 Posts
    Quote Originally Posted by brudgers View Post
    From R313.3 Smoke alarms shall be permitted to be battery operated when installed in buildings without commercial power or in buildings that undergo alterations repairs or additions regulated by Section R313.2.1.


    EXACTLY. So now go read R313.2.1 and in this section, where you can not get access into the crawl or attic, in those places required to have smoke detectors, you can put in battery operated smoke detectors.
    Less is only more where more is no good. - FLW

    Currently using 2006 ICC code cycle.

  15. #15
    Sawhorse rktect 1's Avatar
    Join Date
    Oct 2009
    Location
    Illinois
    Posts
    730
    Thanks
    9
    Thanked 32 Times in 21 Posts
    Quote Originally Posted by brudgers View Post
    Come back to the issue.

    Requiring hardwired smoke alarms when someone screens in a porch is asinine.
    I agree. And when this village amends this section of the code, or ICC changes its mind, I will follow it to the letter. Until then, I enforce this code section, as it is written.
    Less is only more where more is no good. - FLW

    Currently using 2006 ICC code cycle.

  16. #16
    Moderator Mule's Avatar
    Join Date
    Oct 2009
    Location
    Texas
    Posts
    1,520
    Thanks
    20
    Thanked 59 Times in 48 Posts
    Quote Originally Posted by brudgers View Post
    Come back to the issue.

    Requiring hardwired smoke alarms when someone screens in a porch is asinine.
    I agree. However in my opinion by screening in a porch that would not initiate the requirements. See Exception 1 of R314.3.1.

    Now if you make that porch a room then yes you would need to meet the requirements of the 2009 IRC. You have to look at emergency egress (enclosure blocking bedroom egress windows), electrical and other life health safety issues. And of course....is the addition "GREEN"?
    Mule
    Building Official
    Texas

    Built to Code = Building the worst that the code will allow!

  17. #17
    Sawhorse Yankee's Avatar
    Join Date
    Mar 2010
    Location
    New England
    Posts
    1,341
    Thanks
    59
    Thanked 44 Times in 37 Posts
    Quote Originally Posted by rktect 1 View Post
    EXACTLY. So now go read R313.2.1 and in this section, where you can not get access into the crawl or attic, in those places required to have smoke detectors, you can put in battery operated smoke detectors.
    You can snake building power off of an existing circuit in the bedroom up to 4" below ceiling without disrupting the finish material, so your alarm will be hardwired. Then you can use wireless technology for the "interconnected" part. The "interconnected" is the difficulty with wiring the units together in a renovation without attic space.

  18. #18
    Sawhorse
    Join Date
    Oct 2009
    Location
    metro DC
    Posts
    2,801
    Thanks
    13
    Thanked 69 Times in 62 Posts
    stupid requirement, maybe... Code.. well.. yes.

    The only place you may be able to wiggle out of hardwired smoke detectors is the main level of a house (which is probably where the kitchen is)..

    Don't know about you.. with the way I cook... that's the most likely place for a fire/smoldering issues to occur (just did hydro inspection at a senior living facility - the resident of one unit was no where to be found.. but something was cooking on the stove). Contractor turned the stove off.. just sayin'
    (PE)ach
    some days are just that..

  19. #19
    Platinum Member
    Join Date
    Nov 2009
    Location
    state of jefferson
    Posts
    1,044
    Thanks
    17
    Thanked 39 Times in 32 Posts
    stupid ,stupid, stupid! permit for $1,200 worth the roof covering damage and i informed the roofer of the co and smoke alarm requirement. lots of insults and expletives later i told him to write his legislatures and i'm only serving him up the plate of $hit i was handed. sucks to be me sometimes! thanks icc and california building standards commission

  20. #20
    Sawhorse Francis Vineyard's Avatar
    Join Date
    Jan 2010
    Location
    Charlottesville, VA
    Posts
    1,550
    Thanks
    174
    Thanked 206 Times in 161 Posts
    Quote Originally Posted by pwood View Post
    told him to write his legislatures
    Good Advice, Virginia deleted Sections R314.3.1 & R315.2.
    Last edited by Francis Vineyard; March 10th, 2011 at 17:35. Reason: change font