    Depending on the terminology you use, where in the IRC does it address the number of supports under a header?
    If a header spans 3 foot or 12 foot or any other length, is there a section in the IRC that addresses the number of cripples required under that header?
    Figure 602.3(2) shows a drawing that defines different components and gives sections relating to certain ones, but nothing addresses the trimmers.

  2. #2
    Sawhorse mtlogcabin's Avatar
    Join Date
    Oct 2009
    Location
    Big Sky Country
    Posts
    5,427
    Thanks
    85
    Thanked 840 Times in 665 Posts
    TABLE R502.5(1)
    GIRDER SPANSa AND HEADER SPANSa FOR EXTERIOR BEARING WALLS
    (Maximum spans for Douglas fir-larch, hem-fir, southern pine and spruce-pine-firb and required number of jack studs)

  3. The Following 2 Users Say Thank You to mtlogcabin For This Useful Post:

    High Desert (May 5th, 2011), Pcinspector1 (May 5th, 2011)

  4. #3
    Gold Member
    Join Date
    Oct 2009
    Location
    Oregon
    Posts
    888
    Thanks
    23
    Thanked 61 Times in 48 Posts
    I knew that someone named mtlogcabin would know about wood!

  5. #4
    Platinum Member
    Join Date
    Oct 2009
    Location
    MID WEST
    Posts
    1,486
    Thanks
    223
    Thanked 49 Times in 44 Posts
    We call them cripples or trimmers in these parts!

    mtlogcabin is on his game! R502.5(1)

    pc1
    Last edited by Pcinspector1; May 5th, 2011 at 16:29.

  6. #5
    Sawhorse
    Join Date
    Oct 2009
    Location
    metro DC
    Posts
    2,826
    Thanks
    13
    Thanked 74 Times in 66 Posts
    should be in chapter 6, too.. but you'll find the requirements in chapter 5

    so............... why isn't it in the wall section too.. (that's where I would look for it if I hadn't already been beaten into submission)
    (PE)ach
    some days are just that..

  7. #6
    Sawhorse
    Join Date
    Nov 2009
    Location
    West of the river CT
    Posts
    3,615
    Thanks
    602
    Thanked 306 Times in 289 Posts
    Yep...MT nailed it.....I usually tell the contractors that if they want to go rule of thumb.....6' double jacks....but depends on what you hold up....

    I feel the same way peach....
    Boy it's hot!.....And where are we going in this handbasket?

  8. #7
    Sawhorse mtlogcabin's Avatar
    Join Date
    Oct 2009
    Location
    Big Sky Country
    Posts
    5,427
    Thanks
    85
    Thanked 840 Times in 665 Posts
    2009 IRC
    Chapter 6 refers you to chapter 5. Maybe it is in 5 because as you start up with a house the floors would be the first place a header maybe required
    Wood Framing
    R602.3 Design and construction.
    Exterior walls of wood-frame construction shall be designed and constructed in accordance with the provisions of this chapter and Figures R602.3(1) and R602.3.(2) or in accordance with AF&PA's NDS. Components of exterior walls shall be fastened in accordance with Tables R602.3(1) through R602.3(4). Structural wall sheathing shall be fastened directly to structural framing members. Exterior wall coverings shall be capable of resisting the wind pressures listed in Table R301.2(2) adjusted for height and exposure using Table R301.2(3). Wood structural panel sheathing used for exterior walls shall conform to the requirements of Table R602.3(3).
    Studs shall be continuous from support at the sole plate to a support at the top plate to resist loads perpendicular to the wall. The support shall be a foundation or floor, ceiling or roof diaphragm or shall be designed in accordance with accepted engineering practice.

    Exception: Jack studs, trimmer studs and cripple studs at openings in walls that comply with Tables R502.5(1) and R502.5(2).

    Metal framing
    R603.7 Jack and king studs.
    The number of jack and king studs installed on each side of a header shall comply with Table R603.7(1). King, jack and cripple studs shall be of the same dimension and thickness as the adjacent wall studs. Headers shall be connected to king studs in accordance with Table R603.7(2) and the following provisions:

  9. #8
    Platinum Member
    Join Date
    Oct 2009
    Location
    alabama
    Posts
    3,713
    Thanks
    24
    Thanked 216 Times in 185 Posts
    Quote Originally Posted by Pcinspector1 View Post
    We call them cripples or trimmers in these parts!

    mtlogcabin is on his game! R502.5(1)

    pc1
    Cripples are the short studs above or below an opening.

    Here's a video showing cripple headers:

    http://www.youtube.com/watch?v=7Ynu0...feature=relmfu

  10. #9
    Sawhorse
    Join Date
    Nov 2009
    Posts
    789
    Thanks
    0
    Thanked 26 Times in 25 Posts
    your sick...........

  11. #10
    Platinum Member
    Join Date
    Oct 2009
    Location
    alabama
    Posts
    3,713
    Thanks
    24
    Thanked 216 Times in 185 Posts
    Quote Originally Posted by Rick18071 View Post
    your sick...........
    Yes.

    You have no idea how long it took me to find that video after the image came to me.

  12. The Following User Says Thank You to brudgers For This Useful Post:

    ICE (October 12th, 2011)

  13. #11
    Sawhorse ICE's Avatar
    Join Date
    Jun 2011
    Location
    A concrete jungle near you.
    Posts
    5,698
    Thanks
    192
    Thanked 459 Times in 370 Posts
    Any time I need a good laugh I come here. When I am done laughing I have the realization that life isn't all that bad. Seeing those kids having fun I think that I may never have anything to complain about that really matters.

    So what's so damned funny about it? Well for starters is the fact that you thought of it. Then doing it. Only one person replied after that and all he said was, "You're sick." To which you replied "Yes and I had to work for it."

    This is classic stuff for a forum.

    Tiger
    1...2...3...4...5...6...7....8...9...10...11...12...Finally not another damned song

    Tigerloose

Bookmarks


Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •