    I guess things come in spurts. Lately, I have been getting questioned about a "requirement" for GFCI receptacle "within 24 inches of kitchen sinks. As I grow older I have a tendency to jump to assumptions concerning codes; based on memory (lose?). Ok, here it is. There is NO code requirement for a kitchen countertop receptacle within 24 inches of a kitchen sink.
    It isn't what we don't know that causes most of our problems; it's what we do know that ain't so.

  2. #2
    Sawhorse
    Join Date
    Nov 2009
    Location
    West of the river CT
    Posts
    2,884
    Thanks
    432
    Thanked 215 Times in 203 Posts
    E3801.4.1 Wall counter space.

    A receptacle outlet shall be installed at each wall counter space 12 inches (305 mm) or wider. Receptacle outlets shall be installed so that no point along the wall line is more than 24 inches (610 mm), measured horizontally from a receptacle outlet in that space.

    I think that is what gets you there UB.....
    Please support Jim Brown, Deputy Building Official from Gillette, Wyoming for ICC Board of Directors.
    My questions and answers are based on some bastardized hodge podge starting with the 2003 I-codes amended by the state of CT in 2005 and 2009 including the 2005 NEC ....and as of today.....The 2011 Connecticut Amendments to the 2009 International Energy Conservation Code portion of the 2005 State Building Code has been posted to the State Building Inspector’s website

  3. #3
    Administrator jar546's Avatar
    Join Date
    Oct 2009
    Location
    33446
    Posts
    4,704
    Blog Entries
    15
    Thanks
    167
    Thanked 299 Times in 178 Posts
    Items for Sale
    Yes, 24" is a requirement from all edges including sinks, ranges, etc. Basically at not point along the kitchen counter can you be more than 24" from a receptacle. Kitchen appliances cords are 24"
    Admin

  4. #4
    Sawhorse Builder Bob's Avatar
    Join Date
    Oct 2009
    Location
    Sunny SC - Coastal (not Charleston or Myrtle Beach)
    Posts
    1,280
    Thanks
    45
    Thanked 107 Times in 87 Posts
    E3801.4 Countertop receptacles. In kitchens and dining rooms of dwelling units, receptacle outlets for counter spaces
    shall be installed in accordance with Sections E3801.4.1
    through E3801.4.5 (see Figure E3801.4).

    E3801.4.1Wall counter space. A receptacle outlet shall be installed at each wall counter space 12 inches (305 mm) or
    wider. Receptacle outlets shall be installed so that no point along the wall line is more than 24 inches (610 mm), measured
    horizontally from a receptacle outlet in that space.
    Exception: Receptacle outlets shall not be required on a wall directly behind a range or sink in the installation
    described in Figure E3801.4.1.

    This is from the 2006 IRC..... you are correct that a GFCI receptacle is not required 24 inches from the sink.... however, no point on the counter top shall a receptacle be more than 24 inches from another receptacle.
    Lost is the south......
    ******************************
    Can you build to the minimum standards?

    Help us by supporting this forum .....If the advice you seek saved you a few bucks, pass on the wealth to this forum

    http://www.thebuildingcodeforum.com/forum/payments.php

    FWIW- MCP,CBO,CPE, ASCET, and A BYOB Ga. Dawg Fan!

  5. #5
    Sawhorse ICE's Avatar
    Join Date
    Jun 2011
    Location
    A concrete jungle near you.
    Posts
    4,797
    Thanks
    144
    Thanked 295 Times in 240 Posts
    Maybe this is what you are remembering.
    NEC
    552.41 Receptacle Outlets Required.
    (B) Location. Receptacle outlets shall be installed as
    follows:
    (1) Adjacent to countertops in the kitchen [at least one on
    each side of the sink if countertops are on each side
    and are 300 mm (12 in.) or over in width]
    Last edited by ICE; May 22nd, 2013 at 12:08.

  6. #6
    Silver Member
    Join Date
    Nov 2009
    Posts
    125
    Thanks
    37
    Thanked 26 Times in 20 Posts
    Quote Originally Posted by Builder Bob View Post
    E3801.4 Countertop receptacles. In kitchens and dining rooms of dwelling units, receptacle outlets for counter spaces
    shall be installed in accordance with Sections E3801.4.1
    through E3801.4.5 (see Figure E3801.4).

    E3801.4.1Wall counter space. A receptacle outlet shall be installed at each wall counter space 12 inches (305 mm) or
    wider. Receptacle outlets shall be installed so that no point along the wall line is more than 24 inches (610 mm), measured
    horizontally from a receptacle outlet in that space.

    Exception: Receptacle outlets shall not be required on a wall directly behind a range or sink in the installation
    described in Figure E3801.4.1.

    This is from the 2006 IRC..... you are correct that a GFCI receptacle is not required 24 inches from the sink.... however, no point on the counter top shall a receptacle be more than 24 inches from another receptacle.
    Not quite right. Receptacle outlets are to be spaced not more than 48" O.C. This results in no point on the counter top being more than 24" from a (GFCI protected ) receptacle outlet, including the edge of the sink.

  7. #7
    Sawhorse Uncle Bob's Avatar
    Join Date
    Oct 2009
    Location
    Texas
    Posts
    1,402
    Thanks
    9
    Thanked 57 Times in 35 Posts
    Thanks ya'll,

    This came up several time when a kitchen sink was either on an island or a peninsular. I'm told that "the big city" requires gfci receptacles within 24 inches if the sink and I tell them there is no such animal. If there is not a "wall line" there is no requirement for GFCI receptacle. So, the electricians are hard pressed sometimes to find a location on the island or *****ular within 24" of the sink. It is just not required. The confusion comes with "no space along the wall shall be more than 24" from a receptacle. No wall, no requirement other than one receptacle required on island and peninsulars; but not within 24" of sink.

    Thanks for sharing,

    Uncle Bob
    It isn't what we don't know that causes most of our problems; it's what we do know that ain't so.

  8. #8
    Administrator jar546's Avatar
    Join Date
    Oct 2009
    Location
    33446
    Posts
    4,704
    Blog Entries
    15
    Thanks
    167
    Thanked 299 Times in 178 Posts
    Items for Sale
    Quote Originally Posted by Builder Bob View Post
    E3801.4 Countertop receptacles. In kitchens and dining rooms of dwelling units, receptacle outlets for counter spaces
    shall be installed in accordance with Sections E3801.4.1
    through E3801.4.5 (see Figure E3801.4).

    E3801.4.1Wall counter space. A receptacle outlet shall be installed at each wall counter space 12 inches (305 mm) or
    wider. Receptacle outlets shall be installed so that no point along the wall line is more than 24 inches (610 mm), measured
    horizontally from a receptacle outlet in that space.
    Exception: Receptacle outlets shall not be required on a wall directly behind a range or sink in the installation
    described in Figure E3801.4.1.

    This is from the 2006 IRC..... you are correct that a GFCI receptacle is not required 24 inches from the sink.... however, no point on the counter top shall a receptacle be more than 24 inches from another receptacle.
    That is not correct.
    Admin

  9. #9
    Sawhorse
    Join Date
    Nov 2009
    Location
    West of the river CT
    Posts
    2,884
    Thanks
    432
    Thanked 215 Times in 203 Posts
    UB.....if there is 12" on either side of the sink, it needs an outlet......


    E3801.4.2 Island counter spaces.

    At least one receptacle outlet shall be installed at each island counter space with a long dimension of 24 inches (610 mm) or greater and a short dimension of 12 inches (305 mm) or greater.
    Please support Jim Brown, Deputy Building Official from Gillette, Wyoming for ICC Board of Directors.
    My questions and answers are based on some bastardized hodge podge starting with the 2003 I-codes amended by the state of CT in 2005 and 2009 including the 2005 NEC ....and as of today.....The 2011 Connecticut Amendments to the 2009 International Energy Conservation Code portion of the 2005 State Building Code has been posted to the State Building Inspector’s website

  10. #10
    Sawhorse Uncle Bob's Avatar
    Join Date
    Oct 2009
    Location
    Texas
    Posts
    1,402
    Thanks
    9
    Thanked 57 Times in 35 Posts
    Quote Originally Posted by steveray View Post
    UB.....if there is 12" on either side of the sink, it needs an outlet......


    E3801.4.2 Island counter spaces.

    At least one receptacle outlet shall be installed at each island counter space with a long dimension of 24 inches (610 mm) or greater and a short dimension of 12 inches (305 mm) or greater.
    The above does not require the receptacle to be within 24" of the sink; only that a receptacle is required for an Island (sink or no sink). If you have a 4ft wide by 4 ft deep island; there is no requirement that the "required receptacle" be within 24 " of the sink. Also if the island is 8' or even 10' wide; there is a requirement for "only one receptacle" and it is not required to be within 24" of the sink if one is there.
    Last edited by Uncle Bob; May 22nd, 2013 at 17:02.
    It isn't what we don't know that causes most of our problems; it's what we do know that ain't so.

  11. #11
    Administrator jar546's Avatar
    Join Date
    Oct 2009
    Location
    33446
    Posts
    4,704
    Blog Entries
    15
    Thanks
    167
    Thanked 299 Times in 178 Posts
    Items for Sale

    Kitchen countertop receptacle near sink?

    The OP was not about an island sink, correct? We are now discussing 2 different tooics


    Sent from my iPhone using Tapatalk
    Admin

  12. #12
    Platinum Member
    Join Date
    Oct 2009
    Location
    MID WEST
    Posts
    1,312
    Thanks
    194
    Thanked 34 Times in 31 Posts
    UB,
    I concur with your #10 post.

    In most layouts the sink is 36" wide and the receptacles are space beyond 48" to centerline of the sink, same thing happens at the counter near the range in alot of layouts.

    The appliances and the sink are considered separate counter spaces.
    pc1

  13. #13
    Sawhorse
    Join Date
    Nov 2009
    Location
    West of the river CT
    Posts
    2,884
    Thanks
    432
    Thanked 215 Times in 203 Posts
    Correct.....the 24" "cord" requirement does not apply to islands and peninsulas.....but the sink or range would separate them into different spaces and might require 2....


    Quote Originally Posted by Uncle Bob View Post
    The above does not require the receptacle to be within 24" of the sink; only that a receptacle is required for an Island (sink or no sink). If you have a 4ft wide by 4 ft deep island; there is no requirement that the "required receptacle" be within 24 " of the sink. Also if the island is 8' or even 10' wide; there is a requirement for "only one receptacle" and it is not required to be within 24" of the sink if one is there.
    Please support Jim Brown, Deputy Building Official from Gillette, Wyoming for ICC Board of Directors.
    My questions and answers are based on some bastardized hodge podge starting with the 2003 I-codes amended by the state of CT in 2005 and 2009 including the 2005 NEC ....and as of today.....The 2011 Connecticut Amendments to the 2009 International Energy Conservation Code portion of the 2005 State Building Code has been posted to the State Building Inspector’s website

  14. #14
    Sawhorse
    Join Date
    Oct 2009
    Location
    Albany, CA.
    Posts
    377
    Thanks
    1
    Thanked 27 Times in 22 Posts
    4' on center, toaster in the middle= no more than 24" to outlet. One required behind sink if deeper than 12" on straight wall or 18" corner sink

  15. #15
    Moderator raider1's Avatar
    Join Date
    Nov 2009
    Location
    North Logan Utah
    Posts
    480
    Thanks
    6
    Thanked 28 Times in 24 Posts
    Quote Originally Posted by Uncle Bob View Post
    The above does not require the receptacle to be within 24" of the sink; only that a receptacle is required for an Island (sink or no sink). If you have a 4ft wide by 4 ft deep island; there is no requirement that the "required receptacle" be within 24 " of the sink. Also if the island is 8' or even 10' wide; there is a requirement for "only one receptacle" and it is not required to be within 24" of the sink if one is there.
    Correct, if we are talking about kitchen islands and peninsular counter tops.

    The 24" spacing requirements is for Wall Countertop Spaces.

    So if the kitchen sink is located on an island or peninsular coutertop then there is no requirement that a receptacle be located within 24", but if the kitchen sink is located in a Wall countertop space then a receptacle must be located within 24" of the sink on both sides if there is a counter top space of at least 12" adjacent to the sink.

    Chris

  16. #16
    Administrator jar546's Avatar
    Join Date
    Oct 2009
    Location
    33446
    Posts
    4,704
    Blog Entries
    15
    Thanks
    167
    Thanked 299 Times in 178 Posts
    Items for Sale
    Thanks Chris. Nice to see you here. Stop by more often!
    Admin

  17. #17
    Moderator raider1's Avatar
    Join Date
    Nov 2009
    Location
    North Logan Utah
    Posts
    480
    Thanks
    6
    Thanked 28 Times in 24 Posts
    Quote Originally Posted by jar546 View Post
    Thanks Chris. Nice to see you here. Stop by more often!
    Yeah I have been absolutely swamped lately and have not had much time to comment on any forums. I will try to be more active now.

    Chris

Bookmarks


Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •