Thread: Article 250.52(A)(3) in the 2008 NEC

  1. #1
    Sawhorse north star's Avatar
    Join Date
    Oct 2009
    Posts
    2,127
    Thanks
    262
    Thanked 157 Times in 147 Posts

    Article 250.52(A)(3) in the 2008 NEC

    & & &

    I recently came across this memo from the City of Rogers, Arkansas requiring
    compliance from their builders, in regard to the bonding [ i.e. - now known as
    "connecting" ] of the steel reinforcement in the concrete footings vs. having
    2 ground rods.

    http://www.rogersarkansas.com/inspec...ing%20memo.pdf

    Interesting requirement by the City of Rogers, Arkansas, and other municipalities.

    Some pics. on various installations

    http://www.ashireporter.org/articles...s.aspx?id=1676













    Your thoughts! What is your AHJ requiring?


    & & &
    Last edited by north star; September 17th, 2010 at 14:36.


  2. #2
    Administrator jar546's Avatar
    Join Date
    Oct 2009
    Location
    33446
    Posts
    4,539
    Blog Entries
    15
    Thanks
    136
    Thanked 254 Times in 151 Posts
    Items for Sale
    If there is more than 20' of rebar, it must be bonded and used as the GE. This is a requirement but the problem is that the footers are ofter poured before the electrical inspector gets involved. On a new construction that uses rebar in the footer, there is no reason to have ground rods.

    The acorn in the bottom photo ain't gunna cut it. Not rated for connection to rebar.
    Admin

  3. #3
    Moderator
    Join Date
    Oct 2009
    Location
    SW Florida
    Posts
    241
    Blog Entries
    1
    Thanks
    0
    Thanked 29 Times in 19 Posts
    I strickly enforce Section 250.50 of the NEC which requires all the electrodes that are present to be bonded together to form the grounding electrode system. So, if the design of the building or structure calls for steel reinforcement that meets description outlined in Section 250.52(A)(3), a concrete-encased electrode is present and must be bonded.
    Bryan P. Holland, MCP

  4. #4
    Administrator jar546's Avatar
    Join Date
    Oct 2009
    Location
    33446
    Posts
    4,539
    Blog Entries
    15
    Thanks
    136
    Thanked 254 Times in 151 Posts
    Items for Sale
    250.50 is where the requirement comes from


    If there is no rebar then there is no reason to require it for the NEC requirements. If there is rebar that complies with 250.52(A)(3) then it must be bonded.

    Only 1 builder around here does not use rebar in the footing (Seismic B)
    Admin

  5. #5
    Administrator jar546's Avatar
    Join Date
    Oct 2009
    Location
    33446
    Posts
    4,539
    Blog Entries
    15
    Thanks
    136
    Thanked 254 Times in 151 Posts
    Items for Sale
    Bryan, looks like we essentially posted the same thing at the same time without knowing it. Great minds think alike!
    Admin

  6. #6
    Moderator
    Join Date
    Oct 2009
    Location
    SW Florida
    Posts
    241
    Blog Entries
    1
    Thanks
    0
    Thanked 29 Times in 19 Posts

    Lightbulb

    Following is a list of ground clamps listed for use with rebar...

    There are currently only (2) “acorn” style clamps listed for use with REBAR:

    Erico (Eritech): Model # CP58 - #4 rebar

    ILSCO: Models # GRC-38, GRC-48, GRC-68 - #3, 4, and 5 rebar


    Other UL listed Clamps for use with REBAR:


    Erico (Eritech): Model # EK 16 / EK 17

    ILSCO : Model # BGC-2T-DB, BGC-2P-DB, BGC-2PS-DB, BGC-4/0P-DB, BGC-4/0S-DB

    Galvan: Model # JRD

    Bridgeport: Model # RB-16, RB-17

    Regal Fittings: Model # 8181

    Consolidated Manufacturing International: Model # JRD

    Greaves Corp: Model # J29-DB, J30-DB, J31-DB

    NSI Polaris: Model # G140DB / GLC140DB

    Sigma Electric: Model # C-11N, C-11BN, C-11, C-11D, C-11DN, RBC-1D

    Halex Company: Model # C-11

    Thermocraft: Model # JRD, JRD+

    Thomas and Betts: Model # CC1C-45R, CC2C- 45R, CC10C-56R, CC20C-56R, CC40C-56R
    Bryan P. Holland, MCP

  7. #7
    Sawhorse north star's Avatar
    Join Date
    Oct 2009
    Posts
    2,127
    Thanks
    262
    Thanked 157 Times in 147 Posts
    * * *
    I know that the NEC requirement is there for the grounding of encased electrodes,
    but some jurisdictions may not be aware of the requirement, or like us, we
    cannot enforce it. That darned "powers that be" thingy again! It
    would upset the "Apple Cart Kingdoms" around here.

    Also, what do ya'll do if there are ' post tensioned type cables ' used in the
    foundation. What about grounding encased "cables"?
    FWIW, we are Seismic Zone "B" also. The builders around here use "post
    tension type" foundations a lot. Not that they install them correctly, but
    that is what is used here regularly.


    Bryan,

    Good list of approved clamps!

    * * *


  8. #8
    Administrator fatboy's Avatar
    Join Date
    Oct 2009
    Location
    Northern CO
    Posts
    3,937
    Thanks
    66
    Thanked 278 Times in 228 Posts
    We require it, the foundation crews stub it up like the picture shows, Sparky connects to it at roughin.
    Arguing with an inspector is like wrestling with a pig in mud, pretty soon you realize that the pig is enjoying it!

    This response brought to you by one of the paying members of the Building Code Forum.
    You can join the paying members and support this forum, for a small donation at
    http://www.thebuildingcodeforum.com/forum/payments.php

  9. #9
    Moderator Mule's Avatar
    Join Date
    Oct 2009
    Location
    Texas
    Posts
    1,520
    Thanks
    20
    Thanked 59 Times in 48 Posts
    On post tension the concrete crew throws in a couple of pieces of rebar. They tried just throwing in one piece of steel but I showed them where a 20' piece of rebar bent and turned up wasn't totally encased. That they would need to add whatever distance that was turned up to the length of the rebar that was in the beam.
    Mule
    Building Official
    Texas

    Built to Code = Building the worst that the code will allow!

  10. #10
    Platinum Member
    Join Date
    Nov 2009
    Location
    state of jefferson
    Posts
    1,046
    Thanks
    17
    Thanked 39 Times in 32 Posts
    sometimes throwing a not required stick of rebar in the footings can save time and money over a rod. i noticed a 30" piece of freshly cut ground rod laying 25' from a freshly cut ground rod driven in the ground next to the new service. i told the homeowner to buy another rod and lay it in the 36" deep open trench nearby. "you can do that?" he said. some areas have bedrock and hardpan that makes the ufer option or 30" burial option look good.

  11. #11
    Sawhorse chris kennedy's Avatar
    Join Date
    Oct 2009
    Location
    Miami Fla
    Posts
    1,070
    Thanks
    62
    Thanked 66 Times in 55 Posts
    Quote Originally Posted by Bryan Holland View Post
    I strickly enforce Section 250.50 of the NEC which requires all the electrodes that are present to be bonded together to form the grounding electrode system. So, if the design of the building or structure calls for steel reinforcement that meets description outlined in Section 250.52(A)(3), a concrete-encased electrode is present and must be bonded.
    Same here on Florida's east coast. I don't do dwelling units and I always clamp directly to the footers bottom bar with a listed clamp. I have never seen re-bar stubbed up out of the footer/slab like that. I belong to the camp that believes that the portion of the re-bar between the clamp and the pour is a grounding electrode conductor that does not meet the requirements of 250.62, not the grounding electrode described bellow.

    250.52(A)(3) Concrete-Encased Electrode.
    An electrode encased by at least 50 mm (2 in.) of concrete
    , located horizontally near the bottom or vertically, and within that portion of a concrete foundation or footing that is in direct contact with the earth, consisting of at least 6.0 m (20 ft) of one or more bare or zinc galvanized or other electrically conductive coated steel reinforcing bars or rods of not less than 13 mm (½ in.) in diameter, or consisting of at least 6.0 m (20 ft) of bare copper conductor not smaller than 4 AWG. Reinforcing bars shall be permitted to be bonded together by the usual steel tie wires or other effective means. Where multiple concrete-encased electrodes are present at a building or structure, it shall be permissible to bond only one into the grounding electrode system.
    Quotes are from the 08 NEC unless otherwise noted.