Thread: Area increase not allowed for 13R sprinkler system.

  1. #1
    Sawhorse
    Join Date
    Oct 2009
    Location
    Lincoln
    Posts
    174
    Thanks
    18
    Thanked 2 Times in 2 Posts

    Area increase not allowed for 13R sprinkler system.

    Given:

    Three story apartment building, Type VB construction.
    The NFPA-13R sprinkler system.
    An architect who reads 903.3.1.2 to say that the 13R residential sprinkler system is an equal substitute for a NFPA13 system only in R occupancies of four stories or less.

    Now I have read IBC 504.2 several times over and my interpretation is that both height and area increases are allowed for the full NFPA-13 sprinkler system. But the 13R sprinkler system is good for only the height increase.

    Would you concur with my interpretation that the 13R system does not allow for area increase?

    Thanks!

  2. #2
    Sawhorse
    Join Date
    Oct 2009
    Posts
    7,435
    Thanks
    77
    Thanked 424 Times in 394 Posts
    Appears you are correct



    506.3 Automatic sprinkler system increase. Where a building is equipped throughout with an approved automatic sprinkler system in accordance with Section 903.3.1.1, the building area limitation in Table 503 is permitted to be increased by an additional 200 percent (Is = 2) for buildings with more than one story above grade plane and an additional 300 percent (Is = 3) for buildings with no more than one story above grade plane. These increases are permitted in addition to the height and story increases in accordance with Section 504.2.

    Exception: The building area limitation increases shall not be permitted for the following conditions:

    1. The automatic sprinkler system increase shall not apply to buildings with an occupancy in Group H-1.
    2. The automatic sprinkler system increase shall not apply to the building area of an occupancy in Group H-2 or H-3. For buildings containing such occupancies, the allowable building area shall be determined in accordance with Section 508.4.2, with the sprinkler system increase applicable only to the portions of the building not classified as Group H-2 or H-3.
    3. Fire-resistance rating substitution in accordance with Table 601, Note d.

  3. #3
    Sawhorse mtlogcabin's Avatar
    Join Date
    Oct 2009
    Location
    Big Sky Country
    Posts
    4,735
    Thanks
    67
    Thanked 611 Times in 486 Posts
    Would you concur with my interpretation that the 13R system does not allow for area increase?
    Interesting non-lethal, yet legal Self Defense Products available on the market. Feel free to check out this web page , then share with family/friends.
    It is nice to know there are some options offered to protect our loved ones. You may also contact via web page link with any questions, or message me.
    www.mydamselpro.net/graceclawson

  4. #4
    Platinum Member
    Join Date
    Dec 2009
    Location
    Husker Country
    Posts
    1,583
    Thanks
    63
    Thanked 99 Times in 80 Posts
    area increase not allowed for non NFPA 13 sprinkler systems

  5. #5
    Platinum Member
    Join Date
    Aug 2011
    Location
    Mid West
    Posts
    1,280
    Thanks
    85
    Thanked 107 Times in 95 Posts
    does not count

  6. #6
    Sawhorse
    Join Date
    Oct 2009
    Location
    Lincoln
    Posts
    174
    Thanks
    18
    Thanked 2 Times in 2 Posts
    Thanks everyone.

  7. #7
    Platinum Member
    Join Date
    Oct 2009
    Location
    alabama
    Posts
    3,713
    Thanks
    24
    Thanked 215 Times in 185 Posts
    For what is worth, compared with SBC the area increases are cooked into the table already when it comes to group R.

  8. #8
    Sawhorse TJacobs's Avatar
    Join Date
    Oct 2009
    Location
    Peoples Republic of Illinois
    Posts
    1,312
    Thanks
    83
    Thanked 43 Times in 37 Posts
    with all of the above. Area increase = NFPA 13 only.
    Jake

    This response brought to you by one of the paying members of the Building Code Forum.
    You can join the paying members and support this forum, for a small donation at
    http://www.thebuildingcodeforum.com/forum/payments.php

  9. #9
    Sawhorse Builder Bob's Avatar
    Join Date
    Oct 2009
    Location
    Sunny SC - Coastal (not Charleston or Myrtle Beach)
    Posts
    1,295
    Thanks
    45
    Thanked 109 Times in 89 Posts
    Be careful as a building area is allowed to be increased - I can add an extra story.
    Allowable Floor Area is not allowed to be modified by a 13 R system.

    However, they can still do an floor area modification based on open area.......
    Lost is the south......
    ******************************
    Can you build to the minimum standards?

    Help us by supporting this forum .....If the advice you seek saved you a few bucks, pass on the wealth to this forum

    http://www.thebuildingcodeforum.com/forum/payments.php

    FWIW- MCP,CBO,CPE, ASCET, and A BYOB Ga. Dawg Fan!

  10. #10
    Platinum Member
    Join Date
    Oct 2009
    Location
    alabama
    Posts
    3,713
    Thanks
    24
    Thanked 215 Times in 185 Posts
    Quote Originally Posted by Builder Bob View Post
    Be careful as a building area is allowed to be increased - I can add an extra story. Allowable Floor Area is not allowed to be modified by a 13 R system. However, they can still do an floor area modification based on open area.......
    Only relevant if they are of type V construction because adding another story to buildings of other construction types will exceed the 4 story limit for 13R (and obviously, this is limited to residential occupancies).

  11. #11
    Moderator jpranch's Avatar
    Join Date
    Oct 2009
    Location
    Gillette Wyoming
    Posts
    1,703
    Blog Entries
    1
    Thanks
    96
    Thanked 93 Times in 73 Posts
    Seen it, been there, done that. The trick is educating the design professional. You DO NOT get an area increase for 13-R. I would suggest having the design professional call the ICC for a code opinion to confirm. If he or she is not a member of the ICC perhaps you could email the question to staff?