    16' Garage Door Headers

    Double garage doors, nominal 16' wide... I often see them on plans for detached garages. Given that the IRC is essentially intended to allow prescriptive design/building without engineering, how do you address the header span for a 16' garage door? Do you allow an engineered (LVL) or similar component, based on the spec. sheet for that beam? Or do you strictly enforce the IRC span tables (which don't address this)? I hate to require engineering on a 400-500 s.f. detatched garage.

    Just wondering how you look at these in your neck of the woods...

  2. #2
    Sawhorse
    Join Date
    Oct 2009
    Posts
    239
    Thanks
    28
    Thanked 23 Times in 20 Posts

    Re: 16' Garage Door Headers

    The vast majority are using engineered wood products for these. Do not require an engineer to sign off. Manufacturer provides span charts and installation instructions in manual. If anal retentive, their is more info for the asking.

  3. #3
    Sawhorse Uncle Bob's Avatar
    Join Date
    Oct 2009
    Location
    Texas
    Posts
    1,402
    Thanks
    9
    Thanked 57 Times in 35 Posts

    Re: 16' Garage Door Headers

    Paul,

    I see no reason not to accept an engineered (LVL) (gluelam) or similar component, based on the manufacturer's spec. sheet for that beam. That's all I've seen over the past few years. It's well within my comfort zone.

    Min&Max,

    How did you find out my real name? Anal Retentive.

    Uncle Bob
    It isn't what we don't know that causes most of our problems; it's what we do know that ain't so.

  4. #4
    Silver Member
    Join Date
    Oct 2009
    Location
    Salina, KS
    Posts
    492
    Thanks
    0
    Thanked 1 Time in 1 Post

    Re: 16' Garage Door Headers

    Oh, I agree about using the engineered headers, per the mfg. instructions... maybe I confused the issue with my original question. What about using dimensional lumber (4 x ?, multiple 2 x ?, etc.) that aren't on the span tables of the IRC? Anybody allowing this without engineering? Even if it appears over-designed, do you allow it?

  5. #5
    Sawhorse mtlogcabin's Avatar
    Join Date
    Oct 2009
    Location
    Big Sky Country
    Posts
    4,657
    Thanks
    67
    Thanked 597 Times in 473 Posts

    Re: 16' Garage Door Headers

    We run the numbers thru StruCalc if it passes fine if not they have to resubmit. We DO NOT tell them what size is needed.
    Interesting non-lethal, yet legal Self Defense Products available on the market. Feel free to check out this web page , then share with family/friends.
    It is nice to know there are some options offered to protect our loved ones. You may also contact via web page link with any questions, or message me.
    www.mydamselpro.net/graceclawson

  6. #6
    Sawhorse Uncle Bob's Avatar
    Join Date
    Oct 2009
    Location
    Texas
    Posts
    1,402
    Thanks
    9
    Thanked 57 Times in 35 Posts

    Re: 16' Garage Door Headers

    "using dimensional lumber (4 x ?, multiple 2 x ?, etc.) that aren't on the span tables of the IRC"

    Get an Engineer for about $150.00.

    Absolutely, positively, unequivically, NO!

    Uncle Bob
    It isn't what we don't know that causes most of our problems; it's what we do know that ain't so.

  7. #7
    Moderator cboboggs's Avatar
    Join Date
    Oct 2009
    Location
    Eastern MO
    Posts
    277
    Thanks
    3
    Thanked 6 Times in 6 Posts

    Re: 16' Garage Door Headers

    We take the same approach as mtlogcabin. We run construction through a program either StruCalc or Plans Analyst. If it checks out fine if not they have to resubmit.

  8. #8
    Sawhorse conarb's Avatar
    Join Date
    Oct 2009
    Location
    California Bay Area
    Posts
    1,426
    Thanks
    29
    Thanked 53 Times in 43 Posts

    Re: 16' Garage Door Headers

    It's not that simple, almost all garage door headers require portal design, and usually narrow portals integrated with the header, this always requires engineering, listen to your uncle.


    “The best way to get a bad law repealed is to enforce it strictly,” Abraham Lincoln.

  9. #9
    Platinum Member
    Join Date
    Oct 2009
    Location
    alabama
    Posts
    3,713
    Thanks
    24
    Thanked 214 Times in 184 Posts

    Re: 16' Garage Door Headers

    Quote Originally Posted by conarb
    [size=150]It's not that simple, almost all garage door headers require portal design, and usually narrow portals integrated with the header, this always requires engineering, listen to your uncle.
    In areas with significant lateral loads from sesmic or wind, yes.

    In areas without such loads, it's not such an issue.

  10. #10
    Sawhorse
    Join Date
    Oct 2009
    Location
    State of Disbelief
    Posts
    1,658
    Thanks
    468
    Thanked 68 Times in 58 Posts

    Re: 16' Garage Door Headers

    Like UB and conarb, not without an engineers stamp. As brudgers pointed out, I'm in a high wind/seismic/volcanic area plus I'm in CA.

    Luckily, the local contractors know this, it's just the DIY'er who is a potential problem.

    Sue, lost on the frontier

  11. #11
    Silver Member
    Join Date
    Oct 2009
    Location
    Salina, KS
    Posts
    492
    Thanks
    0
    Thanked 1 Time in 1 Post

    Re: 16' Garage Door Headers

    Well, Sue, the DIYers is exactly why I posed the original question. I'm all for helping homeowners that want to improve their homes and I try to guide them through the IRC when they want to do their own designs/plans. Since detached two-car garage/workshops are a common project around here, I see them a lot, and I see some VERY interesting design solutions - most of them noncompliant.

    I often suggest LVLs or other engineered headers along with Hardy Walls or Simpson Strong Walls for lateral/shear on the open end. However, considering the cost of these vs. dimensional and sheet goods, usually the original design doesn''t include them.

    Thanks for the opinions... I keep striving to help out the homeowners!

  12. #12
    Sawhorse mtlogcabin's Avatar
    Join Date
    Oct 2009
    Location
    Big Sky Country
    Posts
    4,657
    Thanks
    67
    Thanked 597 Times in 473 Posts

    Re: 16' Garage Door Headers

    The garage and other window and door openings are prescriptive see
    FIGURE R602.10.6.2
    ALTERNATE BRACED WALL PANEL ADJACENT TO A DOOR OR WINDOW OPENING

    A minimum 3" X 11.25" net header size is required for opening from 6ft to a maximum 18 ft. That would take care of the wind and seismic shear loads. Correct?
    A larger header may still required due to additional floor/roof loads.
    Interesting non-lethal, yet legal Self Defense Products available on the market. Feel free to check out this web page , then share with family/friends.
    It is nice to know there are some options offered to protect our loved ones. You may also contact via web page link with any questions, or message me.
    www.mydamselpro.net/graceclawson

  13. #13
    Silver Member
    Join Date
    Oct 2009
    Location
    Salina, KS
    Posts
    492
    Thanks
    0
    Thanked 1 Time in 1 Post

    Re: 16' Garage Door Headers

    mt - As long as the walls adjacent to the door are 16" or wider, I've used exactly what you cited above - however, it seems that many want to maximize their openings (16' door) with a building that is limited by lot size, resulting in 12" in. or less by the doors! I get 18' wide garges submitted often. Won't work unless a strong wall is used.

    2nd point - It is interesting that the header in figure R602.10.6.2 goes up to 18' in length, with "min. 3" X 11.25" , which means that it might have to be bigger, depending on the actual use. But the table R502.5(1) doesn't go to 18' so how does one determine how much greater than the minimum is required? (Assuming dimensional lumber is used, not LVL). I assume the 3 x 11.25 is based on the alternate braced wall panel working for lateral/shear, and is NOT based on the header supporting the load above. That's why it's minimum for as little as 6' wide and the same up to 18'.

  14. #14
    Sawhorse Uncle Bob's Avatar
    Join Date
    Oct 2009
    Location
    Texas
    Posts
    1,402
    Thanks
    9
    Thanked 57 Times in 35 Posts

    Re: 16' Garage Door Headers

    MtLogCabin,

    "A minimum 3" X 11.25" net header size is required for opening from 6ft to a maximum 18 ft. That would take care of the wind and seismic shear loads. Correct?"

    Does not state that header (6' to 18') can be "dimensional lumber"; only that the minimum net header size shall be 3" X ll.25".

    Maximum length for a "dimensional lumber" header for roof and ceiling only; would require 4-2X12s and be limited to a 14' 1" span (TABLE R502.5(1); which would require a 6" wide wall; provided the building width was not more than 20'.

    Now if they put double doors in; they could use double 2"x10"s (maximum span 8' 5"); with support in the center of the 16' foot opening; and your going to need every inch of that 20' building width. Requires braced walls to be minimum 16" wide each X 3 = 48" should allow two 8' openings (barely).

    I think,

    Uncle Bob
    It isn't what we don't know that causes most of our problems; it's what we do know that ain't so.

  15. #15
    Sawhorse mtlogcabin's Avatar
    Join Date
    Oct 2009
    Location
    Big Sky Country
    Posts
    4,657
    Thanks
    67
    Thanked 597 Times in 473 Posts

    Re: 16' Garage Door Headers

    UB I agree and Under StruCalc what you stated is good by 85% with a .198 deflection 46lbs snow 15 lb dead loads. That's why we use StruCalc to double check submitted design loads that are not prepared by an engineer.
    Interesting non-lethal, yet legal Self Defense Products available on the market. Feel free to check out this web page , then share with family/friends.
    It is nice to know there are some options offered to protect our loved ones. You may also contact via web page link with any questions, or message me.
    www.mydamselpro.net/graceclawson

  16. #16
    Sawhorse Uncle Bob's Avatar
    Join Date
    Oct 2009
    Location
    Texas
    Posts
    1,402
    Thanks
    9
    Thanked 57 Times in 35 Posts

    Re: 16' Garage Door Headers

    MtLogCabin,

    Thanks, I don't know that stuff; so I have to either go by the codes or Engineered. Heck, at 65, I don't want to know that stuff.

    It's good to know that some of ya'll learn stuff beyond the requirements of just knowing the codes.

    Uncle Bob
    It isn't what we don't know that causes most of our problems; it's what we do know that ain't so.

  17. #17
    Administrator fatboy's Avatar
    Join Date
    Oct 2009
    Location
    Northern CO
    Posts
    4,119
    Thanks
    78
    Thanked 310 Times in 254 Posts

    Re: 16' Garage Door Headers

    We allow and check submitted engineered products, do not do design though. Seismic and winds are not an issue here.
    Arguing with an inspector is like wrestling with a pig in mud, pretty soon you realize that the pig is enjoying it!

    This response brought to you by one of the paying members of the Building Code Forum.
    You can join the paying members and support this forum, for a small donation at
    http://www.thebuildingcodeforum.com/forum/payments.php

  18. #18
    Platinum Member
    Join Date
    Oct 2009
    Location
    alabama
    Posts
    3,713
    Thanks
    24
    Thanked 214 Times in 184 Posts

    Re: 16' Garage Door Headers

    Quote Originally Posted by mtlogcabin
    UB I agree and Under StruCalc what you stated is good by 85% with a .198 deflection 46lbs snow 15 lb dead loads. That's why we use StruCalc to double check submitted design loads that are not prepared by an engineer.
    From my time behind the counter, it's probably a good idea to spot check designs submitted by engineers as well.

    The Braille method of plan review is not very reliable.

  19. #19
    Sawhorse Uncle Bob's Avatar
    Join Date
    Oct 2009
    Location
    Texas
    Posts
    1,402
    Thanks
    9
    Thanked 57 Times in 35 Posts

    Re: 16' Garage Door Headers

    Brudgers,

    "From my time behind the counter, it's probably a good idea to spot check designs submitted by engineers as well."

    I'm afraid that as an Inspector; I'm not qualified; nor should I be expected to be qualified to judge Engineered Designs (signed and sealed) that execeed the codes. In that case, I am required to be able to read the Engineer's plans; in order to insure that the construction is per plans.

    "The Braille method of plan review is not very reliable."

    As far as plans that are submitted that are within the "Design Criteria" of R301; I also don't consider using the code requirements, to review plans as "the blind method"; and I believe my answer to the original question reflects that.

    Would be so kind as to show me what part of my answer that was wrong; or where I used the "Braile method of plan review"?

    "A minimum 3" X 11.25" net header size is required for opening from 6ft to a maximum 18 ft. That would take care of the wind and seismic shear loads. Correct?"

    Does not state that header (6' to 18') can be "dimensional lumber"; only that the minimum net header size shall be 3" X ll.25".

    Maximum length for a "dimensional lumber" header for roof and ceiling only; would require 4-2X12s and be limited to a 14' 1" span (TABLE R502.5(1); which would require a 6" wide wall; provided the building width was not more than 20'.

    Now if they put double doors in; they could use double 2"x10"s (maximum span 8' 5"); with support in the center of the 16' foot opening; and your going to need every inch of that 20' building width. Requires braced walls to be minimum 16" wide each X 3 = 48" should allow two 8' openings (barely)."

    Thanks,

    Uncle Bob
    It isn't what we don't know that causes most of our problems; it's what we do know that ain't so.

  20. #20
    Sawhorse JBI's Avatar
    Join Date
    Oct 2009
    Location
    The Empire State
    Posts
    1,645
    Thanks
    533
    Thanked 61 Times in 53 Posts

    Re: 16' Garage Door Headers

    U B - I don't think brudgers was suggesting you were wrong. I think he was just reinfircing that plans should always be checked, regardless of who prepared them. I agree with that 100%, some of the worst plans I've seen have come from engineers... WITH a seal/signature on them.

    Simply looking for that seal/sig (or feeling for the raised seal... the 'braille' method) doesn't cut it.

    That's twice in a week I've agreed with brudgers...




    Life is not a journey to the grave with the intention of arriving safely in a pretty and well preserved body, but rather to skid in broadside, thoroughly used up, totally worn out, and proclaiming, "Wow, what a ride!!!"