1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Accessible junction boxes. Where does it mention a ladder?

Discussion in 'Commercial Electrical Codes' started by TimNY, Jul 11, 2018.

  1. TimNY

    TimNY Platinum Member

    Joined:
    Jan 13, 2010
    Messages:
    1,136
    Likes Received:
    5
    Existing commercial space with ~14' ceilings (exposed truss roof).

    There is existing 3/4" EMT secured to the bottom the the steel trusses with a junction box (4" sq) every 10'.

    New rooms with 8' GWB ceilings were constructed under this EMT & junction boxes. Ceilings only have GWB, no walkways or platforms on top of the ceiling (not rated for storage).

    I contend that the junction boxes are a wiring method and must be accessible; eg they are exposed, you don't have to damage the building to access them. Must be "accessible"-- not "readily accessible".

    Inspector says they need to be accessible with a ladder? The distance between the top of the ceiling joists and the junction boxes ranges from 5' to 6'-6", so I don't even know that a ladder is required. Granted you will have to walk the joists, and if you need a ladder you will have to bring some plywood or use a Little Giant. But more to the point, I don't see what a ladder has to do with "accessible".

    He says "move them to an accessible location" "that can be accessed with a ladder".

    Is there any merit to this? I just don't see it in any version of the NEC. 300.15(A) in the 2017.
     
  2. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,242
    Likes Received:
    781
    Boy that is spoiled??

    What is he going to do when he does an atrium, with j boxes at the top??
     
    Msradell likes this.
  3. Rick18071

    Rick18071 Sawhorse

    Joined:
    Nov 28, 2009
    Messages:
    1,339
    Likes Received:
    80
    The inspector probably said a ladder because that is what is shown in the NEC Handbook.
    I would have them install a 3' wide catway to get to the j boxes, could be plywood.
    And an access hatch to get above the ceiling.
    I would expect an repairman have a ladder for repairs but not sheets of plywood.
     
    TimNY likes this.
  4. ADAguy

    ADAguy Sawhorse

    Joined:
    Sep 11, 2013
    Messages:
    2,214
    Likes Received:
    178
    Comes down to methods and means doesn't it?
     
  5. north star

    north star Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    3,475
    Likes Received:
    179
    $ $ = $ $

    Long time no see **TimNY** !

    Did the Inspector cite a particular Code Section or Article from the NEC ?


    IMO, a ladder isn't applicable.......The J-Boxes ARE accessible if someone
    wants to climb around on the trusses.


    = = $ = =
     
  6. TimNY

    TimNY Platinum Member

    Joined:
    Jan 13, 2010
    Messages:
    1,136
    Likes Received:
    5
    Yes, been a while!

    No, no code was section cited. It seems he wants them "readily accessible" whereas the code requires "accessible". If they need to rent an articulating boom, then so be it.. they're accessible.

    Ultimately the electrician has to deal with it. I offered the walkway, but they had to refer it to "planning" for approval. Electrician may just run new EMT from one end to the other. The boxes aren't even used for anything.. simply a chase.

    I'm all for meeting the code minimum. I'm all for making it better than code minimum. But I have to draw the line at making it difficult for me to exceed the code minimum.
     