1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

comcheck - PEMB

Discussion in 'Commercial Energy Codes' started by Hyrax4978, Jul 31, 2018.

  1. Hyrax4978

    Hyrax4978 Registered User

    Joined:
    Nov 28, 2016
    Messages:
    39
    Likes Received:
    0
    looking at some PEMB insulation options and running them through comcheck to find our most economical option.

    I see in ashrae 90.1 that there are limits to what you are allowed to claim for insulation when it comes to metal buildings. ahshrae seems to limit you to a more realistic U value rather than what the metal building suppliers "claim" the insulated walls can produce. I also see that fenestration looks like it needs to meet NFRC 100.

    IECC doesn't seem to have the same restrictions on the metal buildings in the terms of advertised versus real U values as well as fenestration tests meeting NFRC 100.

    Any insight would be appreciated.
     
  2. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    5,701
    Likes Received:
    640
    Usually the Comchecks I see have a footnote requiring more verification of the claimed U factor...Manufacturers installation instructions? Testing paperwork?
     
  3. Hyrax4978

    Hyrax4978 Registered User

    Joined:
    Nov 28, 2016
    Messages:
    39
    Likes Received:
    0
    I do have product data, but its the sales data which usually offers R or U values of items such as center of glass, or door panel, which is completely different than the tested NFRC data. Ashrae seems to require NFRC compliant data, where IECC doesn't seem to have the same requirement. Unless i am missing something.
    Here is an example, i have a flyer from a PEMB door assembly that shows the calculated U factor as 0.14 meeting certain ASTM methods. But the NFRC compliant method resulted in only a 0.43 U factor. thats a big difference. Ashrae seems to require the NFRC, but i don't see where IECC requires the NFRC. obviously if i just plug in the better of the two U factors it helps me, but i was hoping to better understand this so i can do it correctly.

    Thanks.
     
  4. RLGA

    RLGA Sawhorse

    Joined:
    Oct 18, 2009
    Messages:
    1,208
    Likes Received:
    287
    See IECC C303.1.3.
     
  5. Hyrax4978

    Hyrax4978 Registered User

    Joined:
    Nov 28, 2016
    Messages:
    39
    Likes Received:
    0
    And there it is!!! thanks so much!
     
  6. RLGA

    RLGA Sawhorse

    Joined:
    Oct 18, 2009
    Messages:
    1,208
    Likes Received:
    287
    A bit of advice on standards referenced in the I-Codes: Check the "Reference Standards" chapter (the last chapter in each code) for the standard that you're looking for. If it's not listed, then it is not referenced by that particular I-Code. If it is listed, then just below it are all of the locations where that standard is referenced within the code. Please note that the standards are listed in alphabetical order according to the name of organization that publishes the standard, then numerically for each standard; so, you'll need to know the name of the organization that publishes the standard you're seeking.

    In Chapter 1 of each code there is a section called "Referenced codes and standards," which states in part, "The codes and standards referenced in this code shall be considered to be a part of the requirements of this code to the prescribed extent of each such reference..." This means that just by listing the standard in the Reference Standards Chapter does not mean that the entire content of the standard is part of the code. For example, if the reference is to "Table 10 of XYZ Standard," then only Table 10 is made part of the code. If there is no such specific reference or limitation, then the entirety of the standard is made part of the code.
     