1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Elevator Sump Alarm

Discussion in 'Elevators' started by Francis Vineyard, Jul 28, 2017.

  1. Francis Vineyard

    Francis Vineyard Sawhorse

    Joined:
    Jan 1, 2010
    Messages:
    2,542
    Likes Received:
    196
    An elevator inspector is questioning whether the sump alarm is permitted in the hoistway.

    In reference to the below information and other that you may have what is your determination?

    The plumbing code is silent on where the alarm should be located. But an elevator code interpretation (10-1493) could be interpreted unrelated devices in the hoistway.

    2.8.1 Equipment Allowed

    Only machinery and equipment used directly in connection with the elevator shall be permitted in elevator hoistways, machinery spaces, machine rooms, control spaces, and control rooms.

    2.8.2.2 Only such electrical wiring, raceways, and cables used directly in connection with the elevator, including wiring for signals, for communication with the car, for lighting, heating, air conditioning, and ventilating the car, for fire detecting systems, for pit sump pumps, and for heating and lighting the hoistway and/or the machinery space, machine room, control space, or control room shall be permitted to be installed inside the hoistway, machinery space, machine room, control space, or control room.

    Inquiry 10-1496

    Subject: ASME A17.1-2007, Requirement 2.2.2.5 and 2.8.1

    Concerning sump pumps in elevators equipment allowed in machine spaces

    Question (1): Would it be an acceptable interpretation to classify the electrical disconnect and control panel for the sump pump as being used directly for operation with the elevator, thus permitting the disconnect and control panel to be located in machinery spaces, machinery rooms, etc.?

    Answer (1): No.

    Also contrary to what the plumbing commentary alleges it has always been the intent that the alarm device should not disable the required pump; this language added to the 2015 IPC.

    Note in reference to the above, the plumbing code did not have this exception until the 2006 edition;

    Edition: A17.1-2000 through A17.1-2007 including A17.1a-2008

    Exception: An oil separator is not required in hydraulic elevator pits where an approved alarm system is installed. Such alarm systems shall not terminate the operation of pumps utilized to maintain emergency operation of the elevator by firefighters.
     
  2. north star

    north star Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    3,288
    Likes Received:
    140
    % ~ %

    Have the Elevator Inspector provide you with acceptable,
    cited codes & sections, for your review.


    % ~ %
     
  3. Francis Vineyard

    Francis Vineyard Sawhorse

    Joined:
    Jan 1, 2010
    Messages:
    2,542
    Likes Received:
    196
    The elevator sections and its official interpretation apparently allows only a cord plugged sump pump in lue of a drain.

    As we are aware though often quoted for guidance the commentary code and as demonstrated here was incorrect. Granted official interpretations have been wrong too.

    Would prefer to substantiate the decision on where this alarm is approved that aligns with a specific elevator code with the plumbing (or an electrical) alarm code not because I say so.
     