1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Exterior Duct - Insulation on the inside?

Discussion in 'Commercial Energy Codes' started by Darren Emery, Aug 21, 2017.

  1. Darren Emery

    Darren Emery Sawhorse

    Joined:
    Oct 20, 2009
    Messages:
    444
    Likes Received:
    1
    Ground based HVAC unit for a gymnasium. Plans called for exterior duct insulation and protective wrap. Contractor and engineer now saying the R-4 interior insulation on this duct is sufficient. R-8 is required (2009 ECC adopted), but I'm also concerned about the insulation being on the inside of the duct, rather than the outside. Seems to me that condensation and mold is a likely problem in the future. Would appreciate thoughts on this one - we just recently began enforcing the ECC.

    BTW - we are in Kansas, so we have both extremes: -10 to about 106.
     
    #1 Darren Emery, Aug 21, 2017
    Last edited: Aug 21, 2017
  2. Pcinspector1

    Pcinspector1 Platinum Member

    Joined:
    Oct 28, 2009
    Messages:
    2,007
    Likes Received:
    111
    Darren, might want to check "Thermaduct" it claims it handles the mold issue and has different R-values available.
     
  3. tmurray

    tmurray Sawhorse

    Joined:
    Jun 10, 2011
    Messages:
    1,104
    Likes Received:
    184
    If their product is not an R8 I don't know how you are going to approve it. Your condensation concerns are well founded.
     
  4. Pcinspector1

    Pcinspector1 Platinum Member

    Joined:
    Oct 28, 2009
    Messages:
    2,007
    Likes Received:
    111
    2009 IECC, 503.2.7 Not sure how you interpret the exception #2 ?
     
  5. Darren Emery

    Darren Emery Sawhorse

    Joined:
    Oct 20, 2009
    Messages:
    444
    Likes Received:
    1
    Thanks for the input. The question now is, if they somehow obtain R-8 on the inside, do I approve that?
     
  6. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    5,240
    Likes Received:
    475
    I don't see how you couldn't? You could certainly let them know your concerns, but I doubt there is a code basis for denial.
     
  7. Pcinspector1

    Pcinspector1 Platinum Member

    Joined:
    Oct 28, 2009
    Messages:
    2,007
    Likes Received:
    111
    R5 min. unconditioned space
    R8 min. outside the bldg.
     
  8. tmurray

    tmurray Sawhorse

    Joined:
    Jun 10, 2011
    Messages:
    1,104
    Likes Received:
    184
    I would agree with Steveray. I would make sure I documented that my concerns were expressed to the engineer and that there was no violation of the code to prohibit their proposed design.

    For what it's worth, I don't know why anyone would ever insulate on the inside of a duct. As you mentioned, there is an increase in the likelihood that it will be conducive to mold growth, but it also introduces potential contaminants in the air stream through both material off-gassing and particles such as fiberglass, which are known respiratory irritants. Additionally, it completely screws up your friction calculations for your ductwork, you now have to buy larger, more expensive ductwork to deal with the reduction in area of the duct and friction loss. The only advantage I can think of is that the insulation is protected from damage.
     
  9. ICE

    ICE Sawhorse

    Joined:
    Jun 23, 2011
    Messages:
    7,220
    Likes Received:
    421
    The insulation is on the inside to protect it from the elements.
     
  10. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    5,240
    Likes Received:
    475
    Kind of like insulating on the inside of the house..........
     
  11. mtlogcabin

    mtlogcabin Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    6,421
    Likes Received:
    385
    604.13 Internal insulation.
    Materials used as internal insulation and exposed to the airstream in ducts shall be shown to be durable when tested in accordance with UL 181. Exposed internal insulation that is not impermeable to water shall not be used to line ducts or plenums from the exit of a cooling coil to the downstream end of the drain pan.

    Needs to be R-8 minimum

    http://ww1.owenscorning.com/literature/pdfs/HVACCatalog.pdf
     
    steveray likes this.
  12. Paul Sweet

    Paul Sweet Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    838
    Likes Received:
    82
    Internal duct insulation used to be used a lot for sound reduction, and still is to a limited extent, mostly when very low noise levels are needed.
     
  13. JCraver

    JCraver Sawhorse

    Joined:
    Feb 20, 2014
    Messages:
    272
    Likes Received:
    62
    I'd bet 90%+ of the houses built in the 80's - 90's around here have ducts in the crawlspaces that are insulated on the inside. I spent a summer building them for a guy when I was in HS - lived that whole summer covered in contact cement... I don't think they had too many troubles with them - or at least, I've not heard of many of them being replaced.

    I agree with the other guys ^^^ up there, your guy needs to be putting in R8.
     