1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Fire pump room requirements

Discussion in 'Commercial Building Codes' started by Hyrax4978, Jun 12, 2018.

  1. Hyrax4978

    Hyrax4978 Active Member

    Joined:
    Nov 28, 2016
    Messages:
    34
    Likes Received:
    0
    It was just determined a building we are designing will need a fire pump. where in the code do we find requirements for the room? Basically looking for ratings and the such.

    Thanks,
    Brian
     
  2. RLGA

    RLGA Sawhorse

    Joined:
    Oct 18, 2009
    Messages:
    1,092
    Likes Received:
    256
    IBC Section 913.2.1 (2015 edition)
     
  3. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    5,653
    Likes Received:
    627
    If it is an electric pump that stuff gets pretty complicated too....
     
  4. Hyrax4978

    Hyrax4978 Active Member

    Joined:
    Nov 28, 2016
    Messages:
    34
    Likes Received:
    0
    Yes, thats what i found out. the owner already has a diesel pump at another location so thats the route they want to take.
     
  5. Hyrax4978

    Hyrax4978 Active Member

    Joined:
    Nov 28, 2016
    Messages:
    34
    Likes Received:
    0
    How about for the diesel fuel tank that is between 150 and 200 gallons of fuel oil? rating the room is easy, but does that large quantity of fuel trigger anything else?
     
  6. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    5,653
    Likes Received:
    627
    Is the fuel in the building? You would have to look at control area requirements....
     
  7. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,096
    Likes Received:
    755
    High rise or other

    Might be allowed a Day tank in the building and another tank somewhere else..

    What kind of occupancy// business???
     
  8. RLGA

    RLGA Sawhorse

    Joined:
    Oct 18, 2009
    Messages:
    1,092
    Likes Received:
    256
    Diesel fuel is a Class II combustible liquid, which is permitted 120 gallons. But since a sprinkler system is installed, the quantity can be increased by 100% to 240 gallons.
     
  9. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    5,653
    Likes Received:
    627
    You da man Ron!
     
    my250r11 likes this.
  10. Hyrax4978

    Hyrax4978 Active Member

    Joined:
    Nov 28, 2016
    Messages:
    34
    Likes Received:
    0
    Thank you!!!!! Just saved me about 2 hours of hunting around!!!!
     
  11. IJHumberson

    IJHumberson Sawhorse

    Joined:
    Oct 30, 2009
    Messages:
    81
    Likes Received:
    19
    Chapter 4 in NFPA 20, Standard for the Installation of Stationary Pumps for Fire Protection, also has separation requirements for the Fire Pump room (basically, for high-rise it's 2-hr, for non-high-rise it's 1-hr).
     
  12. north star

    north star Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    3,468
    Likes Received:
    178
    # ~ #

    What about the type of diesel fuel tank(s),
    ...single wall, double wall, containment
    plans ?


    # ~ #
     