1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Floor Drains In Mech. Rooms & Other Spaces

Discussion in 'Commercial Plumbing Codes' started by north star, Mar 12, 2018.

  1. north star

    north star Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    3,504
    Likes Received:
    186
    = = >

    Greetings to all !

    I am seeking input as to how your jurisdiction handles Floor Drains
    in Mechanical or Electrical Rooms.......Typically, in Restrooms
    there are Trap Primers installed.


    I have a project where the Military Bldg. owner is installing a
    high security vault, 11' x 9' sq. ft., plus a Floor Drain.

    QUESTION # 1: Do you require ALL trap seals to be protected

    from drying out [ RE: `12 IPC, Section 1002.4 ] ?

    QUESTION # 2: If you answered "No" to Question # 1, do those

    trap seals ever dry out ?

    QUESTION # 3: If you answered "Yes" to Question # 1, how are

    the trap seals protected ?

    Thanks for your input !

    < = =
     
  2. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    5,701
    Likes Received:
    640
    They do dry out.....Town Hall bathrooms do it all the time....I think they have some type of
    mechanical flapper now, but trap primer more common...
     
    JBI likes this.
  3. north star

    north star Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    3,504
    Likes Received:
    186
    = = >

    Thanks **steveray** !


    While the trap primers are [ typically ] considered to be the
    most common, ...ProVent makes one kind of a waterless Trap
    Seal.


    [​IMG]


    I am curious as to how others are addressing this Code requirement.

    < = =
     
  4. Keystone

    Keystone Sawhorse

    Joined:
    Feb 23, 2010
    Messages:
    728
    Likes Received:
    67
    The seal will dry out. Trap Gaurd is how we handle it.

    An old way of dealing with a floor drain that was installed as emergency only was to pour vegetable oil within but this was when workers stayed with a job for most of there career and took pride in the job & maintenance.
     
    #4 Keystone, Mar 12, 2018
    Last edited: Mar 12, 2018
    my250r11 likes this.
  5. JBI

    JBI Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    2,708
    Likes Received:
    249
    While the IPC provides a few options for maintaining a water seal, at an older Town Hall I once worked in we simply told the janitor to use more water when washing the bathroom floors to insure the trap stayed full.
     
    north star likes this.
  6. mp25

    mp25 Registered User

    Joined:
    Jun 2, 2016
    Messages:
    47
    Likes Received:
    8
    My state plumbing code (IL) provides 3 methods (code updated in 2014):
    1. addition of vegetable oil
    2. deep seal trap (8" max) - takes longer to evaporate
    3. Automatic Trap Primer
     
  7. SRK_Mech

    SRK_Mech Registered User

    Joined:
    Dec 14, 2016
    Messages:
    19
    Likes Received:
    0
    I do code review for NJ, NY State and NY City:
    Question #1 then 3: Yes. Trap primers.
    I noticed that janitors are using Swiffer instead of a mop and a bucket of water. No wonder why these rooms smell so bad.
     
  8. ADAguy

    ADAguy Sawhorse

    Joined:
    Sep 11, 2013
    Messages:
    2,260
    Likes Received:
    182
    Love you guys, so much knowledge shared but not always transmitted.

    Thank you
     
  9. Francis Vineyard

    Francis Vineyard Sawhorse

    Joined:
    Jan 1, 2010
    Messages:
    3,006
    Likes Received:
    372
    2015 IPC;
    Section 1002.4
    has been expanded to cover two additional types of trap seal protection devices and to distinguish between the different types of water-supplied trap seal protection devices.

    The latest trap seal protection device is for floor drains only and utilizes a specially designed and tested insert below the floor drain strainer plate. When water runs into the floor drain, the insert allows the water to pass and then closes to significantly reduce evaporation of the trap seal.

    1002.4.1 Trap Seal Protection. Trap seals of emergency floor drain traps and traps subject to evaporation shall be protected by one of the methods in Sections 1002.4.1.1 through 1002.4.1.4.
    1002.4.1.1 Potable Water Supplied Trap Seal Primer Valve. A potable water supplied trap seal primer valve shall supply water to the trap.
    Water supplied trap seal primer valves shall conform to ASSE 1018. The discharge pipe from the trap seal primer valve shall connect to the trap above the trap seal on the inlet side of the trap.
    1002.4.1.2 Reclaimed or Gray Water Supplied Trap Seal Primer Valve.
    A reclaimed or gray water supplied trap seal primer valve shall supply water to the trap. Water supplied trap seal primer valves shall conform to ASSE 1018. The quality of reclaimed or gray water supplied to trap seal primer valves shall be in accordance with the requirements of the manufacturer of the trap seal primer valve. The discharge pipe from the trap seal primer valve shall connect to the trap above the trap seal on the inlet side of the trap.
    1002.4.1.3 Waste Water Supplied Trap Primer Device. A waste water supplied trap primer device shall supply water to the trap. Waste water supplied trap primer devices shall conform to ASSE 1044. The discharge pipe from the trap seal primer device shall connect to the trap above the trap seal on the inlet side of the trap.
    1002.4.1.4 Barrier Type Trap Seal Protection Device. A barrier type trap seal protection device shall protect the floor drain trap seal from evaporation. Barrier type floor drain trap seal protection devices shall conform to ASSE 1072. The devices shall be installed in accordance with the manufacturer’s instructions.

    Same here in all cases where they have maintenance personnel.
     