1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Footing width table Q.

Discussion in 'Residential Building Codes' started by Pcinspector1, Nov 7, 2018.

  1. Pcinspector1

    Pcinspector1 Platinum Member

    Joined:
    Oct 28, 2009
    Messages:
    2,479
    Likes Received:
    235
    Q. The IRC 2012 Table R403.1

    What would the footing width be for a 2-story on 2,000 lb soil using poured foundation walls? Light frame construction for the walls above the foundation.

    Is 12 inches correct?

    We typically see 16-inch wide footings here, I think its for the goof factor?
     
  2. Builder Bob

    Builder Bob Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    1,920
    Likes Received:
    236
  3. Pcinspector1

    Pcinspector1 Platinum Member

    Joined:
    Oct 28, 2009
    Messages:
    2,479
    Likes Received:
    235
    Has a 20 snow load.

    Does the table indicate 12-inches minimum? It would be conventional light frame construction.

    Not sure if I understand what 8-inch solid masonry means on the table which leads me to believe it should be 21-inches?
     
  4. Ty J.

    Ty J. Sawhorse

    Joined:
    Aug 2, 2017
    Messages:
    142
    Likes Received:
    68
    12x6 is the minimum required.

    Check with the AHJ, some jurisdictions require that 1500psf be assumed unless supporting geotech indicates a greater bearing value may be used, which would require 15x6 footings..


    As a cautionary note, the minimum footing widths established under Table R403.1 are only based upon 20-ft of roof tributary at 50-psf snow load, 16-ft of floor tributary, 10-ft first story walls, and 8-ft second story walls. If your design uses spans imparting greater tributary, footings may need to be increased.

    This is reflected in the 2015 IRC by footnote "b" of Table 403.1(1). Per the 2015 IRC, footings follow the table, then are increased at a prescribed rate of 2-in to width and 1-in to depth for every 2-ft of building width over an assumed width of 32-ft.

    As an example, a 40-ft wide home with a center load bearing wall of conventional 2-story construction would require 24x10 footings (16x6 typ. + 8-ft adjustment [8x4] = 24x10).

    Generally speaking, following footnote "b" of the 2015 IRC will greatly oversize footings because it is based upon a floor and roof system bearing on a center load bearing wall. Thus, this footing is sized for 50% of all roof and floor loads. Given the 40-ft example home, it is infeasible to assume that the floor system would clear span 20-ft to the center wall, whereas roof system is manageable with trusses.
     
    Pcinspector1 likes this.
  5. Ty J.

    Ty J. Sawhorse

    Joined:
    Aug 2, 2017
    Messages:
    142
    Likes Received:
    68
    Masonry built home.

    Conventional light frame includes a typical concrete foundation.
     
    JBI and Pcinspector1 like this.
  6. JBI

    JBI Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    2,748
    Likes Received:
    264
    Don't forget the footnotes... tables are based on a 32' wide home with center bearing wall, adjustments for wider or narrower home in footnote b.
    The 2015 IRC for 2 story light frame above a basement is 16" minimum for 20# snow load and 2,000# soils.
    Remember these are 'prescriptive' provisions, not the be all and end all. They can always go above code minimum.
     
  7. HForester

    HForester Member

    Joined:
    Sep 21, 2015
    Messages:
    114
    Likes Received:
    34
    2 foot excavator bucket...get it done with some safety factor
     
  8. Pcinspector1

    Pcinspector1 Platinum Member

    Joined:
    Oct 28, 2009
    Messages:
    2,479
    Likes Received:
    235
    Any inspectors using a pocket penetrometer probe to check soil pressure?
     
  9. Pcinspector1

    Pcinspector1 Platinum Member

    Joined:
    Oct 28, 2009
    Messages:
    2,479
    Likes Received:
    235
    [​IMG] pocket Penetrometer
     
  10. Keystone

    Keystone Sawhorse

    Joined:
    Feb 23, 2010
    Messages:
    758
    Likes Received:
    78
    To anyone using a penetrometer, STOP. These devices are not to be used in determining soil bearing in a structural application. These devices are an industry joke that is another greatly marketed play item. I suggest anyone contact the manufacture of the device and they will tell you the penetrometer is not to be used in a structural application...

    At plan review we assume soil bearing to be 1500PSF.
     
    Ty J. likes this.
  11. Pcinspector1

    Pcinspector1 Platinum Member

    Joined:
    Oct 28, 2009
    Messages:
    2,479
    Likes Received:
    235
    I don't have a penetrometer or have I seen a turd party inspector use one but couldn't believe they are very accurate. With that said, I still do a footing inspection and was taught to use my heal of my boot, maybe this is for show?

    Which would you trust more?
     
  12. HForester

    HForester Member

    Joined:
    Sep 21, 2015
    Messages:
    114
    Likes Received:
    34
    Incredible.....
     
  13. Keystone

    Keystone Sawhorse

    Joined:
    Feb 23, 2010
    Messages:
    758
    Likes Received:
    78
    When I started in the direction of building inspector I spent some time with a engineering company, training and field work of soils, concrete and asphalt so I know enough to be dangerous but not smart. Ill visually look, use my foot and ball it in my hand.
     