    Dismiss Notice
    Dismiss Notice
Fryer to open flame appliance clearnace
Discussion in 'Commercial Mechanical Codes' started by fireguy, Oct 28, 2011.
  1. Codegeek
    Codegeek Sawhorse
    Jun 17, 2011
    717
    1
    That was not my point. My point was that if a standard has direction on how to more clearly help a CO in determining if something is compliant, then use it. I'm not suggesting that a CO use a document to enforce just to get their rocks off. It's those that do that give the rest of the CO's a terrible reputation.
  2. cda
    cda Sawhorse
    Oct 19, 2009
    14,755
    847
    Do not know how it works in the international community,
    But the extinguishing company installers around here do look at fryer clearance and certify the system has it
  3. beach
    beach Gold Member
    Oct 20, 2009
    853
    0
    That one got me wondering, so I checked NFPA 96 (2011) Section 12.1.2.5.1 which states: "If the fryer and the surface flames are at different horizontal planes, the minimum height of 203mm (8 in.) shall be measured from the higher of the two." (underscore mine)
    I believe you would still need a a min. 8" baffle plate if the fryer is below 8" from the cooktop
  4. mtlogcabin
    mtlogcabin Sawhorse
    Oct 17, 2009
    6,779
    553
    Just to clarify
    If the fryer is 6" below the surface flame then a minimum 2" plate would be needed to meet the 8" requirement.
    Correct
    Or do you think an 8" plate would still be required?
  5. beach
    beach Gold Member
    Oct 20, 2009
    853
    0
    My opinion is that the difference in height between the fryer and cooktop is not relevant, the min. 8" baffle gets installed on the highest of the two appliances or, if they were the same height, either one.
  6. cda
    cda Sawhorse
    Oct 19, 2009
    14,755
    847
    I believe you would still need a a min. 8" baffle plate if the fryer is below 8" from the cooktop""""
    Good point , now need to start looking at that thanks
    As we all know it is the vapors that burn, not the liquid
  7. fireguy
    fireguy Gold Member
    May 4, 2010
    577
    2
    True, but when you have a basket of onion rings dripping grease, then pass the basket over the gas charbroiler, you get fumes.
  8. cda
    cda Sawhorse
    Oct 19, 2009
    14,755
    847
    OK time to wake up this thread
    So how do you measure the sixteen inches???
    Between the fryer and any open-top flame units:
    16" (41 cm)
    From NFPA 96
    12.1.2.4
    All deep-fat fryers shall be installed with at least a 406 mm (16 in.) space between the fryer and surface flames from adjacent cooking equipment.
    Commentary::::
    It is important to note that the distance to be measured is not between appliances or even between cooking surfaces. This minimum distance is measured between the nearest edge of the deep-fat fryer appliance and the actual surface flames of any adjacent appliance. Since electric cooking appliances typically do not have flames, the distance between them and a deep-fat fryer is not an issue. Exhibit 12.1 shows a situation where the fryer is located within 406 mm (16 in.) of the other cooking equipment. However, because the other cooking equipment is electric and does not produce a flame, this separation requirement does not apply.
  9. cda
    cda Sawhorse
    Oct 19, 2009
    14,755
    847
    Barrier
    Yes or No??????????
  10. cda
    cda Sawhorse
    Oct 19, 2009
    14,755
    847
    Barrier
    Yes or No ???
    assume the two appliances are touching
Share This Page