1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Have I reached the exit yet?

Discussion in 'Commercial Building Codes' started by JPohling, Apr 11, 2018.

  1. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    13,737
    Likes Received:
    713

    Not sure agree


    Say you have a restaurant with a patio.

    Part of the exiting is through the patio

    I do not think you add the restaurant ol to the patio ol??

    Assumed patio people are gone or going when the restaurant people start leaving
     
  2. ADAguy

    ADAguy Sawhorse

    Joined:
    Sep 11, 2013
    Messages:
    2,010
    Likes Received:
    157
    With a restaurant you "never" assume anything. The volume can alter from minute to minute.
    FD looks at worse condition not owners optimum. Consider holiday and sporting event crowds.
     
  3. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    13,737
    Likes Received:
    713

    Yes but there is a design ol and exiting

    Can not control overcrowding, except to empty the place

    Set there and watch the pre paid fight till it is over.
     
  4. mtlogcabin

    mtlogcabin Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    6,571
    Likes Received:
    452
    If the door leading to the patio dining area is signed as an exit and is a raised area or enclosed with a fence or guard as required here when serving alcohol outdoors then we use the cumulative load requirements and would require two exits off the patio dining area.
     
  5. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    13,737
    Likes Received:
    713
    I am waiting for an exit plan for this thread
     
  6. JPohling

    JPohling Sawhorse

    Joined:
    Aug 16, 2011
    Messages:
    750
    Likes Received:
    29
    It is attached to my initial post???
     
    my250r11 likes this.
  7. ADAguy

    ADAguy Sawhorse

    Joined:
    Sep 11, 2013
    Messages:
    2,010
    Likes Received:
    157
    Word pictures often miss the point, your plan says it all.
    That courtyard is a real gore (collection) point.
    Wish I had opened it earlier.
    If each room were to evacuate at the same time in a panic, ouch!
     
  8. JPohling

    JPohling Sawhorse

    Joined:
    Aug 16, 2011
    Messages:
    750
    Likes Received:
    29
    Fire Marshall has agreed that this plan is acceptable. Re name the area above the stair to Egress Court (no occupancy) and we are good.

    This is an area that is say 30'x30' that is immediately adjacent to a 10'-0" wide stair. Even if the total occupant load of the building were to exit at once to this spot they would all be able to make their way to grade within a minute.
     
  9. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    13,737
    Likes Received:
    713

    Exit plan as will this thread ever end
     
  10. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    13,737
    Likes Received:
    713

    Yea

    I do not have to use my parachute
     
  11. north star

    north star Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    3,423
    Likes Received:
    176
    @ * @

    Thanks for the update **JPohling** !.......In an effort to
    promote this Forum, would the Fire Marshall in your
    topic be interested in visiting here, ...possibly becoming
    a Sawhorse ?

    I'm trying to promote this MUCH VALUED resource. :D


    @ * @
     
  12. Rick18071

    Rick18071 Sawhorse

    Joined:
    Nov 28, 2009
    Messages:
    1,218
    Likes Received:
    54
    This is a problem because the court is 30' wide than the stairway is only 10' wide. Doors have an exception but stairways don't:

    The 2nd paragraph of 2009 IBC 1027.5.1 Where an egress court exceeds the minimum required width and the width of such egress court is then reduced along the path of travel, the reduction in width shall be gradual.
     