1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

How to properly insulate a non vented roof

Discussion in 'Residential Energy Codes' started by Jake the Dog, Aug 19, 2018.

  1. Jake the Dog

    Jake the Dog Registered User

    Joined:
    Aug 19, 2018
    Messages:
    2
    Likes Received:
    0
    I am enclosing what was a screen room off the back of my house and making it living space. The rafters are double 2x8. I was planning on using an R21 batt to insulate so I would have space for airflow. My drywall installer (also a GC) said I do not need to leave space since there is actually no air flow at all since the roof has no peak.
    The inspector wants to see a higher r value. R30 would completely stuff the cavity and compress down to a value of r21 any way.
    Is it better to stuff the cavity or leave the air space?
    It should be noted also that the roof is covered in solar panels.
     
  2. Jake the Dog

    Jake the Dog Registered User

    Joined:
    Aug 19, 2018
    Messages:
    2
    Likes Received:
    0
    That's some good information. Unfortunately the roof is already up and covered in solar panels. Adding foam under the sheathing isn't really an option unless I am cutting to fit the cavities. I got a quote for spray foam but it's a lot of money (about $2200 for r30 equivalent). Any other options?
     
  3. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,657
    Likes Received:
    836
    Welcome
     
  4. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,657
    Likes Received:
    836
    Not into insulation, Lower the ceiling a little so the r 30 is not smashed??

    Maybe your best route to go all the way around is the spray in
     
  5. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,657
    Likes Received:
    836
    Ask the nice inspector where in the book is he getting the requirement::

    The inspector wants to see a higher r value.

    So you can research it!!!!!!!!!!!!

    And post the section cited here
     
  6. tmurray

    tmurray Sawhorse

    Joined:
    Jun 10, 2011
    Messages:
    1,371
    Likes Received:
    314
    The objective of the vented ceiling space is to keep your roof sheathing below freezing. Hot roofs in heating climates must be designed well in order to operate correctly. Completed incorrectly, a hot roof will cause ice damming and can cause water to enter into the living space.

    Generally, we look for at least an R50.
     
  7. mtlogcabin

    mtlogcabin Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    6,746
    Likes Received:
    543
    Compressing fiberglass insulation reduces the R-value. Ask the spray foam contractor for a pricefor applying an inch or two of spray foam and then install the R-21
     
  8. mark handler

    mark handler Sawhorse

    Joined:
    Oct 25, 2009
    Messages:
    9,654
    Likes Received:
    540
  9. Keystone

    Keystone Sawhorse

    Joined:
    Feb 23, 2010
    Messages:
    732
    Likes Received:
    67
    Can you pack down the ceiling from inside to achieve the R Value? If so will it affect the required minimum ceiling height required by code?

    We handle all of these on a case by case basis, there are times when a ceiling can't be insulated to a target R Value without significant cost, so we note the reasoning and move on to what can be achieved.
     
  10. rogerpa

    rogerpa Silver Member

    Joined:
    Nov 5, 2009
    Messages:
    212
    Likes Received:
    38
  11. rogerpa

    rogerpa Silver Member

    Joined:
    Nov 5, 2009
    Messages:
    212
    Likes Received:
    38
    Oops. All of NewJersey requires R-49. I misread the table.
     
  12. Robert

    Robert Sawhorse

    Joined:
    Jan 29, 2016
    Messages:
    147
    Likes Received:
    15
    I don't know about your code but in CA the code is very specific about unvented insulated ceilings...it spells it out 3 or four options clearly. I often use a combination of spray (non-permeable) and batt (permeable) as mtlogcabin mentioned, since spray is pricey, but another option is tight fitted rigid insulation sheets (like styrofoam with no permeability), cut to fit the joist bays...seal the perimeters. This would not require ventilation and is cheaper then spray. Batt, if used by itself, needs ventilation. When the warm air moves through batt into the cold air, it condenses, causing moisture, causing all kinds of problems.
     
  13. Rick18071

    Rick18071 Sawhorse

    Joined:
    Nov 28, 2009
    Messages:
    1,415
    Likes Received:
    98
    Are you allowed to use batts in cathedral ceilings in CA?
     
  14. Robert

    Robert Sawhorse

    Joined:
    Jan 29, 2016
    Messages:
    147
    Likes Received:
    15
    Yes, but needs to be vented above the batts. Typically the depth needed for the batt to meet energy requirements plus the required 1 1/2" airspace above the batts will mean very deep rafters, so I usually do spray or a combination of spray and batt (as long as the spray is applied to the underside of the roof sheathing).
     