1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

IBC 2012 Egress Questions

Discussion in 'Commercial Building Codes' started by Engineer22, Aug 12, 2017 at 3:40 PM.

Tags:
  1. Engineer22

    Engineer22 Member

    Joined:
    Saturday
    Messages:
    9
    Likes Received:
    0
    Hey all,

    Working on a project, and I have two basic IBC 2012 questions:

    1) Minimum # of stairs needed for a 12' ceiling height?

    2) Given project occupant load of 300, how many 36" wide doors are needed?
    [2 doors? 300 x .2 = 60" --> therefore 2 doors needed to satisfy this requirement?]

    Thanks for any guidance!
     
  2. RLGA

    RLGA Sawhorse

    Joined:
    Oct 18, 2009
    Messages:
    868
    Likes Received:
    139
    Not sure I understand the question. Two stairways are required unless a single means of egress is permitted from an upper story. If you're talking about the number of risers needed from floor to floor, then it depends. Risers are permitted to be 4 to 7 inches in height. If you want to minimize the number, start with 7 inches and divide the floor-to-floor height by 7 inches. This will give you the number of risers. If the division creates a fraction, then round up the number of risers and divide the floor-to-floor height by the revised number of risers to get the actual riser height.

    Yes. A 36-inch door actually provides about 33 inches of egress width when measured between the stop and the face of the door in a 90-degree open position. Therefore, you will have 66 inches of egress width, which exceeds the 60 inches required.
     
    Engineer22 likes this.
  3. Engineer22

    Engineer22 Member

    Joined:
    Saturday
    Messages:
    9
    Likes Received:
    0
    Thank you!

    Regarding the number of stairs needed for a 12' ceiling height:

    I meant the minimum number of risers*

    a) I assume 120" at 6" is the minimum, as it will give me 24 risers. Is this the answer?

    Dividing 120" by 7" will give me an odd number.
     
  4. RLGA

    RLGA Sawhorse

    Joined:
    Oct 18, 2009
    Messages:
    868
    Likes Received:
    139
    Actually, it is 144 inches (12 inches per foot at 12 feet = 144 inches), and, yes, it will be 24 risers using 6-inch risers.
     
    Engineer22 likes this.
  5. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    12,377
    Likes Received:
    521
  6. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    12,377
    Likes Received:
    521
    Have not heard someone calculate number of stairs.

    So where do the landings calculate in??
     
  7. mark handler

    mark handler Sawhorse

    Joined:
    Oct 25, 2009
    Messages:
    8,884
    Likes Received:
    299
    You do not design stairs to a ceiling height you design to the floor to floor height.
     
    fatboy and cda like this.
  8. fatboy

    fatboy Administrator

    Joined:
    Oct 17, 2009
    Messages:
    5,107
    Likes Received:
    211
    And the result does not have to be a whole number....................

    Assuming 144" finished floor to finished floor, you could go with 21 rises, at 6.875" (6 -7/8")=144.375, which you could lose the excess 3/8 total over the run of the stairs and easily still be compliant.
     
  9. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    5,125
    Likes Received:
    443
    Just don't miss on the 144" as that is the max and if you miss you add a landing and would have to significantly redesign...
     
    RLGA likes this.
  10. rogerpa

    rogerpa Silver Member

    Joined:
    Nov 5, 2009
    Messages:
    197
    Likes Received:
    24
    This has changed in 2015.
    R311.7.3 Vertical rise.
    A flight of stairs shall not have a vertical rise larger than 147 inches (3734 mm) between floor levels or landings.
     
  11. RLGA

    RLGA Sawhorse

    Joined:
    Oct 18, 2009
    Messages:
    868
    Likes Received:
    139
    That's true for the IRC, but for the IBC it is still 12 feet.
     
  12. PJC89

    PJC89 Well-Known Member

    Joined:
    Jul 27, 2017
    Messages:
    45
    Likes Received:
    1
    Every occupant on every story must have access to minimum of two exits (i.e., exit stairway, horizontal exit, exterior exit door). When the occupant load exceeds 500 persons access to three exits must be provided. When the occupant load exceeds 1,000 persons access to four exits must be provided.

    Each of the exit stairways must be sized to handle the occupant load it serves based on 0.3 inches/person but no less than 44 inches based on your situation. The exit door to the stairway must also be sized to handle the occupant load at 0.2 inches/person but not less than 34 inches clear width.

    Refer to Chapter 10 (number of exits and egress width) https://up.codes/viewer/general/int_building_code_2012/chapter/10/means-of-egress#10
     