    Dismiss Notice
    Dismiss Notice
Insulation requirements
Discussion in 'Residential Energy Codes' started by Brenden, Jun 9, 2017.
  1. Brenden
    Brenden New Member
    Jun 9, 2017
    1
    0
    So my house was recently damaged by fire and the assessor mentioned they would be replacing all exterior facing walls, however I live in an older home and the walls are not insulated. Would the contractor be required, by code, to install insulation when replacing the walls?
    I live in zone 4.
    Thanks!
  2. cda
    cda Sawhorse
    Oct 19, 2009
    13,185
    626
    Maybe if they pull a permit
    Will insurance pay, more than likely not
    Would I ask yes
    Should you put it in YES
  3. cda
    cda Sawhorse
    Oct 19, 2009
    13,185
    626
    Welcome
  4. tmurray
    tmurray Sawhorse
    Jun 10, 2011
    1,184
    227
    It would depend on your insurance policy. Here the insurance policy must be to reconstruct your home to current code.
  5. my250r11
    my250r11 Sawhorse
    Feb 16, 2015
    239
    71
    More than likely, if exposing the studs.
  6. rogerpa
    rogerpa Silver Member
    Nov 5, 2009
    202
    29
    I think "yes".
    Section R102.7.1 Additions, alterations or repairs.
    Additions, alterations or repairs to any structure shall conform to the
    requirements for a new structure without requiring the existing structure
    to comply with the requirements of this code,
    unless otherwise stated.
    Additions, alterations, repairs and relocations shall not cause an
    existing structure to become unsafe or adversely affect the performance
    of the building."
    Hopefuly, you have an insurance rider for codes, laws, and ordinances.
    Pcinspector1 likes this.
  7. jwilly3879
    jwilly3879 Sawhorse
    Apr 2, 2010
    100
    10
    Probably to the depth of the studs.
  8. ICE
    ICE Sawhorse
    7,075
    451
  9. steveray
    steveray Sawhorse
    Nov 25, 2009
    5,375
    534
    Fill the cavities, does not necessarily have to meet new code...
  10. mtlogcabin
    mtlogcabin Sawhorse
    Oct 17, 2009
    6,485
    415
    N1101.3 (R101.4.3) Additions, alterations, renovations or repairs.
    Additions, alterations, renovations or repairs to an existing building, building system or portion thereof shall conform to the provisions of this code as they relate to new construction without requiring the unaltered portion(s) of the existing building or building system to comply with this code. Additions, alterations, renovations or repairs shall not create an unsafe or hazardous condition or overload existing building systems. An addition shall be deemed to comply with this code if the addition alone complies or if the existing building and addition comply with this code as a single building.
    Exception: The following need not comply provided the energy use of the building is not increased:
    1. Storm windows installed over existing fenestration.
    2. Glass only replacements in an existing sash and frame.
    3. Existing ceiling, wall or floor cavities exposed during construction provided that these cavities are filled with insulation.
    4. Construction where the existing roof, wall or floor cavity is not exposed.
    5. Reroofing for roofs where neither the sheathing nor the insulation is exposed. Roofs without insulation in the cavity and where the sheathing or insulation is exposed during reroofing shall be insulated either above or below the sheathing.
    6. Replacement of existing doors that separate conditioned space from the exterior shall not require the installation of a vestibule or revolving door, provided, however, that an existing vestibule that separates a conditioned space from the exterior shall not be removed.
    7. Alterations that replace less than 50 percent of the luminaires in a space, provided that such alterations do not increase the installed interior lighting power.
    8. Alterations that replace only the bulb and ballast within the existing luminaires in a space provided that the alteration does not increase the installed interior lighting power.
Share This Page