1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Question About Corridor Doors NFPA 101 / 80

Discussion in 'Commercial Fire Codes' started by JItter77, Jan 11, 2018.

  1. JItter77

    JItter77 New Member

    Joined:
    Jan 11, 2018
    Messages:
    1
    Likes Received:
    0
    Hello,
    I work maintenance in a nursing home and have some questions regarding corridor doors. We are a single story facility with 4 wings. Each wing is basically its own smoke compartment with a 1 hour smoke wall and 1 hour rated doors / frames etc etc. Each wing consists of 15 resident rooms and some resident rooms have fire rated doors and others do not. According to NFPA 80 any door with a fire rated label must be inspected as such regardless of the surrounding walls and what not. In NFPA 101 version 2012 under corridor doors (19.3.6.3) section 19.3.6.3.3 says that "compliance with NFPA 80 is not required." How i interpret section 19.3.6.3 in general is that that corridor doors that are not part of a smokewall / firewall / hazardous rooms are only required to resist smoke and not follow the much stricter guidelines of NFPA 80 even if the door has a label. All rooms have a smoke detector and the hallway / rooms are fully on automatic sprkinlers.

    If anyone could clear this up it would be great.

    Thanks
     
  2. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,242
    Likes Received:
    781
    Welcome
     
  3. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,242
    Likes Received:
    781
  4. ADAguy

    ADAguy Sawhorse

    Joined:
    Sep 11, 2013
    Messages:
    2,214
    Likes Received:
    178
    Good question, awaiting the answer.
     
  5. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,242
    Likes Received:
    781
    Not sure if the question is clear

    Without floor plan
     
  6. Builder Bob

    Builder Bob Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    1,794
    Likes Received:
    198
    Generally, the doors to the patient rooms are required to resist the passage of smoke but do not require closures - Doors may have to meet the 20 min fire resistant opening protective, and smoke seal requirements, but generally closures are left off of patient rooms.

    Fire/smoke barriers are required to create the smoke compartment and opening protectives are required to meet NFPA 80 - Closure, latch, and resistance to hose stream test are a part of meeting NFPA 80. (most likely a double set of doors in a corridor held open by door magnets)

    See section 19.3.6.3.1 in the code and then read A 19.63.6.3.5 in Appendix A ---

    "... under normal or fire conditions are self-closing, might create a special hazard for the personal safety of a room occupant"
     
    IJHumberson likes this.
  7. FM William Burns

    FM William Burns Moderator

    Joined:
    Oct 17, 2009
    Messages:
    2,826
    Likes Received:
    74
    I may be missing something but my concern is that some of your resident rooms exist without labeled doors and are not protected in accordance with the code:

    19.3.6.1 Corridor Separation.


    Corridors shall be separated from all other areas by partitions complying with
    19.3.6.2 through 19.3.6.5(see also 19.2.5.4), unless otherwise permitted by one of the following:

    (1) Smoke compartments protected throughout by an approved supervised automatic sprinkler system in accordance with 19.3.5.8 shall be permitted to have spaces that are unlimited in size and open to the corridor, provided that all of the following criteria are met:
    (a)* The spaces are not used for patient sleeping rooms, treatment rooms, or hazardous areas.


     
  8. Sleepy

    Sleepy Active Member

    Joined:
    Jan 6, 2017
    Messages:
    57
    Likes Received:
    28
    Yes, 19.3.6.1 requires separation and then 19.3.6.2 describes the required wall construction (if sprinklered, no rating required, just resist the passage of smoke), and 19.3.6.3 describes the required doors (again, if sprinklered no rating, just resist the passage of smoke, and the doors have to have a latch, but no closer is required).

    I have always figure this was because in healthcare occupancies there is always staff available to assist patients. Part of their training, I believe, is to evacuate the patient if needed (in which case closers on doors would be in the way), or to close the door to compartmentalize smoke. If there is actual fire they would be evacuating the patients.
     
  9. Builder Bob

    Builder Bob Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    1,794
    Likes Received:
    198
    or using stay in place strategy
     
  10. tmurray

    tmurray Sawhorse

    Joined:
    Jun 10, 2011
    Messages:
    1,326
    Likes Received:
    287
    I always understood the reason why the door does not require an automatic closing device was that this would delay egress in this situation (gurneys, mobility impairments, etc.).
     