1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Space at the bottom of a Fire Door

Discussion in 'Commercial Fire Codes' started by RJJ, Aug 8, 2018.

  1. RJJ

    RJJ Platinum Member

    Joined:
    Oct 17, 2009
    Messages:
    2,836
    Likes Received:
    16
    Just wondering what you all would allow for the space located at the bottom of a fire door? Like to hear some feed back and why!
     
  2. RLGA

    RLGA Sawhorse

    Joined:
    Oct 18, 2009
    Messages:
    1,208
    Likes Received:
    287
    What do you mean by "space"? Are you referring to the gap between the floor surface and the bottom of the door?
     
  3. ADAguy

    ADAguy Sawhorse

    Joined:
    Sep 11, 2013
    Messages:
    2,260
    Likes Received:
    182
    That is what he is alluding too, at what dimension is the gap too big to affect the fire rating?
    Or, can the door swing over dissimilar flooring materials, carpet to vct without a threshold?
     
  4. RJJ

    RJJ Platinum Member

    Joined:
    Oct 17, 2009
    Messages:
    2,836
    Likes Received:
    16
    The space / gap between the floor and the bottom of the door?
     
  5. RLGA

    RLGA Sawhorse

    Joined:
    Oct 18, 2009
    Messages:
    1,208
    Likes Received:
    287
    NFPA 80 states 3/4-inch maximum, unless the door assembly has been tested with a gap greater than 3/4-inch.
     
  6. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,453
    Likes Received:
    796
    I take it the gap is only in play ...

    When the door is closed
     
  7. Paul Sweet

    Paul Sweet Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    945
    Likes Received:
    111
    The bottom of the door is at negative pressure during a fire, so air will be pulled in rather than flames & smoke escaping.
     
    RLGA likes this.
  8. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,453
    Likes Received:
    796
    That’s not how it was in Backdraft??

    I am thinking pressure may depend on the stage of the fire???
     
  9. RLGA

    RLGA Sawhorse

    Joined:
    Oct 18, 2009
    Messages:
    1,208
    Likes Received:
    287
    As a fire burns and heat rises, it draws combustion air from the lower levels, and door bottom clearances is an area where that air is drawn through. As the air is sucked through the bottom of the door in puts an inward pressure on the door (inward toward the fire). Hot air and gases build up in the upper portion of the space creating an outward pressure on the upper surface of the door. These two forces will attempt to warp the door. This is why fire doors are tested with a neutral plane at 40 inches above the floor per UL10C and NFPA 252.

    If smoke begins to be drawn back through gaps at the upper portion of the door, then the fire is starving for oxygen and hot combustible gases begin to build up inside the space (i.e., backdraft). If oxygen is suddenly introduced into the space (e.g., a window breaks), then the hot combustible gases may rapidly re-ignite (explosive-like) similar to a properly balanced fuel/air mixture.
     
    linnrg, tmurray and cda like this.
  10. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,453
    Likes Received:
    796
    Thank you

    Late in the evening to think about fire dynamics
     
  11. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    5,701
    Likes Received:
    640
    3/4" is what I remembered, but never had a copy of NFPA 80...Thanks Ron!
     
  12. RJJ

    RJJ Platinum Member

    Joined:
    Oct 17, 2009
    Messages:
    2,836
    Likes Received:
    16
    Yes thanks! I have a hard copy of NFPA 80 buried some place. Sometimes finding stuff I save is like looking for Jimmy Hoffa! 3/4 is what I remembered. Just ran across 6 doors that have been installed @ 11/4" off the floor. That is why I raised the question.
     