1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Storeroom set with deadbolt

Discussion in 'Door & Hardware forum *Sponsored by Allegion' started by ADAguy, Sep 28, 2018.

  1. ADAguy

    ADAguy Sawhorse

    Joined:
    Sep 11, 2013
    Messages:
    2,483
    Likes Received:
    207
    So, are they viewed as accessible if the room is limited to school maintenance staff only?
     
  2. LGreene

    LGreene Sawhorse
    Staff Member

    Joined:
    Oct 20, 2009
    Messages:
    1,089
    Likes Received:
    77
    If you mean a deadbolt that is separate from the lockset or latchset, technically this would not be compliant with the egress requirements - except that NFPA 101 has an exception for existing hardware on doors serving an occupant load of 3 or less (the IBC does not). The accessibility standards don't require the door to unlatch with one operation like the egress requirements do...the hardware just can't require simultaneous operations. So the application would be accessible as long as the hardware does not require tight grasping, pinching, or twisting of the wrist, if it is mounted between between 34-48" AFF, and if it meets the operable force limits (depending on which standard).
     
  3. ADAguy

    ADAguy Sawhorse

    Joined:
    Sep 11, 2013
    Messages:
    2,483
    Likes Received:
    207
    Ah Lori, as the deadbolt is only on the corridor side you can egress via the interior latch but then only if this is a storeroom set, not an independent deadbolt.
     
  4. LGreene

    LGreene Sawhorse
    Staff Member

    Joined:
    Oct 20, 2009
    Messages:
    1,089
    Likes Received:
    77
    A storeroom function just means that the outside knob/lever is always locked and the latchbolt is retracted with a key, so I wasn't sure whether you were describing a mortise or interconnected lock with an integral deadbolt, or a cylindrical storeroom function lock with a separate deadbolt.

    If turning the inside lever retracts both the latchbolt and deadbolt, that should be acceptable. If the deadbolt has to be retracted by a thumbturn before turning the lever to retract the latchbolt, this is typically only allowed for the entrance doors to dwelling units and sleeping units, or where allowed by the NFPA 101 exception for existing hardware on doors serving an occupant load of 3 or less. It's not really an accessibility issue, but it is an egress issue.
     
  5. ADAguy

    ADAguy Sawhorse

    Joined:
    Sep 11, 2013
    Messages:
    2,483
    Likes Received:
    207
    Ah but it is indeed Lori, as an operable part it must comply.
     
  6. LGreene

    LGreene Sawhorse
    Staff Member

    Joined:
    Oct 20, 2009
    Messages:
    1,089
    Likes Received:
    77
    I agree that operable parts must comply with the accessibility standards, but I'm not sure what the objection is (if there is one).
     
  7. ADAguy

    ADAguy Sawhorse

    Joined:
    Sep 11, 2013
    Messages:
    2,483
    Likes Received:
    207
    No objection, if the exterior deadbolt is separate from the latch mechanism a paddle key may be required as a Title 1 request of an employee.
     