1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Swimming pools, TD

Discussion in 'Commercial Building Codes' started by Jaber Alhaji, Aug 8, 2018.

  1. Jaber Alhaji

    Jaber Alhaji Registered User

    Joined:
    Dec 23, 2017
    Messages:
    37
    Likes Received:
    1
    In new high rise Bldg , there are swimming pools in level 2 roof. These swimming pools are located outside the building in a non covered area roof . The occupant load is 46 persons (less than 50, then the common path of travel is 23 meters), but the distance from the most remote point to the nearest stair is bigger than 50 meter. Your 2Ind Opinion per IBC, 2015 is highly appreciated.
     
  2. Jaber Alhaji

    Jaber Alhaji Registered User

    Joined:
    Dec 23, 2017
    Messages:
    37
    Likes Received:
    1
  3. RLGA

    RLGA Sawhorse

    Joined:
    Oct 18, 2009
    Messages:
    1,208
    Likes Received:
    287
    Occupied roofs are required to have means of egress per Section 1004.5. You'll need a second means of egress, not just because the common path of egress travel exceeds the maximum distance permitted, but because the code requires two exits regradless. Section 1006.3 requires that occupied roofs be provided with the number of exits or access to exits per Table 1006.3.1, and that table requires two when the occupant load is 1 to 500.

    You said this is a high-rise, so there should be at least two means of egress at the second story. Don't the pool occupants have access to both stairways?
     
  4. Jaber Alhaji

    Jaber Alhaji Registered User

    Joined:
    Dec 23, 2017
    Messages:
    37
    Likes Received:
    1
  5. RLGA

    RLGA Sawhorse

    Joined:
    Oct 18, 2009
    Messages:
    1,208
    Likes Received:
    287
    Got it--thanks.

    Not compliant.
     
  6. Jaber Alhaji

    Jaber Alhaji Registered User

    Joined:
    Dec 23, 2017
    Messages:
    37
    Likes Received:
    1
     
  7. RLGA

    RLGA Sawhorse

    Joined:
    Oct 18, 2009
    Messages:
    1,208
    Likes Received:
    287
    Still not compliant due to common path of egress travel distance exceeding 23 meters.
     
  8. Jaber Alhaji

    Jaber Alhaji Registered User

    Joined:
    Dec 23, 2017
    Messages:
    37
    Likes Received:
    1