    Dismiss Notice
    Dismiss Notice
Torque test
Discussion in 'Commercial Electrical Codes' started by ICE, Nov 23, 2017.
  1. ICE
    ICE Sawhorse
    7,152
    487
    Is there a standard procedure to be followed when inspecting a terminal torque? More often than not, the hardware is torqued and when a wrench is applied it indicates that the hardware is at or above the specified value. There is also an approach whereby the hardware is tightended under the specified value and the test sets the correct torque.
    It’s reasonable to assume that there is written instruction on the subject that can be referred to. So be a Peach and send me in the right direction. She was always willing to set me straight.
    #1 ICE, Nov 23, 2017
  2. north star
    north star Sawhorse
    Oct 19, 2009
    3,447
    177
    Haven't heard from **the Peach** in a long time.
    Anyhoo, ...in a search of the topic, I came across the
    following info:
    How can the inspector implement verification of proper torque ?
    If an inspector questions what authority he or she has to implement verification
    of proper torque, the Code is there to back you up......Section 110.3(B) in the
    National Electrical Code requires that equipment be installed according to its
    listing and labeling........This requirement includes verifying the given torque
    setting........Not only do we have the authority, but it is also our obligation as
    inspectors to ensure life safety.......An example of a torque inspection policy from
    Santa Ana, California is included in Exhibit 1.
    Before you start implementing this in your jurisdiction, make sure that you have
    the support of the Building Official........When the Building Official authorizes you
    to move forward, you become the educator for the electricians and general
    contractors.........While some electricians are very knowledgeable and are
    accustomed to using torque tools, you can’t assume that every electrician owns
    the proper tools or knows how to use them.......You may need to tell them what
    tools they will need and where they can purchase them.......They may need
    direction in locating the torque values, and you may need to help them to read
    the torque values on their torque tools.
    Which connections should be torqued ?
    All field connections must be tightened using appropriate torque tools......The
    connections that should be torqued in the field normally consist of bolts,
    connectors and terminals including the following items:
    • Breakers
    • Neutral/ground bars
    • Mechanical, insulated, piercing lug
    • Bolts on compression-type connectors
    • Mechanical lug & Lay-in lugs
    • MSB bussing, bolt-in breakers
    Although factory connections in equipment should be tightened to the proper value
    when they arrive at the job site, there may be indications of loosened connections
    apparent to the inspector........If loose connections are detected, they may need to
    be re-tightened to an appropriate torque value.
    Before you torque…
    All tools should be calibrated to allow for an accurate torque value........New torque
    devices come fully calibrated and will stay calibrated for a year.......Each year
    thereafter, recognized companies must calibrate the equipment and apply a sticker
    showing the date the calibration was done.
    The manufacturer may also require an oxide inhibitor/antioxidant for field-installed
    wiring.......Always check the manufacturer’s installation instructions.
    [​IMG]
    This information is only one Link out there on the "world wide webby."
    Tiger, do you want more info ?
    ICE likes this.
  3. ICE
    ICE Sawhorse
    7,152
    487
    Thanks North Star. My choice is method number two. It would be great to find a few more jurisdiction requirements.
  4. jwilly3879
    jwilly3879 Sawhorse
    Apr 2, 2010
    127
    25
    When the inspector came for a service install I was in the process of torquing the entrance conductors. He said he had never seen anyone use a torque wrench.
    Michael.L, Joe Engel and cda like this.
  5. conarb
    conarb Sawhorse
    Oct 22, 2009
    3,125
    212
    I have never seen an electrician torque any electrical connections, and I've built everything from supermarkets, to two cyclotrons, and one single family home with an 1,100 amp main service. I wouldn't miss it, as an owner of several airplanes I am familiar with mechanics torquing nuts and bolts.
    Looks like our Tiger has done it again, he has figured out a way to drive construction costs even higher, maybe the ICC could establish a yearly award and name it "The Tiger Award" for the inspector who establishes the most innovative way to increase costs.
  6. ICE
    ICE Sawhorse
    7,152
    487
    Well then conarb, I doubt that the cost of doing business ever got in your way. I always require a torque wrench test on commercial electrical equipment. A strict application would cause all residential electrical to be torque tested. And trust me with this, residential is loosey goosey.
    Having built more airplanes than you've owned, I too know a thing or two about nuts and bolts. The average electrician, not so much.
    Unless forewarned, electricians button everything up and request an inspection. I show up and ask for the torque wrench that they don't have. Not a problem...we'll meet again soon.
    At the next attempt we set the torque wrench and go to work. Invariably I am told that the terminals were uniformly loose prior to my intervention. Several contractors have told me that the terminals were so loose that they are concerned about the jobs that they have done in the past.... That's how loose they are.....losing sleep loose.
    #6 ICE, Nov 24, 2017
  7. north star
    north star Sawhorse
    Oct 19, 2009
    3,447
    177
    Alright Tiger, here are three more Links to information on Torquing.
    One of the Links is from U.L.......Another Link is from the San Diego
    Chapter of the ICC.........This particular Link has a few of the cities in the
    San Diego Chapter.......You may want to contact them for their procedures.
    Link # 1: https://www.e-hazard.com/blog/lets-have-a-torque-talk-electrical-connections-and-torque-requirements/
    Link # 2: http://www.iccsandiego.org/text/News/2014_Electrical_Newsletters.pdf
    Link # 3: https://library.ul.com/wp-content/uploads/sites/40/2015/02/Electrical-Connections-Issue-2-2013.pdf
    Some good information in all three Links. :D
    ICE likes this.
  8. cda
    cda Sawhorse
    Oct 19, 2009
    13,973
    742
  9. cda
    cda Sawhorse
    Oct 19, 2009
    13,973
    742
  10. ICE
    ICE Sawhorse
    7,152
    487
    On more than one occasion they provided a ft.lb. wrench for an inch lb. torque..... or they have the wrench still in the wrapper hoping that a different inspector shows up and doesn't require a torque test....that way the wrench can be returned to the store. Too often they lack the allen head or socket that fits the hardware. There won't be any advance work to write down the torque values for each different size terminal.... so I waste time while they find that out. And then there's the cheapest wrench available....it has a pointer.
    i have had to show them how to hold a terminal lug with a wrench or pliers to keep from ripping it loose. Sometimes I have to drag a job into compliance.
  11. conarb
    conarb Sawhorse
    Oct 22, 2009
    3,125
    212
    The only torquing I see done on jobs is by the Special Inspector inspecting structural steel, I've watched them and they log all the values as they torque the bolts and nuts, copies of their reports are given to the structural steel contractor along with me, I then give copies of all special inspections to my structural engineer and the field inspector. Torque logs go right along with weld inspection logs and UT logs. I recently found loose nuts on an entire post to beam connection, I made the steel contractor come back and tighten them up but didn't insist on torquing them.
  12. Pcinspector1
    Pcinspector1 Platinum Member
    Oct 28, 2009
    2,238
    185
    ditto
    I've been an inspector for several years and have not been asked by any BO above me to enforce this requirement. I see a lot more issues in the box than this.
    Is there any truth that Aluminum SE is the reason for this requirement due to shrinkage?
  13. Rick18071
    Rick18071 Sawhorse
    Nov 28, 2009
    1,250
    58
    In large commercial jobs I tell the electrician that I will be expecting them to torque connections. I like to see the tools and I have them mark the terminals that they are torqued for my inspection. Sometimes on large voltage I like to witness the torquing. Just witnessed one on a 45,000 v transformer a few days ago.
  14. cda
    cda Sawhorse
    Oct 19, 2009
    13,973
    742
    Any loose electrical connection can cause a high resistance fire.
    Picking on the Canadians and this is a wire nit connection.
    Joe Engel and tmurray like this.
  15. Mark K
    Mark K Platinum Member
    May 12, 2010
    1,281
    48
    I believe that this became a concern after problems with the use of aluminum wire. The problem is that aluminum is more likely to creep thus resulting in a loose connection.
  16. cda
    cda Sawhorse
    Oct 19, 2009
    13,973
    742
    Or if any type wire connection is not tight,
    There can be high resistance heating
  17. Norcal
    Norcal Member
    Aug 8, 2016
    14
    2
    A improperly torqued copper connection is just as bad as a improperly torqued aluminum one.
  18. conarb
    conarb Sawhorse
    Oct 22, 2009
    3,125
    212
    Tiger:
    This is the solution to your screw driver problem, demand that the electrical contractor (or solar contractor) be there with a torque wrench to show you that the connections are properly torqued, in the meantime buy stock in companies that make torque wrenches.
  19. ICE
    ICE Sawhorse
    7,152
    487
    Some percentage of electrical connections never see a torque wrench. With residential that would be 100%. So does it really matter or is torque requirements a result of engineers being in charge?
    With non-residential and I've come across many that were loose or too tight. Many inspectors don't even mention torque; so rest assured that lots of installations are loose or too tight. I'm not hearing about connections bursting into flames.
    Several contractors have become concerned about their past work once I introduced them to the concept. "Way loose" was a term they used. One guy said that he was losing sleep over it.
  20. Michael.L
    Michael.L Sawhorse
    May 10, 2018
    109
    17
    At my last job, I oversaw the construction of a 1MW solar system at an industrial location. The contractor hired to do the job was a real piece-of-work. He didn't have a firm grasp of the electrical code, had his crew do lots of "wing-it in the field" installation techniques. Didn't have many of the necessary specialized equipment needed for the job, including not having a torque wrench. When they suddenly had to do some torque demonstrations of the solar panel framework fittings for the design engineer, they had to borrow one of my personal torque wrenches. I was not pleased.
    After the system was completed and they left the job, we started having issues with one of our 250KW central inverters. After hours of testing and troubleshooting, I discovered the problem to be a loose connection in an electrical terminal. I ended checking all of them and none were properly torqued.
    fatboy and ICE like this.
Share This Page