Reading this section and thinking it is going to ruin the self storage industry. (or make people throw stuff away)...Would you all apply this to a self storage facility as I believe the majority of what is stored there is furniture? Not that big of a deal for a one story, but a 2 story would get really tough unless the industry has already addressed this. I just dealt with one that was 2003 based and it was a nightmare to get them to understand fire ratings (barriers) and eventually they sprinklered to get a 2 story...What are you seeing out there?
[F] 903.2.9 Group S-1. An automatic sprinkler system shall
be provided throughout all buildings containing a Group S-1
occupancy where one of the following conditions exists:
1. A Group S-1 fire area exceeds 12,000 square feet
(1115 m2).
2. A Group S-1 fire area is located more than three stories
above grade plane.
3. The combined area of all Group S-1 fire areas on all
floors, including any mezzanines, exceeds 24,000
square feet (2230 m2).
4. A Group S-1 fire area used for the storage of commercial
trucks or buses where the fire area exceeds 5,000
square feet (464 m2).
5. A Group S-1 occupancy used for the storage of upholstered
furniture or mattresses exceeds 2,500 square feet
(232 m2).
[F] 903.2.9 Group S-1. An automatic sprinkler system shall
be provided throughout all buildings containing a Group S-1
occupancy where one of the following conditions exists:
1. A Group S-1 fire area exceeds 12,000 square feet
(1115 m2).
2. A Group S-1 fire area is located more than three stories
above grade plane.
3. The combined area of all Group S-1 fire areas on all
floors, including any mezzanines, exceeds 24,000
square feet (2230 m2).
4. A Group S-1 fire area used for the storage of commercial
trucks or buses where the fire area exceeds 5,000
square feet (464 m2).
5. A Group S-1 occupancy used for the storage of upholstered
furniture or mattresses exceeds 2,500 square feet
(232 m2).