• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Defining a "Room" for I-4

JenniferinHouston

Registered User
Joined
Mar 6, 2020
Messages
9
Location
Houston, TX
We are converting a quality lease house to an (I-4) nonprofit daycare for 10 children ages 6 weeks- 3 years old. The code indicates rooms where care is provided must have an exterior exit (or sprinklers). To accommodate this the landlord is allowing us to convert a couple of the bedroom windows into doors (for example, one to be used as the crib/ sleeping room and the other as the play room with each opening to the backyard). Does anyone know if this code is interpreted so strictly that it would prevent us from even bringing the children into the dining room for lunch unless it also had an exterior door? Also, one of the bedrooms is directly next to the front door. In a fire we would surely just go out the front-- must I also add a door to that room as well? This seems extreme. The house is only 1700 sq ft and already has 4 exterior doors.
 
Do egress windows count as emergency exits?
What is a “quality lease house”?
 
Welcome

Houston you have a problem.


First if you have the doors to the outside you are an “E” occupancy



The I-4 kicks in for age and no doors to outside.

1. yes the children can wonder, it is just the room designated for the care, has to have the door.

2. No you can go through a room to get out, so the front room has to have a door directly to the outside.

3. you also have to make the great state of Texas day care inspector happy.


Is this in an incorporated city?? Or County area??
 
Welcome

Houston you have a problem.


First if you have the doors to the outside you are an “E” occupancy



The I-4 kicks in for age and no doors to outside.

1. yes the children can wonder, it is just the room designated for the care, has to have the door.

2. No you can go through a room to get out, so the front room has to have a door directly to the outside.

3. you also have to make the great state of Texas day care inspector happy.

___________________________
1. Is there a code that says the room designated for care must have a door? If so, would you mind sending me the code number. I think I missed that.
2. What if we didn't have a door on it? I want to turn it into a children's library. If it opened into the entry hall is that enough flow to consider it not separated?
3. :)
4. This is in the incorporated part. 77003 in Houston.


Is this in an incorporated city?? Or County area??
 
I want to make sure I understand, CDA. Are you thinking we can't be I-4 bc we must be E (due to outside doors)? I spoke to an architectural firm here in town (they build churches and schools) and they're the ones that told me that I-4 classification. They knew our kids ages. Do you think that might be incorrect?
 
Section 1006.2.2.4 states two exits or exit access doorways are required from "day care facitilies, rooms or spaces." This does not require every day care room to have two means of egress. Your building is a facility, so it must provide two means of egress. If the day care was a tenant (multiple rooms) in an office building, for example, the tenant space must have two means of egress. If the day care was just one room in a church building, then that room would be required to have two means of egress.
 
You are an I-4 if

children under the age of two

and


The room does not:::

each of these child care rooms has an exit door directly to the exterior,


308.6 Institutional Group I-4, Day Care Facilities

Institutional Group I-4 occupancy shall include buildings and structures occupied by more than four persons of any age who receive custodial care for fewer than 24 hours per day by persons other than parents or guardians, relatives by blood, marriage or adoption, and in a place other than the home of the person cared for. This group shall include, but not be limited to, the following: Adult day care Child day care


308.6.1 Classification as Group E

A child day care facility that provides care for more than four but not more than 100 children under the age of two, where the rooms in which the children are cared for are located on a level of exit discharge serving such rooms and each of these child care rooms has an exit door directly to the exterior, shall be classified as Group E. See Section 427 for special requirements for Day Care.
 
To add to my post above, the inclusion of "rooms or spaces," in my opinion, is superfluous. The IBC definition of a "facility" is "All or any portion of buildings, structures, site improvements, elements and pedestrian or vehicular routes located on a site."

In the three examples I provided in my previous post, each day care described can be considered a facility by definition. Thus, the mention of "rooms or spaces" just confuses the issue as the original post clearly illustrates.

To get even more geeky about it, the IBC tends to not use the Oxford comma (anywhere), which could also add to the confusion of interpreting the code if someone is not so grammatically inclined. If the Oxford comma was used, then the code requirement would have stated: "...facilities, rooms, or spaces." Thus, each item is clearly delineated as being optional in the series; whereas, without the additional comma (as it is currently printed), the sentence could be interpreted to read as follows: "...facilities and rooms or spaces." Thus, based on this interpretation, all facilities and each room or space would be required to provide two means of egress. However, I don't think that was the intent--but it could be interpreted that way.

Don't believe me? Here's a case that was decided because of a lack of a comma: https://www.huffpost.com/entry/oxford-comma-court-case-ruling-overtime_n_58cad41ae4b0ec9d29d9dd28
 
You are an I-4 if

children under the age of two

and


The room does not:::

each of these child care rooms has an exit door directly to the exterior,


308.6 Institutional Group I-4, Day Care Facilities

Institutional Group I-4 occupancy shall include buildings and structures occupied by more than four persons of any age who receive custodial care for fewer than 24 hours per day by persons other than parents or guardians, relatives by blood, marriage or adoption, and in a place other than the home of the person cared for. This group shall include, but not be limited to, the following: Adult day care Child day care


308.6.1 Classification as Group E

A child day care facility that provides care for more than four but not more than 100 children under the age of two, where the rooms in which the children are cared for are located on a level of exit discharge serving such rooms and each of these child care rooms has an exit door directly to the exterior, shall be classified as Group E. See Section 427 for special requirements for Day Care.
What code edition are you pulling this from? The reference to Section 427 is not mentioned in any IBC edition I have (which is all of them), which means it must be some local amendment.
 
What code edition are you pulling this from? The reference to Section 427 is not mentioned in any IBC edition I have (which is all of them), which means it must be some local amendment.


Close.
From 2015

ok 2 1/2 or less

but door directly to outside



0500718D-9DC7-4C80-95E5-0EDD059D94DD.jpeg
 
To add to my post above, the inclusion of "rooms or spaces," in my opinion, is superfluous. The IBC definition of a "facility" is "All or any portion of buildings, structures, site improvements, elements and pedestrian or vehicular routes located on a site."

In the three examples I provided in my previous post, each day care described can be considered a facility by definition. Thus, the mention of "rooms or spaces" just confuses the issue as the original post clearly illustrates.

To get even more geeky about it, the IBC tends to not use the Oxford comma (anywhere), which could also add to the confusion of interpreting the code if someone is not so grammatically inclined. If the Oxford comma was used, then the code requirement would have stated: "...facilities, rooms, or spaces." Thus, each item is clearly delineated as being optional in the series; whereas, without the additional comma (as it is currently printed), the sentence could be interpreted to read as follows: "...facilities and rooms or spaces." Thus, based on this interpretation, all facilities and each room or space would be required to provide two means of egress. However, I don't think that was the intent--but it could be interpreted that way.

Don't believe me? Here's a case that was decided because of a lack of a comma: https://www.huffpost.com/entry/oxford-comma-court-case-ruling-overtime_n_58cad41ae4b0ec9d29d9dd28



in Texas there is a State day care regulator

They will actually bring out the tape measure and measure each room.

From that they determine how many children can be in each room.

Plus divide them by age

Normally their occupant load is less than what we calculate.

Since I have been doing this, now in three cities, it has always been each room needs a door to the outside, to eliminate I-4. Never have been challenged
 
in Texas there is a State day care regulator

They will actually bring out the tape measure and measure each room.

From that they determine how many children can be in each room.

Plus divide them by age

Normally their occupant load is less than what we calculate.

Since I have been doing this, now in three cities, it has always been each room needs a door to the outside, to eliminate I-4. Never have been challenged
I agree, to make it a Group E, a door must open directly to the exterior. However, I don't think making it a Group E is what the OP was intending to do--I think they were planning to keep it a Group I-4. The Group E allows some minor relaxation of code requirements over the Group I-4, which is why they provide the alternative.
 
I agree, to make it a Group E, a door must open directly to the exterior. However, I don't think making it a Group E is what the OP was intending to do--I think they were planning to keep it a Group I-4. The Group E allows some minor relaxation of code requirements over the Group I-4, which is why they provide the alternative.


I think she is not getting good info, and wants to be an E.

If the rooms do not have doors directly to the outside, the building would require a fire sprinkler system.


I think this is unamended::


903.2.6 Group I

An automatic sprinkler system shall be provided throughout buildings with a Group I fire area.

Exceptions:

1. An automatic sprinkler system installed in accordance with Section 903.3.1.2 shall be permitted in Group I-1 Condition 1 facilities.

2. An automatic sprinkler system is not required where Group I-4 day care facilities are at the level of exit discharge and where every room where care is provided has not fewer than one exterior exit door.

3. In buildings where Group I-4 day care is provided on levels other than the level of exit discharge, an automatic sprinkler system in accordance with Section 903.3.1.1 shall be installed on the entire floor where care is provided, all floors between the level of care and the level of exit discharge and all floors below the level of exit discharge other than areas classified as an open parking garage.





I normally tell prospective day cares, locate the younger children in the rooms that already have doors to the outside.
 
I think you are right, now that I look at it from the sprinkler vs. no sprinkler perspective.
 
This is the house: 428 Middle, Houston. How can I make this thing day care facility ready where the kids can go (in a group with a teacher) in and out of every room except the kitchen?
 
My plan was to convert a window to a door in each of the tow back bedrooms, but not the front one. I hoped to make the font one a children's library. As for the one's with the (new) exterior exits the one nearest the backyard would be our play room and the middle one our crib room. However, I'd hoped the children could still eat in the dining room for meals, etc.
 
My plan was to convert a window to a door in each of the tow back bedrooms, but not the front one. I hoped to make the font one a children's library. As for the one's with the (new) exterior exits the one nearest the backyard would be our play room and the middle one our crib room. However, I'd hoped the children could still eat in the dining room for meals, etc.


As stated before the room identified, to the state, that will be used for actual day care, where the children will be the majority of the time, 2 1/2 years and younger,,,,

Shall have a door direct to the outside.

If they are in a dining room or play room or other for an hour or so, do not worry about those doors.

So cheapest route is locate the 2 1/2’s in the rooms you wish to convert the windows to doors.



How many total children are you trying to get approved for??????
 
Yes, you got it. It's a house, so the rooms are not large. We went to the house again tonight. I think my ideal is to add only ONE pair of exterior french doors on the back bedroom heading into the yard and then join the two back bedrooms so it's one large (albeit weirdly shaped) space. The front room would be our crib room for sleeping. The pickle I'm in is there's no real way to add another exterior door to that front room. I think CPS is going to say no to that even though Its SO close the front door. I mean literally you walk out the bedroom and you're standing in front entry... Rules are rules though, so I doubt they'll bend.
 