Yikes
SAWHORSE
Proposed A-2 restaurant 24'x65', two stories plus basement, sprinklered, built out to property lines on both sides and rear (it's a very narrow lot!). Front court (open to the sky) will have an outdoor bar, dining patio, and 12" tall wheelchair ramp to public R.O.W.
Once the basement occupants join up with the first floor occupants, the cumulative occupancy load at the first floor exceeds 49 and now the first floor is definitely A-2 occupancy.
Q1: Does having the B accessory exit through the A-2 somehow limit the B occupancy to 75' CPET instead of the 100' normally allowed to a sprinklered B occupancy? does the B Occupancy get treated like an "A" occupancy for CPET just because it passes through the CPET?
Q2: When a B occupancy is accessory to an A occupancy per 303.1.2 (either exception #1 or 2), does it still need to have the 1 hr. occupancy separation described in table 508.4?
- 2nd floor is <750 SF, and has 45 occupants going down a stair and discharging directly to the exterior front dining patio / exit court.
- Ground floor has some indoor dining, elevator, and the main kitchen.
- Basement has a bar/dining area, <750 SF, and has only on egress path, a single stair going up to the first floor. Including the stairway path, CPET from basement though first floor to exterior front dining patio / exit court is greater than 75' but less than 100'.
Once the basement occupants join up with the first floor occupants, the cumulative occupancy load at the first floor exceeds 49 and now the first floor is definitely A-2 occupancy.
Q1: Does having the B accessory exit through the A-2 somehow limit the B occupancy to 75' CPET instead of the 100' normally allowed to a sprinklered B occupancy? does the B Occupancy get treated like an "A" occupancy for CPET just because it passes through the CPET?
Q2: When a B occupancy is accessory to an A occupancy per 303.1.2 (either exception #1 or 2), does it still need to have the 1 hr. occupancy separation described in table 508.4?