Does this qualify as “one-story portion”?

Yikes

SAWHORSE
Joined
Nov 2, 2009
Messages
4,105
Location
Southern California
The image below shows 2022 CBC table 601, footnote b.3, and my building concept. My building has a one story portion of an A occupancy, but it is on the 2nd level, above a parking garage. Put another way, it is not 2 stories of Type A; only one story is Type A.
Does it still qualify under this footnote? The owner wants exposed wood trusses.

IMG_3322.jpeg
 
Last edited:
Only if the garage story is constructed as a "podium building," which essentially makes the roof of the garage a new ground plane, on top of which you then construct a one-story building. It has nothing to do with use group classification. See IBC 510.2
 
Only if the garage story is constructed as a "podium building," which essentially makes the roof of the garage a new ground plane, on top of which you then construct a one-story building. It has nothing to do with use group classification. See IBC 510.2
The A-3 use has an occupant load >300, so I can’t use the podium exception.
 
A little more info:
1. Truth be told, the owner had already removed the existing fire-rated ceiling from 1962 and exposed the wood trusses with an approved set of plans from 2007. The plans still called the building type III-1hr (type Iii-A) but there was no code analysis describing how this could possibly be approvable, so I was trying to de-rate the building down to Type IIIB.

However, I just remembered that prior to 2015, the IBC / CBC allowed for sprinklers to serve as a substitution for 1 hour construction when not otherwise being utilized for an area increase. So that must be how it previously got approved. I will not attempt any further de-rating of the building, and will keep it at Type III-A.
 