Hello,
According to IRC 2009:
M1601.4.1 Joints and seams.
Joints of duct systems shall be made substantially airtight by means of tapes, mastics, liquid sealants, gasketing or other approved closure systems. Closure systems used with rigid fibrous glass ducts shall comply with UL181A and shall be marked181A-P for pressure-sensitive tape, 181A-M for mastic or 181 A-H for heat-sensitive tape. Closure systems used with flexible air ducts and flexible air connectors shall comply with UL 181B and shall be marked181B-FX for pressure-sensitive tape or 181B-M for mastic. Duct connections to flanges of air distribution system equipment or sheet metal fittings shall be mechanically fastened. Mechanical fasteners for use with flexible nonmetallic air ducts shall comply with UL 181B and shall be marked 181B-C. Crimp joints for round metal ducts shall have a contact lap of at least 11/2 inches (38 mm) and shall be mechanically fastened by means of at least three sheet-metal screws or rivets equally spaced around the joint. Closure systems used to seal metal ductwork shall be installed in accordance with the manufacturer's installation instructions.
How serious is this if the tape is not marked or worse, does not conform to the proper UL standard? How would one respond to something like this:
"The HVAC company that did the installation has confirmed that their supply house only supplies UL rated tape and that tape is labeled on the package but not on the tape face."
Would a home inspector agree to this?
Thank you.
According to IRC 2009:
M1601.4.1 Joints and seams.
Joints of duct systems shall be made substantially airtight by means of tapes, mastics, liquid sealants, gasketing or other approved closure systems. Closure systems used with rigid fibrous glass ducts shall comply with UL181A and shall be marked181A-P for pressure-sensitive tape, 181A-M for mastic or 181 A-H for heat-sensitive tape. Closure systems used with flexible air ducts and flexible air connectors shall comply with UL 181B and shall be marked181B-FX for pressure-sensitive tape or 181B-M for mastic. Duct connections to flanges of air distribution system equipment or sheet metal fittings shall be mechanically fastened. Mechanical fasteners for use with flexible nonmetallic air ducts shall comply with UL 181B and shall be marked 181B-C. Crimp joints for round metal ducts shall have a contact lap of at least 11/2 inches (38 mm) and shall be mechanically fastened by means of at least three sheet-metal screws or rivets equally spaced around the joint. Closure systems used to seal metal ductwork shall be installed in accordance with the manufacturer's installation instructions.
How serious is this if the tape is not marked or worse, does not conform to the proper UL standard? How would one respond to something like this:
"The HVAC company that did the installation has confirmed that their supply house only supplies UL rated tape and that tape is labeled on the package but not on the tape face."
Would a home inspector agree to this?
Thank you.