• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Restaurant occupancy - convert unused attic into kitchen space

Morphdesigns

Sawhorse
Joined
Dec 4, 2013
Messages
44
Location
Waupun
Working on an existing 2 story+attic restaurant. VB Construction, 4000 sqft ground floor, 3500 sqft 1st floor, 900 sqft attic. 2009 IBC states A-2/VB can only be 1 story. Original construction was late 1800's, was last remodeled in 2003 and followed the current state code. (the state I am in, Wisconsin, had their own code) They adopted the IBC code the following year. This building is built into a hill, so the ground floor exits at grade at the front, the 1st floor exits at grade at the back.
Current posted Occupant load, ground flr @ 96, 1st flr @ 130. Kitchen is at ground level. Each level contains bar and dining areas. This restaurant is out in the country, so it has a well, no municipal water supply.

He wants to convert the small, currently unoccupied storage, attic space into a kitchen. It currently has 1 stair that leads directly outside from this attic space.

We are on IBC 2009, so current codes states:
VB A-2 - max 1 story w/ max. 6000 sqft/flr
IBC 903.2.1.2 - (2) need to sprinkler if fire area has an occupant load of 100 or more (1st floor has load of 130)
(3) Need to sprinkler if fire area is located on a floor other than a level of exit discharge serving such occupancies (current attic space / proposed kitchen is on level above)


Do to costs, he is not in favor of a full sprinkler system. We looked at a type of chemical fire suppression tool, but then found out that it cannot be used in occupied areas.

Has anybody worked on a facility like this and get it to pass? We were looking at doing a variance, but you need to have a system / rational for providing an equivalent degree of safety if we do not do a sprinkler system.
 
Should be using Chapter 34 for existing buildings and if it's only attic area that's being worked on it would be a partial change of occupancy as applicable.
The IEBC where adopted encourages modifications for impracticalities especially if it's an historic designated structure.
 
If this was my project, I would look at options of adding the kitchen onto the side of the building instead of going up into the attic. You could do a simple addition and fire separate it with masonry and a door with a magnetic hold-open. Who wants stairs up to a kitchen anyway?
 