• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Motor Disconnect Location

Looks like you have to reach over the conveyor. If that's the case no.Will not meet clearance requirements. On top of that, you just can't get to it safely it would appear.

BSSTG
 
steveray is correct about the no working space required for a switch and I know that you will disagree. Where's the motor and can you see the disconnect from the motor?

 
With that located in that position it certainly would be a real pain to put a lock on the switch for LO/TO it even worse try to remove it!
 
# ~ #

The term "Readily Accessible" comes to mind [ RE: Article 100, Definitions ],
as it applies to Article 430.102.

I vote "non compliant", because no one should have to climb over anything
to access this disconnect.

# ~ #
 
The disconnect clearly doesn't have the required working clearances mandated in 110.26, and it's not a "switch."

VIOLATION
 
No apparent violation from picture - provided the working clearances in FRONT of the equipment comply to the applicable condition 1 -2-3 of table 110.26(A) (1) for the voltage to ground at the terminals and the notes to the table.
 