• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Signage required above portable exinguishers in cabinets?

JPohling

Sawhorse
Joined
Aug 16, 2011
Messages
1,590
Location
San Diego
2013 California Building Code governs. High rise Type 1A construction. Building inspector, not fire is requiring that we install these flag type 3D signs above the FE cabs in common areas and inside suites.
I do not see that as a code requirement anywhere in the CBC. Is this a fire code requirement?
 
2013 California Building Code governs. High rise Type 1A construction. Building inspector, not fire is requiring that we install these flag type 3D signs above the FE cabs in common areas and inside suites.
I do not see that as a code requirement anywhere in the CBC. Is this a fire code requirement?


Ask the nice inspector for code section, so you can review it

But,

Is the cabinet door solid, so you do not know what is in it???

If solid door does it say fire extinguisher on the door??
 
IFC


6 Unobstructed and unobscured.
Portable fire extinguishers shall not be obstructed or obscured from view. In rooms or areas in which visual obstruction cannot be completely avoided, means shall be provided to indicate the locations of extinguishers.
 
Thanks guys! looks like it is a stretch to require signs when the extinguishers are located along the normal path of travel and not obstructed.
 