• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Zone 5 insulation Requirements?

FKNY

Registered User
Joined
May 28, 2017
Messages
1
Location
Clay, ny
I have a contractor building me a home in upstate NY, zone 5. The builder is using 2'x4' walls. The builder is using R13 in the walls and house wrap on the outside. Is this to NY codes and Energy Star v3.1 requirements?
 
Welcome

May be Tuesday till you hear an answer.

If that is what was approved by the building dept, more than likely meets "minimum" code.

As the owner you can always request a higher R.
 
Here is an easier source

It is from the 2009 more than likely had not changed

BUT Check!!

https://energycode.pnl.gov/EnergyCodeReqs/?state=New York



h. "13+5" means R-13 cavity insulation plus R-5 insulated sheathing. If structural sheathing covers 25 percnt or less of the exterior, insulating sheathing is not required where structural sheathing is used. If structural sheathing covers more than 25 percent of exteriror, structural sheathing shall be supplemented with insulated sheathing of atleast R-2.
 
New York state currently uses an amended version of the 2015 IRC (https://codes.iccsafe.org/public/document/toc/446/)

Table N1102.1.2, Zone 5 requires R-20 or R-13+R-5 for wood framed walls.

If that is what was approved by the building dept, more than likely meets "minimum" code.
R105.4 Validity of permit.
The issuance or granting of a permit shall not be construed to be a
permit for, or an approval of, any violation of any of the provisions of
this code or of any other ordinance of the jurisdiction.
Permits
presuming to give authority to violate or cancel the provisions of this
code or other ordinances of the jurisdiction shall not be valid. The
issuance of a permit based on construction documents and other data
shall not prevent the building official from requiring the correction of
errors in the construction documents and other data. The building
official is authorized to prevent occupancy or use of a structure where in
violation of this code or of any other ordinances of this jurisdiction.

I can't speak to the requirements of Energy Star v3.1 but I'd guess what your builder is doing won't pass that either.
 
New York state currently uses an amended version of the 2015 IRC (https://codes.iccsafe.org/public/document/toc/446/)

Table N1102.1.2, Zone 5 requires R-20 or R-13+R-5 for wood framed walls.


R105.4 Validity of permit.
The issuance or granting of a permit shall not be construed to be a
permit for, or an approval of, any violation of any of the provisions of
this code or of any other ordinance of the jurisdiction.
Permits
presuming to give authority to violate or cancel the provisions of this
code or other ordinances of the jurisdiction shall not be valid. The
issuance of a permit based on construction documents and other data
shall not prevent the building official from requiring the correction of
errors in the construction documents and other data. The building
official is authorized to prevent occupancy or use of a structure where in
violation of this code or of any other ordinances of this jurisdiction.

Is there no sheathing under the house wrap?

I can't speak to the requirements of Energy Star v3.1 but I'd guess what your builder is doing won't pass that either.
 