• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Sub-floor sheeting install Q.

SCBO1

Platinum Member
Joined
Oct 28, 2009
Messages
4,351
Location
MID WEST
Has anyone seen 3/4" OSB floor sheeting installed where the joints are not staggered? 20x24 room addition with the 4x8 ends butted to each other. In my 30 years of inspection and construction I have never seen this done before? Homeowner mistake. It's glued and will have concrete board and tile floor added at the finish stage. Would you request this be tore out and redone or do you think that concrete board placed and staggered over the seams will suffice?
 
Sounds like a novice error to me. I think it's a "general good carpentry" practice. APA Sturdi floor specs recommends "staggered end joints" in their drawings but not in the text. Can you have the joints blocked?
 
You also indicate that they are "butted? No space between?
What are they attached with (nails, screws, ringshanks,) ?
Are attachments into solid materlal without shiners?
 
Joe, you are correct a novice error. All the end butts land on floor joist.

ADAguy, attached with gun nails into FJ's and not much space between butts.
 
Agree that it is an error, but 3/4" is typically tongue and groove, so possibly less critical?
 
What of side to side, solid blk'g beneath?, did nail heads depress surface of panels (over driven?)
 
No over driven nails and no blocking between FJ's, OSB is T&G. FJ's on 16-inch O/C, not much deflection. I wondered if if cold be strapped prior to cement board application or even if that would be necessary?
 