• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,022
Location
Somewhere Too Hot & Humid
Now this should be a great topic of discussion. Let's evaluate a situation that I have encountered before.

In a mobile home park certain sections in groups of 4 to 6 have an underground electrical service that supplies 4-6 meters and service disconnects.

Then, each of those 4-6 service disconnects travel UG to another area between mobile homes where they supply a sub-feed panel mounted on a 4x4 or 6x6 pole when then sub-feeds an individual mobile home that has its own panelboard inside (set up as a sub of course).

So, we know that the service has to have ground rods since it is just on poles and it is OK for all 4-6 disconnects to share the same set of ground rods (no ufer or CEE)

BUT.......

Is the first sub-feed considered another structure since a pole with plywood meets the definition of a structure just like the mobile home? If so, do you also require ground rods at the 1st sub-feed and at the mobile home?
 