There are many instances where it either pays to be a multi-discipline inspector (I am but no longer believe it that) or when the inspectors and plan reviewers need to talk. Here is one such example:
In a major repair garage, the pit is often a troublesome spot. NEC 511.3(C)(3) allows the pit area's classification to be either Class 1, Division 1 or Class 1, Division 2 based on whether or not ventilation is provided, specifically 4 air exchanges per hour. (it used to be 4 exchanges)
The electrical inspector is often told one thing but unless it can be verified by the mechanical inspector, all is lost. I have witnessed similar situations in other overlap disciplines.
Thoughts?