• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Required Bathroom Receptacles in Dwelling Units

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,028
Location
Somewhere Too Hot & Humid
If a house has 4 bathrooms and the electrician runs a 20A circuit to feed all 4 bathroom receptacles only, is that code compliant? I am talking about required circuits, not GFCI protection or anything else.
 
210.11(C)(3) Bathroom Branch Circuits.
In addition to the number of branch circuits required by other parts of this section, at least one 120-volt, 20-ampere branch circuit shall be provided to supply a bathroom receptacle outlet(s). Such circuits shall have no other outlets.
Exception: Where the 20-ampere circuit supplies a single bathroom, outlets for other equipment within the same bathroom shall be permitted to be supplied in accordance with 210.23(A)(1) and (A)(2).
 
Last edited:
210.11(C)(3) Bathroom Branch Circuits.
In addition to the number of branch circuits required by other parts of this section, at least one 120-volt, 20-ampere branch circuit shall be provided to supply a bathroom receptacle outlet(s). Such circuits shall have no other outlets.
Exception: Where the 20-ampere circuit supplies a single bathroom, outlets for other equipment within the same bathroom shall be permitted to be supplied in accordance with 210.23(A)(1) and (A)(2).

Nice! Do you have an answer to share?
Also, I assume you have a PDF of the NEC? Where and how much?
 
Nice! Do you have an answer to share?
Also, I assume you have a PDF of the NEC? Where and how much?

More than one bathroom is allowed. If three or more women reside there, two is all you get.

I have PDF of all of the California codes....supplied by my employer.
 
Yes, code-compliant. Bad idea though. A hair dryer probably draws about 1000 watts (8.3 amps). Two bathrooms with two teenage girls could easily mean two blowdryers plus a curling iron or two running at the same time. Permissible, but bad practice, in my opinion.
 
Yes, code-compliant. Bad idea though. A hair dryer probably draws about 1000 watts (8.3 amps). Two bathrooms with two teenage girls could easily mean two blowdryers plus a curling iron or two running at the same time. Permissible, but bad practice, in my opinion.
1000 W? Most of the newer hairdryers are at least 1500 if not 1800 W.
 