If I have a 40A CB that feeds #8awg to a 40A range plug, can I use a 4x4x1-1/2" deep junction box to mount the range plug if the box is properly installed and grounded?
Yes, if there is external cable clamps, No if there are internal clamps. 2017 NEC table 314.16 (A) allows 7- #8 conductors. Red, white and black coming in; red, white and black going out; plus one total for the equipment grounds. Total of 7 - #8 conductors allowed in the 21 cubic inch metal box.
Did you change the question? I would have sworn that the original question asked about the size of the junction box required to extend the circuit a short distance. If i read it wrong (maybe, LOL) then yes, a deeper box is required. Would a raised cover or plaster ring suffice, hmmmm? 314.24 (B)-yes, a plaster ring could work, if its deep enough.
can I use a 4x4x1-1/2" deep junction box to mount the range plug if the box is properly installed and grounded?
Would it be called a junction box if a range plug is installed?
314.24 (b)(3) Conductors 8, 6 and 4 AWG- Not less than a 2-1/16" box. Is this what you were wanting us to see?