• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

IPC and UPC Common Venting Violations

Francis Vineyard

Registered User
Joined
Jan 1, 2010
Messages
3,105
Location
Charlottesville, VA
Below are descriptive photographs taken from an illustrative book by Bob Scott; Plumbing Venting Decoding Chapter 9 of the IPC. This book was intended as a handbook to the 2015 IPC. However I could not find the code sections in the IPC where these double bowl connections are in violation. Do you know the sections they violate in the IPC or are they in the UPC?

Thanks in advance for your input.





 
@ ~ @

Francis,

From the `06 UPC, Section 704.2:
"Two fixtures set back-to-back, or side-by-side,
within the distance allowed between a trap and its
vent may be served by a single vertical drainage pipe
provided that each fixture wastes separately into an
approved double-fixture fitting having inlet openings
at the same level."


I do not know of the reasoning behind this Section ! o_O


@ ~ @
 
Interesting, common venting is typically associated with the attached photo and the fact that this person illustrates a correct and incorrect method under the sink is ridiculous to say the least. Whats the difference? The double pattern fitting is in most of the attached pictures. I wonder if that book tells one how to clean those traps that do not break apart-LMAO
 

Attachments

  • common vent(2).JPG
    common vent(2).JPG
    55.3 KB · Views: 29
  • common vent(1).JPG
    common vent(1).JPG
    45.5 KB · Views: 29
The Scott book is about VENTING. The issue of the hard piped sink outlets thru the trap is not the point of the photo.
The violation is that when venting two traps on a horizontal common vent, a 'double pattern fitting" must be used according to the IPC Common Vent section (same in the IRC).

Coincidentally, the double pattern fitting provides for the required full size cleanout for the 2 inch drain...(but again, that's not forcing the double pattern fitting)

On the other issue of hard piped between the sink outlet and the double wye....there is nothing in the IPC and IRC that prohibits that practice. Cleanouts are required for horizontal drainage piping. The trap can be rodded through the sink strainer assembly. And maybe for a commercial establishment, this is not a bad practice as piping below sinks take a beating and joints would probably end up leaking (a lot.)
 
Lets resurrect this question again, if a Kitchen sink has one P-trap, no Wye is required. If two P-traps (typical with a double and G.Disposer), then Double Wye is needed not a single Wye, not for the drain but for the vent system per P3107 Common Vent... Is this the correct code section?
 
Section 3107.2. It might be easy to first think about a vertical common vent with fixtures connecting at the same level. Now lay it down. What do you have to change? The double sanitary tee has to become a double wye. The vent can't be at the "top" (the cleanout end) of the double-wye because horizontal dry vent piping can't be below the flood level rim of the fixture. "The vent AT the connection" for a horizontal common vent arrangement is common for modern cast iron systems. For no-hub, fittings EZS 13 and EZS 35 "vented tub wyes" . There isn't an equivalent in PVC/ABS (that I know of) and I suspect, because of that, the vent was allowed to be downstream of the interconnection. (I don;t wee an equivalent vented tub wye for hubbed cast iron but that needed fitting might have been a threaded Durham-type fitting in the old days as they didn't make hubbed cast iron in 2 inch...I think.)
 
SECTION P3107
COMMON VENT
P3107.1 Individual vent as common vent. An individual
vent shall be permitted to vent two traps or trapped fixtures as
a common vent. The traps or trapped fixtures being common
vented shall be located on the same floor level.
P3107.2 Connection at the same level. Where the fixture
drains being common vented connect at the same level, the
vent connection shall be at the interconnection of the fixture
drains or downstream of the interconnection.
 