2015 IBC, Seattle amendments.
I have a Type II-B, fully sprinklered, B occupancy, 4 story building. There is a separated A-3 occupancy on the 3rd story. In Seattle amendments, there is an exception that no separation is required between groups A-2 or A-3 and Groups B and M occupancies when both are protected with an automatic sprinkler system. Per Table 504.4, the B occupancy can be 4 stories and the A-3 occupancy can be 3 stories. Is the building allowed to be 4 stories as long as the A-3 occupancy is on a story no higher than the 3rd story?
I have a Type II-B, fully sprinklered, B occupancy, 4 story building. There is a separated A-3 occupancy on the 3rd story. In Seattle amendments, there is an exception that no separation is required between groups A-2 or A-3 and Groups B and M occupancies when both are protected with an automatic sprinkler system. Per Table 504.4, the B occupancy can be 4 stories and the A-3 occupancy can be 3 stories. Is the building allowed to be 4 stories as long as the A-3 occupancy is on a story no higher than the 3rd story?